Need some help from Venezuela

Macondo

Member
73
0
6
Location
Venezuela
Thank you Sir,

View attachment 758045 View attachment 758044View attachment 758043 First picture, 03 black wires from power company to 3 x 60 amp breaker, neutral goes bottom. Second picture, old distribution box 03 wire (red, blue and red) to 03 breaker 60 amp each one (our home is almost 60 years old). And last picture the very well known switch that I have my doubts.
Kill a watts is on my to-do list, I will buy on ebay. Next time when need to start the genset I will use the voltmeter to check to monitor volts in side home. And yes, I will never move "AC reconnection switch" while it is running.
Thanks you all for your advice.
 

NDT

Well-known member
Steel Soldiers Supporter
10,146
5,807
113
Location
Camp Wood/LC, TX
The two left breakers in your second picture are Federal Pacific and they are widely regarded as defective. They won't trip when needed to. Consider replacing them.
 

Chainbreaker

Well-known member
1,747
1,827
113
Location
Oregon
So you have 4 wires coming out of generator's load terminals: L1, L2, L3 & LO correct?

Why is the Ammeter-Voltmeter Switch on your Control Panel shown switched to single phase (1 L3-L1) ? If you want to user your panel mounted meter to read 3 phase voltages & load you need to switch it to the 3 phase selections (the switch positions with the "3" above them).
 
Last edited:

Macondo

Member
73
0
6
Location
Venezuela
So you have 4 wires coming out of generator's load terminals: L1, L2, L3 & LO correct?

Yes sir.
Why is the Ammeter-Voltmeter Switch on your Control Panel shown switched to single phase (1 L3-L1) ?

​I moved after I shoot it down.

If you want to user your panel mounted meter to read 3 phase voltages & load you need to switch it to the 3 phase selections (the switch positions with the "3" above them).

Yes sir, when it was working was in one of L3...so that was my original doubt, Where of 3 of L3.

Thanks a lot. All of you are a great support!
 

uniquify

Active member
221
210
43
Location
Sioux Falls, SD
I'm a visual learner. Hopefully this will help someone else.

The 4 positions on the blue arc are for 3-phase.
The 2 positions on the red arc are for 1-phase.

ammeter-voltmeter-switch-positions.png

Assuming you have the voltage adjusted properly:
When the switch is on any of the positions with the yellow dots, the voltage should be 208. (3-phase)
When the switch is on any of the positions with the green dots, the voltage should be 120. (1-phase or 3-phase)
When the switch is on the position with the purple dot, the voltage should be 240. (1-phase)

Edit: I'm not sure what the voltage should be at the purple dot when the reconnection switch is in the 1-phase 120V setting.
 
Last edited:

Macondo

Member
73
0
6
Location
Venezuela
Dear Sir,
Thanks so much, very, very helpful. "One image, thousands words!"
I will work with this.
Yours,

Macondo

I'm a visual learner. Hopefully this will help someone else.

The 4 positions on the blue arc are for 3-phase.
The 2 positions on the red arc are for 1-phase.

View attachment 758069

Assuming you have the voltage adjusted properly:
When the switch is on any of the positions with the yellow dots, the voltage should be 208. (3-phase)
When the switch is on any of the positions with the green dots, the voltage should be 120. (1-phase or 3-phase)
When the switch is on the position with the purple dot, the voltage should be 240. (1-phase)

Edit: I'm not sure what the voltage should be at the purple dot when the reconnection switch is in the 1-phase 120V setting.
 
115
7
18
Location
Miami
Many thanks for your replay.
Yes, positive we have 3-phase, so my doubt is which 3 Phase positions switch select because I don't want to damage the generator.
Please take a picture of your circuit breaker panel your connections and the connections to the generator versus the switch position


Sent from my iPhone using Tapatalk
 