    Please define what fluctuations means to you.

    Have you mesured/ tested your hertz reading with an independent meter?

    I have not yet measured it with my multimeter. The gauge wasn't moving a whole lot probable ranging from 57-63Hz and not bouncing either. i would dial it in to 60Hz and then it would occasionally climb then i would dial it back and it would hold for a minute before dropping so i would raise it back up a bit. Ashamed to admit that i just don't know enough about this subject to understand what causes the hertz to change...IE is it the genset or the draw put on it etc. My main concern right now was the %rated load meter not reading anything when it had a significant load on it. After reading through some other posts i see that the Dials may need to be cleaned and cycled. I pulled the unit back into my shop to give it a cleaning and figured that i may as well remove the top cover while it was inside and make sure everything was clean behind the rear selector as well and in doing so can't figure out how to get it off. i have every bolt and screw pulled off but the lid won't come off. is it glued on as well? it looks like i can see some sealant seeping out at the seams but i really don't want to damage the panel

  2. #32
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    5,444
    Thanks
    9,890
    Thanked 4,646 Times in 2,272 Posts

    Default

    Yes, it's probably glued down with RTV. A putty knife works well to get it up.

    For me, a fluctuation is the raising and lowering of the hertz, (read that as engine speed) that is somewhat "orderly". For instance, 57-63. It goes up about as much as it goes down. There can be several reasons for the. Also important is the frequency between the hertz swings. Fast and slow oscillations. Different reasons for them also. Fast oscillating set are called hunting sets. You can hear the engine speed go up and down. Sometimes it chugs along like someone is turning it on and off. Slow oscillating is often difficult to hear, unless you watch the gage and tune your ear to it.

    One reason your hertz can be unsteady is the load changes. Things get turned on and off automatically. It's best to load test using a resistive load. No load swing, no need for the gen set to try and self correct the hertz. Loose linkages and such also can be a problem. Also droop. But we won't go there until all else fails.

    You our need to use an independent meter to read the hertz. If you can get an old analog meter, it's best. The digital meters sometimes don't read hertz changes as well as analog.

    As for your percent of load problem, also keep in mind that S6 and S8 have to be in the right positions in relation to one another. If you are not sure, read the Operaters TM.

    got to run, it's 01:35
    Last edited by Guyfang; 01-11-2019 at 20:47.

  3. The Following 2 Users Say Thank You to Guyfang For This Useful Post:

    dav5 (01-12-2019), Farmitall (01-12-2019)

  4. #33
    Private
    Join Date
    Nov 2018
    Location
    Alaska
    Posts
    25
    Thanks
    11
    Thanked 8 Times in 7 Posts

    Default

    Thanks ill get on that this week. Im fairly sure i had both S6 and S8 in the correct positions and i did show load at one time and then it just went away. I ordered some deoxit to clean out the switches I also bought a clamp on meter so i can verify amperage independently although not entirely sure on the procedure to do that. how can i figure the amperage coming off of the generator rather than going to each individual component i have hooked to it? Ive got the unit hooked up to a main panel on the plant so I'm using both 120 and 240 Should i measure each wire at the lugs of the generator and combine? sorry again but I'm learning as i go

  5. The Following User Says Thank You to SalmonSlayer For This Useful Post:

    Guyfang (01-13-2019)

  6. #34
    General
    Join Date
    Nov 2016
    Location
    South Hampton Roads, Virginia
    Posts
    420
    Thanks
    273
    Thanked 406 Times in 228 Posts

    Default

    Clamp meter on the wires coming off main lugs. Red and Black will be hot. White is neutral and will probably have a balancing load on it. On one of my test runs I had 50.35 amps on Red, 53.25 amps on Black, and 3.05 amps on the White. I was testing on a stove and I think the control circuits provided the imbalance of 3 amps. I have removed the oven light. Single Phase, 240 volts.
    Attached Images Attached Images

  7. The Following 2 Users Say Thank You to Zed254 For This Useful Post:

    Farmitall (01-13-2019), Guyfang (01-13-2019)

  8. #35
    Private
    Join Date
    Nov 2018
    Location
    Alaska
    Posts
    25
    Thanks
    11
    Thanked 8 Times in 7 Posts

    Default

    so to calculate the load i would then add them all up? so in your instance you were drawing a little over 106? that can't be right

  9. #36
    General
    Join Date
    Nov 2016
    Location
    South Hampton Roads, Virginia
    Posts
    420
    Thanks
    273
    Thanked 406 Times in 228 Posts

    Default

    Each leg defines the amps. No addition. I had the generator maxed out on the stove and measured all 3 loads. Our 803s are good for 52 amps with a resistive load and no derating. I'm no electrician but I think my Black cable pulling 53.25 amps is equal to the Red and White cables combined - 50.35 + 3.05 = 53.4....close enough. The control circuits are 120 volt and cause the minor imbalance.

    Measure either the Black or the Red to give you the amps you are pulling. Again, single phase, 240 volts. Measure both Red and Black to see how balanced your load is.
    Last edited by Zed254; 01-13-2019 at 16:53.

  10. The Following 3 Users Say Thank You to Zed254 For This Useful Post:

    Farmitall (01-14-2019), Guyfang (01-14-2019), Light in the Dark (01-15-2019)

  11. #37
    Private
    Join Date
    Nov 2018
    Location
    Alaska
    Posts
    25
    Thanks
    11
    Thanked 8 Times in 7 Posts

    Default

    gotcha. thanks a lot! Ive been reading the TM's and I'm going crosseyed.

  12. The Following 2 Users Say Thank You to SalmonSlayer For This Useful Post:

    Guyfang (01-14-2019), Light in the Dark (01-15-2019)

  13. #38
    General
    Join Date
    Dec 2015
    Location
    Eubank, KY
    Posts
    430
    Thanks
    780
    Thanked 316 Times in 184 Posts

    Default

    Quote Originally Posted by SalmonSlayer View Post
    so to calculate the load i would then add them all up? so in your instance you were drawing a little over 106? that can't be right
    Current remains the same in a series circuit. The circuit being out of the gen, through your load and back to the gen. Its a simple seris circuit and either hot leg will give you the total current being drawn.
    No adding of anything.

  14. The Following 3 Users Say Thank You to Farmitall For This Useful Post:

    Guyfang (01-14-2019), Light in the Dark (01-15-2019), SalmonSlayer (01-13-2019)

  15. #39
    General
    Join Date
    Aug 2013
    Location
    West greenwich/RI
    Posts
    554
    Thanks
    19
    Thanked 321 Times in 182 Posts

    Default

    Not to go too far back into this discussion, but if you are going to stock up on filters, check RockAuto.com there are dozens of compatible oil filters, available for as little as $1.50 ea. if you do some creative searching you can find tons of options. You can also get Wix for about $4. They also have the fuel filters, fuel/water separators, air filters etc. If you buy in bulk and stock up you'll save a fortune.

  16. The Following 3 Users Say Thank You to Ray70 For This Useful Post:

    Farmitall (01-14-2019), Guyfang (01-14-2019), Light in the Dark (01-15-2019)

  17. #40
    4 Star General Light in the Dark's Avatar
    Join Date
    Aug 2016
    Location
    MA
    Posts
    1,341
    Thanks
    1,196
    Thanked 942 Times in 576 Posts

    Default

    Last time I did a big filter buy, I went through Fleet Filter (www.fleetfilter.com). I see prices are up (shocker) but they do run sales on occasion

    https://www.fleetfilter.com/filter/51374.html

    https://www.fleetfilter.com/filter/33348.html

    I will check out Rock Auto the next go round.