• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

MEP803a tripping overload fault while other unit chugs along no problems.

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
I've got one unit that runs fine with two 5400w dryer elements connected in parallel but my other one is tripping the overload circuit within a minute or so of loading it down.

S8 was gritty as **** and presented a volt meter problem when I first got the unit and the unit has had work done on it concerning the the main generator wiring. I cleaned S8 and resolved the volt meter issue but now having issues with the unit holding power under a 3/4 load.

I'll try cleaning S8 again using Deoxit and see where that leads me.

Note: This unit was saturated with gritty dust throughout and required a thorough cleaning and compressed air to even be presentable.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,561
5,066
113
Location
MA
Soak, cycle dozens of times, soak, cycle a dozen times, soak, drink a beer, cycle, soak... that Deoxit is great stuff. Clean until you get tired of cleaning. If it were me, I would also be cleaning all of the terminal board connections in that same rear control area at the same time!
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
Soak, cycle dozens of times, soak, cycle a dozen times, soak, drink a beer, cycle, soak... that Deoxit is great stuff. Clean until you get tired of cleaning. If it were me, I would also be cleaning all of the terminal board connections in that same rear control area at the same time!
Thanks and will do. My wife was going to town and I put four cans of Deoxit on the shopping
list.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,561
5,066
113
Location
MA
The switch might be bad too... but its more likely a corrosion/contamination issue.
 

Guyfang

Moderator
Staff member
Moderator
15,826
21,986
113
Location
Burgkunstadt, Germany
Saw several S8's in the big auction site one for 85 smackers. Old style, but still, whats a can of deox cost times how many you have used and figure out how many hours invested in the old switch?
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
Saw several S8's in the big auction site one for 85 smackers. Old style, but still, whats a can of deox cost times how many you have used and figure out how many hours invested in the old switch?
Yes it reaches a point of diminished returns at some point but I figure it's worth a try considering that a cleaning resolved my volt meter issue a short while ago. I'll try it once more and see what happens then probably go for a new switch.
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
Update: I used a can of CRC cleaner on the S8 switch and exercised it thoroughly. Hooked up my dryer element loads and tried it again....no dice. Still faulting with an overload fault showing on the fault panel. The ammeter DID start working however but was pegging to the right. I cut the load in half (5400w and it was reading @ 75% load.....which I know is wrong. I shut the set down and could faintly smell electrical burning smell.


I spent the rest of the morning checking the wiring connections point to point according to the schematic. While looking at a connection on the under side of S8 using a mirror and a bright LED Maglight I noticed that the contacts on connection #28 of S8 were burnt to a crisp. Most of one contact was missing, lots of evidence of heating and arching. There's no question that S8 has to be replaced at this point and have a couple coming(Thanks Guyfang for the reference on the bay).

I'll replace S8 when the new one arrives and update further.

Thanks to Light in the Dark and Guyfang for your suggestions.....both were correct.
 

Guyfang

Moderator
Staff member
Moderator
15,826
21,986
113
Location
Burgkunstadt, Germany
S8 Switch Terminals
FromWire #Wire #From
TB3-2002A243176CP6-12
TB3-8008A344162BP6-7
TB3-10010A845160BP6-8
TB3-4004A946177BP6-10
TB4-1167B1347175BP6-9
P6-32179B14L1001ATB3-1
TB3-6006A20L1001BK1-A1
TB3-7007A22L2002BK1-B1
TB3-12012A26L3003ATB3-3
TB3-5005A32L3003BK1-C1
TB3-11011A36L0006DTB4-4
TB3-9009A38L0006BTB2-L0
TB4-1167A41
 
Last edited:

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,561
5,066
113
Location
MA
I wonder if you cleaned out something that was preventing the burn up prior (so the current again flowed properly after cleaning) or if the burn up was present, but its time was just up to be discovered.
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
S8 Switch Terminals
FromWire #Wire #From
TB3-2002A243176CP6-12
TB3-8008A344162BP6-7
TB3-10010A845160BP6-8
TB3-4004A946177BP6-10
TB4-1167B1347175BP6-9
P6-32179B14L1001ATB3-1
TB3-6006A20L1001BK1-A1
TB3-7007A22L2002BK1-B1
TB3-12012A26L3003ATB3-3
TB3-5005A32L3003BK1-C1
TB3-11011A36L0006DTB4-4
TB3-9009A38L0006BTB2-L0
TB4-1167A41
TB-3 connection 12 is one leg of a winding used in the 120/240v circuit so that would account for it being overloaded and not being able to carry the full load as only two windings in the generator were active, the third making only
partial or no contact due to the burnt S8 contacts on terminal 28. From the S8 schedule, 120/240 single phase, terminal 28 is active in the circuit along with terminals 26, 25, 21 to L1.
 
Last edited:

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
I wonder if you cleaned out something that was preventing the burn up prior (so the current again flowed properly after cleaning) or if the burn up was present, but its time was just up to be discovered.
I'm positive that the burnt contact was there all along and causing my fault. The set would run without fault on a lesser load of 5400w. It was difficult if even possible to get the spray under the switch I think my cleaning had little effect on that aspect of it. It did however clean the terminal that enabled the ammeter to work.
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
S8 Switch Terminals
FromWire #Wire #From
TB3-2002A243176CP6-12
TB3-8008A344162BP6-7
TB3-10010A845160BP6-8
TB3-4004A946177BP6-10
TB4-1167B1347175BP6-9
P6-32179B14L1001ATB3-1
TB3-6006A20L1001BK1-A1
TB3-7007A22L2002BK1-B1
TB3-12012A26L3003ATB3-3
TB3-5005A32L3003BK1-C1
TB3-11011A36L0006DTB4-4
TB3-9009A38L0006BTB2-L0
TB4-1167A41
Am I missing something? Is one of your columns mislabeled? Is the third column supposed to be "terminal" for S8?
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
15,826
21,986
113
Location
Burgkunstadt, Germany
I sent you the listing, for when you get the new switch. Never, ever, just mark the wires and disconnect them. If someone else hooked up something wrong, you just repeated his mistake.
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
I sent you the listing, for when you get the new switch. Never, ever, just mark the wires and disconnect them. If someone else hooked up something wrong, you just repeated his mistake.
Yes I understand that completely and will follow the list. Is that page in a manual or is that of your own design?

There is wiring in the set that has sharpie marker on them but I went through it this morning and cleaned, tightened and verified the connections by the wire numbers and point to point via the schematic. That's when I observed the burnt contacts.

Thanks once again for your assistance!
 

Guyfang

Moderator
Staff member
Moderator
15,826
21,986
113
Location
Burgkunstadt, Germany
I should not have written "I". Its a "WE" project. Chris Medico is also involved in this project. Its just a very big PITA. Every once in a while I ask a member to check something on a gen set, as I do not have one to look at. So don't be surprised If I ask you!
 

Farmitall

Well-known member
Steel Soldiers Supporter
544
274
63
Location
Eubank, KY
I should not have written "I". Its a "WE" project. Chris Medico is also involved in this project. Its just a very big PITA. Every once in a while I ask a member to check something on a gen set, as I do not have one to look at. So don't be surprised If I ask you!
No problem, I'd be glad to help if I can, just say the word.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks