MEP 802 or 803

Buickrat

New member
28
1
1
Location
New Hampshire
I would chose the 803. I have a similar size house, but have gas hot water/heat, so not as much demand as you, but when I need it, it's there.

You can have an electrician wire in a manual transfer switch and a 50 amp cord/plug to plug into the genny. I installed a weather tight 50 amp outlet to the side of the 803. I plug the cord to into it when the power goes out, and power the whole house. The cable will be at least half the cost of the install. Good outdoor rated 4 wire #6 gauge cable is 10 bucks a foot, and you want the genny as far from the house as possible.
Technically, they call for #2 wire and a 60-70 amp breaker, as the 803's can put out 62 amps, and if a couple things decide to kick on at the same time, it will do that. That wire will cost more.
 

dav5

Active member
396
181
43
Location
Mono, Ontario
I would go with the 803 also. The 802 vibrates way more and if the 803 is being used for sporadic outages fuel economy isn't really much of an issue. You may have the odd long term outage but over a 10 year period I suspect the usage will be minimal and not a factor. I would rather have excess capacity than not enough capacity. Load bank it occasionally and wet stacking isn't an issue.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,522
4,964
113
Location
MA
Oh yeah, the 803s are smooooooth operators! Tough to explain to someone how a 4 cylinder engine can be smoother and quieter than a twin half its size... but its true.
 

justicelee26

Member
41
4
8
Location
South Carolina
The 803 seems like quite a machine. Just the right amount of power to keep everything going without burning though too much fuel. I’m having a hard time finding any in my area but I will keep looking. I just measured my inrush current on my 2-ton AC compressor. It is drawing 69 inrush amps! It seems like I might need to get a hard start kit just to get this thing turned on with the 803.
 

98G

Former SSG
Steel Soldiers Supporter
5,845
3,885
113
Location
AZ/KS/MO/OK/NM/NE, varies by the day...
I would chose the 803. I have a similar size house, but have gas hot water/heat, so not as much demand as you, but when I need it, it's there.

You can have an electrician wire in a manual transfer switch and a 50 amp cord/plug to plug into the genny. I installed a weather tight 50 amp outlet to the side of the 803. I plug the cord to into it when the power goes out, and power the whole house. The cable will be at least half the cost of the install. Good outdoor rated 4 wire #6 gauge cable is 10 bucks a foot, and you want the genny as far from the house as possible.
Technically, they call for #2 wire and a 60-70 amp breaker, as the 803's can put out 62 amps, and if a couple things decide to kick on at the same time, it will do that. That wire will cost more.
Not to derail, but good top of the line 6/4 cable is under $3/ft...


An MEP803 seems like the choice....
 

csheath

Active member
713
196
43
Location
FL
The 803 seems like quite a machine. Just the right amount of power to keep everything going without burning though too much fuel. I’m having a hard time finding any in my area but I will keep looking. I just measured my inrush current on my 2-ton AC compressor. It is drawing 69 inrush amps! It seems like I might need to get a hard start kit just to get this thing turned on with the 803.
Can't remember what my 3.5 ton package unit was but it was north of 70 amps. You can hear the 803 engine labor for a few milliseconds when it starts but it starts and runs fine without a hard start kit

Good luck finding one at a reasonable price. Anything over a couple of grand is nuts for a used machine you will have to sort IMO. Prices have gone bonkers since last year. I would buy a new Perkins single phase unit and fabricate my own enclosure and exhaust before paying the prices they are bringing now.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,522
4,964
113
Location
MA
The pricing is nuts. Ive got a 10k for sale locally, that with what I am asking, I cannot even replace it for! Auction prices a few days ago were over 5k for units that used to be about a grand....
 

gatorbob

Member
110
3
18
Location
Saint Augustine, FL
The 803 seems like quite a machine. Just the right amount of power to keep everything going without burning though too much fuel. I’m having a hard time finding any in my area but I will keep looking. I just measured my inrush current on my 2-ton AC compressor. It is drawing 69 inrush amps! It seems like I might need to get a hard start kit just to get this thing turned on with the 803.
I would get a soft start kit not hard start kit. I'm out $100 on a hard start kit that barely made a difference except reduce the inrush time. Does your meter have an inrush function or are you getting that reading via a "max" button? As others have said, you may be fine doing nothing but a soft start kit should give you quite a bit of safety margin.
 
Last edited:

gatorbob

Member
110
3
18
Location
Saint Augustine, FL
I read about Micro-air EasyStart here and it also worked for me. Although, I could never get accurate measurements before or after. Before the install, my meter captured low inrush readings but an electrician measured the actual inrush to be 2-3X higher. He had a meter that cost several hundred dollars more.
 

gatorbob

Member
110
3
18
Location
Saint Augustine, FL
Type W is around $4 per foot and good for 87 amps in 6ga
This is what I went with. Glad I did because I was pushing 66 amps today on a load test. Although my pin/sleeve connectors are only rated for 60 A. The next step is 100 A and those prices are just way too high even with the Elecdirect knock off type. I wasn't expecting to get more than 62 A out of MEP-803A and was surprised.
 

gatorbob

Member
110
3
18
Location
Saint Augustine, FL
I haven't had mine installed long enough to know how it holds up given the cost but you can definitely hear the difference. It doesn't sound like an AC system starting anymore. It ramps up so slowly for those ~5 seconds. It's quieter than the video given that the compressor is inside the condenser unit. I don't have a good enough meter to be sure of the highest inrush. The first second of inrush knocked ~100 amps off my stock startup inrush. I think the 2nd second might go a bit higher but have no way to measure.

I got it in case my MEP fails I can still use a smaller portable unit. Plus, I am thinking not having that inrush might be a good thing if some other motor starts at the same time when using the MEP-803A. I might even have enough headroom to run hot water at the same time.
 

smokem joe

Active member
500
66
28
Location
Green OH
This is what I went with. Glad I did because I was pushing 66 amps today on a load test. Although my pin/sleeve connectors are only rated for 60 A. The next step is 100 A and those prices are just way too high even with the Elecdirect knock off type. I wasn't expecting to get more than 62 A out of MEP-803A and was surprised.
I wouldn't worry about the 60A plugs. They are tested much higher than that to certify them at 60A. I have run 75A on mine for a load test through 50A plugs
 

justicelee26

Member
41
4
8
Location
South Carolina
The soft start looks really cool. I think it would only be worth the money if it allowed me to run my water heater or my clothes dryer at the same time as the AC. My only problem now is finding a generator. I have a good lead on an 802a but everyone has me convinced the 803a is better.
 

Guyfang

Moderator
Staff member
Moderator
15,674
21,593
113
Location
Burgkunstadt, Germany
Considering how long you will maybe need it, load management should take care of that problem. You don't plan to run for years on end. But for extended time periods, for instance, several weeks, it may become a problem if you have to add maybe extra loads to the equation. Unforeseen things. If it's right on the limit of the 802, then the 803 sounds maybe better. But then I grew up in a power generatin environment where more is better.
 