Thread: Rented a Load Bank

  1. #1
    Private
    Join Date
    Apr 2012
    Location
    So Cal
    Posts
    22
    Thanks
    4
    Thanked 4 Times in 4 Posts

    Default Rented a Load Bank

    Mep-803

    I rented a load bank. I wanted a 30kw but they only had a 100kw so I wonít be able to get much variations in the load to test with.

    I didnít get as early of a start as I wanted. I fired the generator up and decided to let it warm up before I put some load on it. So I went the bath room and came back. Right when I walked up to the generator it shut off...

    It would not start back up because it tripped the CB1 breaker. I restarted it and it ran for 20 seconds and died and it tripped cb1. To I reset cb1 and and turn it to prime run and it tripped cb1....

    I took much longer than I should have to figure it out. Turned out the primary fuel pump went bad?. It was pulling 16amps not making pumping noise then tripping cb1. So I stole a fuel pump from another generator and warmed it up and played with the load bank for a little bit before it was dark. I will run it for real when it stops raining.

    Running this load bank in 120/208 3phase it looks like my options of load are:

    3.5 kw
    7.5 kw
    ~11kw
    ~15kw

    After doing a short 15 minis of warming up to 11kw I set it to 15kw and it ran for about 15 mins then the overload light came on and it dropped the load. I need to find in the TM the overload parameters so I can test to see if itís working. If anyone can point it out to me that would be helpful!

    Also, given my above options of load, will running this generator all day at 11kw be a good enough test/work out?


    Pic showing 16amps on fuel pump
    https://uploads.tapatalk-cdn.com/201...71aaa08afa.jpg

    https://uploads.tapatalk-cdn.com/201...8f2ad2332c.jpghttps://uploads.tapatalk-cdn.com/201...0d543989cd.jpghttps://uploads.tapatalk-cdn.com/201...24e84afa82.jpg



    Sent from my iPhone using Tapatalk
    Last edited by bosko; 01-07-2019 at 03:59.

  2. #2
    Colonel
    Join Date
    Nov 2016
    Location
    South Hampton Roads, Virginia
    Posts
    345
    Thanks
    185
    Thanked 322 Times in 184 Posts

    Default

    I run mine single phase, resistive load (electric stove): 52 amps x 240 volts = 12,480 watts.....call it 12.5Kw maximum capacity. Military derates the machines by 20% (Rated at 10Kw). The Rating ID plate (in TM and bolted to machine above fuel cap) gives you 34 amps in 3 phase. You will need to research the proper calculation to determine maximum watts the machine can pull but you might be expecting it to pull more load than it is built for.
    Last edited by Zed254; 01-07-2019 at 17:53. Reason: corrected derating value

  3. The Following 4 Users Say Thank You to Zed254 For This Useful Post:

    69birdman (01-07-2019), Farmitall (01-07-2019), Guyfang (01-07-2019), SCSG-G4 (01-07-2019)

  4. #3
    General
    Join Date
    Feb 2017
    Location
    NY
    Posts
    489
    Thanks
    38
    Thanked 251 Times in 178 Posts

    Default

    Its a 10k generator with a bit more. 15k is alot more. I would do 11k and if you dont see major black soot/smoke in a few minutes i could call it good. Overloading it could be dammaging to the generator. That kind of defeats the purpose of a maintence load test.

    How much does it cost to rent a load bank?

  5. The Following 4 Users Say Thank You to Bmxenbrett For This Useful Post:

    DieselAddict (01-07-2019), Farmitall (01-07-2019), Guyfang (01-07-2019), SCSG-G4 (01-07-2019)

  6. #4
    4 Star General
    Join Date
    Mar 2014
    Location
    Efland, NC
    Posts
    1,710
    Thanks
    364
    Thanked 1,270 Times in 773 Posts

    Default

    I think we should have a discussion about ratings. These things are rated as primary power sources. This means they can provide their rating full time without damage. That is10kw of resistive load. To do that with reliability you MUST have some overhead on the prime mover side and the electrical side for environmental conditions. The fact that we CAN load these things above the "rating" means we are dipping into the extra factors engineered into the set to achieve the 24/7 (PRIME) rating. Please don't expect one of these sets to make 15kw for any length of time.

    I always "TEST" my units above nameplate because that can quickly show a problem but I don't expect one to be able to run 133% for long.

    Personally I would call 15 minutes at 15kw a monster win and not do it again.

    Oh, and I would never do 15kw in single phase mode.

    Strictly my opinion.
    Chris Medico
    MEP-003a (sold), MEP-803a, MEP-802a, & MEP-831a

  7. The Following 11 Users Say Thank You to DieselAddict For This Useful Post:

    69birdman (01-07-2019), BeStihl (01-09-2019), bosko (01-08-2019), Buickrat (01-07-2019), dav5 (01-07-2019), Farmitall (01-07-2019), Floridianson (01-07-2019), Guyfang (01-07-2019), jamawieb (01-07-2019), uniquify (01-07-2019), Zed254 (01-07-2019)

  8. #5
    Colonel
    Join Date
    Dec 2015
    Location
    Eubank, KY
    Posts
    370
    Thanks
    598
    Thanked 241 Times in 148 Posts

    Default

    Quote Originally Posted by DieselAddict View Post
    I think we should have a discussion about ratings. These things are rated as primary power sources. This means they can provide their rating full time without damage. That is10kw of resistive load. To do that with reliability you MUST have some overhead on the prime mover side and the electrical side for environmental conditions. The fact that we CAN load these things above the "rating" means we are dipping into the extra factors engineered into the set to achieve the 24/7 (PRIME) rating. Please don't expect one of these sets to make 15kw for any length of time.

    I always "TEST" my units above nameplate because that can quickly show a problem but I don't expect one to be able to run 133% for long.

    Personally I would call 15 minutes at 15kw a monster win and not do it again.

    Oh, and I would never do 15kw in single phase mode.

    Strictly my opinion.
    And your opinion is well taken here....and I agree completely. Thank you for the reminder to all.

    I don't know why people try to beat these generators up repeatedly for no good reason. Used as intended, they will pretty much last a very long time and perform well.

    I find it similar to guys that take out four wheelers and try to wreck them every chance they get, then have to spend unnecessary money in repairs, only to go out the next weekend and do it again.

  9. The Following 2 Users Say Thank You to Farmitall For This Useful Post:

    DieselAddict (01-07-2019), Guyfang (01-07-2019)

  10. #6
    4 Star General Light in the Dark's Avatar
    Join Date
    Aug 2016
    Location
    MA
    Posts
    1,202
    Thanks
    1,101
    Thanked 788 Times in 487 Posts

    Default

    I know the engine will handle it, as its rated for higher from Lister from the factory... but yeah, no need to whip a horse just because you can. I test to about 13.5kw and if it pulls, shes good.

    http://www.lister-petter.com/p/power...ngines/16/lpw4
    Non Semper Erit Aestas

  11. The Following 2 Users Say Thank You to Light in the Dark For This Useful Post:

    Farmitall (01-07-2019), Guyfang (01-07-2019)

  12. #7
    4 Star General
    Join Date
    Mar 2014
    Location
    Efland, NC
    Posts
    1,710
    Thanks
    364
    Thanked 1,270 Times in 773 Posts

    Default

    Make sure you are considering apples to apples. The engine from Lister is rated for ~18kw without accessories. No fan, alternator, or generator head.

    You don't have not as much overhead as you might expect looking the factory ratings.
    Chris Medico
    MEP-003a (sold), MEP-803a, MEP-802a, & MEP-831a

  13. The Following 4 Users Say Thank You to DieselAddict For This Useful Post:

    dav5 (01-07-2019), Farmitall (01-07-2019), Guyfang (01-07-2019), Light in the Dark (01-07-2019)

  14. #8
    4 Star General Light in the Dark's Avatar
    Join Date
    Aug 2016
    Location
    MA
    Posts
    1,202
    Thanks
    1,101
    Thanked 788 Times in 487 Posts

    Default

    I hadn't read the fine print on their tech document on the LPW4, but everything you said is correct. Kind of silly... but I suppose all manufacturers dabble in the grey area of "marketing facts".
    Non Semper Erit Aestas

  15. The Following 4 Users Say Thank You to Light in the Dark For This Useful Post:

    dav5 (01-07-2019), DieselAddict (01-07-2019), Farmitall (01-07-2019), Guyfang (01-07-2019)

  16. #9
    4 Star General
    Join Date
    Mar 2014
    Location
    Efland, NC
    Posts
    1,710
    Thanks
    364
    Thanked 1,270 Times in 773 Posts

    Default

    I love this community since we all come together to learn and share.
    Chris Medico
    MEP-003a (sold), MEP-803a, MEP-802a, & MEP-831a

  17. The Following 4 Users Say Thank You to DieselAddict For This Useful Post:

    dav5 (01-07-2019), Farmitall (01-07-2019), Guyfang (01-07-2019), Zed254 (01-07-2019)

  18. #10
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    4,909
    Thanks
    8,123
    Thanked 3,898 Times in 1,958 Posts

    Default

    You guys are what make it great! Together we are strong.

  19. The Following User Says Thank You to Guyfang For This Useful Post:

    dav5 (01-07-2019)

Page 1 of 3 1 2 3 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •