Recent content by Dog Breath

  1. D

    MEP-002a possible Injector Pump Issues

    Your generator will run on straight sea foam You can also get your tank as low as possible and add a gallon of sea foam. Run it and let it circulate with a load.
  2. D

    MEP-002a possible Injector Pump Issues

    I would get yourself an infrared temp gun and check each exhaust pipe for a temperature difference. A cool exhaust may indicate a dirty injector.
  3. D

    Mep003 voltage drop after 7500w

    An update on my issue. After switching control cubical the problem goes with the cubical. Same issues different 003. Next I switched the vr between generators with the issue following the vr. I sent the suspect vr to @kloppk to test and repair. I did pick up two more 4000w heaters cheap and...
  4. D

    Mep003 voltage drop after 7500w

    I will switch vr’s later this afternoon and make sure all contacts are clean and report back. Thankyou
  5. D

    Mep003 voltage drop after 7500w

    Well I hooked up the bad cubicle to the other 003 and I’m getting 53 volts at the convenience receptacle and L0/L1 and L0/L3 both 53 volts 🤷‍♂️ I will clean connections tomorrow and do some testing.
  6. D

    Mep003 voltage drop after 7500w

    I checked all wires in the cubicle. Nothing loose. I exchanged cubicle with another working 003 and it works as it should 70% load 8800w with no issues. So I will have to dig into the bad cubicle
  7. D

    Mep003 voltage drop after 7500w

    Ok I will figure out how to measure the field voltage. My electrical knowledge is limited
  8. D

    Mep003 voltage drop after 7500w

    This control box has a new avr from kloppk. I could switch avr’s from another unit to check
  9. D

    Mep003 voltage drop after 7500w

    @Scoobyshep are you talking the voltage regulator? I have a new ac vr installed in the control box.
  10. D

    Mep003 voltage drop after 7500w

    This unit will run my 7500w heater for hours. If I add 1300 more watts my hertz goes from 60 to 63, volt drop from 240 to 140 then up to 180, load% from 55% to 30%. When adding the extra load it seems to electrically drop then pick up drop pick up. The engine runs strong and does not bog...
  11. D

    Mep-003a no.1 piston

    Guy fang I did find that but apparently it didn’t sink in the first time. I read the first part of it for pistons 1&2and got side tracked. 🤦🏻‍♂️ I was mainly looking to confirm which piston was no1. The fan side. Anyway both units- valves are adjusted and injectors are in. Going together good...
  12. D

    Mep-003a no.1 piston

    I would like to confirm that no.1 piston is on the fan side and firing order is 1234 for valve adjustment. I cannot find firing order in any of the manuals or a search
  13. D

    Mep-003a reactor

    Thankyou Pb
  14. D

    Mep-003a reactor

    It must clean up the power or stabilize the outgoing ac. Trying to simplify the explanation. It must apply to single phase as well as 3 phase power?
  15. D

    Mep-003a reactor

    What is the purpose of the reactor in the ac output control box?