    Default MEP-803A inside an S-280 Shelter

    After spring cleaning my 803a and finding varmint nests (and recent rain after cleaning) I've began the process of moving it indoors.

    I was going to build a structure but I have a spare S-280 Shelter that I think may be a perfect fit.

    I'm seeking thoughts as to why this is (or isn't) a good idea.

    The measurements work, gen set fits through front door and there's 22" clearance on each side,and over 30" clearance front and back.

    The shelter has a vented front door, a vented back window, an open vented ceiling, and a side hatch for cables, hoses, etc.

    It also already has a breaker panel (which I'd rewire 3 phase).

    I'd probably do a rubber floor (garage tiles) and mount the genset to the structure so I could move it if required.

    Operator panel to the back (more lighting) and fuel tank to the front (easy access to fuel at door).

    I'd add the remote start wifi setup and mount an external wifi antenna.

    Also solar panel on roof to keep batteries charged.

    20190510_164318.jpg 20190510_164817.jpg 20190510_164736.jpg 20190510_164716.jpg

    I may use the open hole in top for an electronic exhaust (or fan) to increase cool air flow in summer, have not researched options yet.

    The S-280 has a polyurethane foam core with aluminum skins.

    I'll clear enough space to extend exhaust or use the existing opening.

    Aside from testing it out, I have no way of knowing if it will make less noise, have adequate air flow, etc.

    Open to any thoughts and suggestions, thanks!
    O Lord, won't you buy me a diesel Humvee. My friends all drive Teslas, that won't work for me. Worked hard all my lifetime, no help from the DMV. So Lord, won't you buy me a diesel Humvee.

  2. #2
    Colonel m715's Avatar
    Join Date
    Mar 2008
    Location
    western ma.
    Posts
    238
    Thanks
    14
    Thanked 111 Times in 49 Posts

    Default

    I think that will work fine. I want to do the same type set up with my generator and air compressor. Keeping equipment out of the weather and a dry place to work on it is a good thing. Also helps keep noise down.

  3. The Following User Says Thank You to m715 For This Useful Post:

    Weller (05-17-2019)

  4. #3
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    6,266
    Thanks
    12,096
    Thanked 5,594 Times in 2,693 Posts

    Default

    Its all about room to move. Can you put it in there and still be able to get the doors open and do PMCS type stuff? Cause I tell you, trying to do some simple chore, when you cant turn around, makes it a bear. And second, ventilation. Keeping it cool enough to not over heat in the summer. I know how it gets hot there, and I really know how hot a gen set can make a small room. Those are your two big problems.

  5. The Following 3 Users Say Thank You to Guyfang For This Useful Post:

    319cssb (05-19-2019), SCSG-G4 (05-18-2019), Weller (05-19-2019)

  6. #4
    Colonel Weller's Avatar
    Join Date
    May 2016
    Location
    Kern County, CA
    Posts
    220
    Thanks
    362
    Thanked 176 Times in 80 Posts

    Default

    Got to spend some time planning this weekend. I think movement will be good, especially if I apply your quick release technique to the side doors. Ventilation is going to require some testing. Front door is vented but not sure how much air will flow. Rear windows offer plenty and I'll likely add an exhaust fan (or fans) for summer. I have enough ecu's that I could add one but goal is to keep noise down.

    Generator gets very little use in summer, since home runs on solar. The challenge is I do run it on the hottest days of summer (100 degrees plus) but typically only about 2 hours, cooling the house before sundown.

    Here's a peek inside current shell.

    20190518_143213.jpg

    I'm liking the possibilities of a clean controlled environment. I'd put in a new distribution panel (3 phase) and put my surplus hubbell connectors to use.
    O Lord, won't you buy me a diesel Humvee. My friends all drive Teslas, that won't work for me. Worked hard all my lifetime, no help from the DMV. So Lord, won't you buy me a diesel Humvee.

  7. #5
    General
    Join Date
    Nov 2016
    Location
    South Hampton Roads, Virginia
    Posts
    578
    Thanks
    416
    Thanked 554 Times in 319 Posts

    Default

    I once had a generator similar to this generac 5500 (https://www.northerntool.com/shop/to...0713_200370713) inside a 12x20 building. Each side wall had a window and I opened them up when running.....and held my breath if I had to enter the building for generator maintenance. During an 8 day outage one summer it really struck me by how HOT it was in the building. The exhaust was adding more heat than the windows could transfer out of the shed. I then assembled a metal exhaust hose to get those hot exhaust fumes out of the building. This set up improved the conditions inside the shed quite a bit.

    For an 802 or 803 I would also consider a plenum or some way to deliver FRESH outside air to the intake. The easiest method might be a dedicated exhaust duct off the top of the machine that directs exhaust from the radiator directly outside the building. Your windows and open door would allow a good supply of fresh outside cooling air. And as you first stated you need to run an engine exhaust pipe outside the S280 shed.

  8. The Following 2 Users Say Thank You to Zed254 For This Useful Post:

    Guyfang (05-20-2019), Weller (05-20-2019)

  9. #6
    General
    Join Date
    Feb 2017
    Location
    NY
    Posts
    580
    Thanks
    41
    Thanked 328 Times in 225 Posts

    Default

    At 22in on each side that dosnt give you much room to open the door. Much less open the door and get by them. But in all reality these things dont need much maintenance.

    I still want to build a roof over mine. Just keeping the snow,rain and sun off it will help a ton im sure.

  10. The Following User Says Thank You to Bmxenbrett For This Useful Post:

    Weller (05-20-2019)

  11. #7
    Colonel Weller's Avatar
    Join Date
    May 2016
    Location
    Kern County, CA
    Posts
    220
    Thanks
    362
    Thanked 176 Times in 80 Posts

    Default

    Awesome, thanks. The hole that's already in the ceiling may be perfect for an exhaust duct.
    O Lord, won't you buy me a diesel Humvee. My friends all drive Teslas, that won't work for me. Worked hard all my lifetime, no help from the DMV. So Lord, won't you buy me a diesel Humvee.

  12. #8
    Colonel Weller's Avatar
    Join Date
    May 2016
    Location
    Kern County, CA
    Posts
    220
    Thanks
    362
    Thanked 176 Times in 80 Posts

    Default

    Quote Originally Posted by Bmxenbrett View Post
    At 22in on each side that dosnt give you much room to open the door. Much less open the door and get by them. But in all reality these things dont need much maintenance.

    I still want to build a roof over mine. Just keeping the snow,rain and sun off it will help a ton im sure.
    Getting the doors open works, getting past an open door won't. My current outdoor setup (up against a a shed) is tighter than that and I make it. Like you said, not much maintenance required.
    O Lord, won't you buy me a diesel Humvee. My friends all drive Teslas, that won't work for me. Worked hard all my lifetime, no help from the DMV. So Lord, won't you buy me a diesel Humvee.