    Default MEP 803A Surging, Not holding frequency

    I have a MEP 803A that is new to me. it starts right up and while it's cold runs great, once it warms up the frequency won't hold steady. i shot a video showing this. it is very long but it is one cut from start up to shut down. Any help would be appreciated. If you are reading this directly after me posting just be patient on the video as it is currently being uploaded.


  2. #2
    General
    Join Date
    Aug 2013
    Location
    West greenwich/RI
    Posts
    564
    Thanks
    20
    Thanked 335 Times in 189 Posts

    Default

    Hello, Have you done any service on the machine? Fuel filters, oil etc? and have you tested it under a load?
    I'd be curious to see if the frequency swing starts sooner and is more pronounced when under a load.
    My first thought is a fuel supply issue which will probably be exaggerated if you test under a load.
    Also, make sure the fuel cap vent ( on the inside of the cap is open and not in the closed position.

  3. The Following 2 Users Say Thank You to Ray70 For This Useful Post:

    Farmitall (06-27-2019), Guyfang (06-26-2019)

  4. #3
    General
    Join Date
    Jan 2012
    Location
    Massachusetts
    Posts
    514
    Thanks
    51
    Thanked 637 Times in 279 Posts

    Default

    To me it seems to be a fuel delivery problem. Starts to starve, RPM's drop, gets fuel again and over revs causing Hz to drop and then go high.
    Possibilities in my mind are...
    - Failing primary fuel pump?
    - Crap in the tank randomly clogging fuel pickup?
    - Clogged fuel filter on the primary fuel pump?
    - Clogged primary and/or secondary fuel filters?
    - Water in fuel water separator?
    MEP-831A Governor Controller Replacements for the SLC100, 2990-01-477-1371, 98-19539.
    https://www.steelsoldiers.com/showth...49#post2176649

    MEP-802A/MEP-803A Remote Start Kits

    https://www.steelsoldiers.com/showth...57#post2208457
    MEP-802A, Two MEP-831A's

  5. The Following 2 Users Say Thank You to kloppk For This Useful Post:

    Farmitall (06-27-2019), Guyfang (06-26-2019)

  6. #4
    Private
    Join Date
    Jun 2019
    Location
    Central PA
    MVPA
    833-6872
    Posts
    8
    Thanks
    4
    Thanked 1 Time in 1 Post

    Default

    i took the gas cap off and it didn't help, i cant figure out which position is open and which is closed.

  7. #5
    General
    Join Date
    Nov 2016
    Location
    South Hampton Roads, Virginia
    Posts
    456
    Thanks
    308
    Thanked 442 Times in 250 Posts

    Default

    Inverted cone inside fuel cap has 'OPEN' and 'CLOSED' stamped on it. Point the small cross bar at 'OPEN'.
    Attached Images Attached Images
    Last edited by Zed254; 06-26-2019 at 13:16. Reason: Added pic

  8. The Following 3 Users Say Thank You to Zed254 For This Useful Post:

    Conatus (06-28-2019), Farmitall (06-27-2019), Guyfang (06-26-2019)

  9. #6
    4 Star General
    Join Date
    Sep 2011
    Location
    Ripley/TN
    Posts
    1,152
    Thanks
    139
    Thanked 905 Times in 552 Posts

    Default

    I agree sounds like fuel delivery. Fuel pump not able to deliver enough fuel, filters clogged or something blocking the fuel pickup in the tank.

  10. The Following 2 Users Say Thank You to jamawieb For This Useful Post:

    Farmitall (06-27-2019), Guyfang (06-26-2019)

  11. #7
    3 Star General
    Join Date
    Mar 2013
    Location
    Oregon
    Posts
    817
    Thanks
    518
    Thanked 828 Times in 440 Posts

    Default

    Quote Originally Posted by Zed254 View Post
    Inverted cone inside fuel cap has 'OPEN' and 'CLOSED' stamped on it. Point the small cross bar at 'OPEN'.
    Often the fuel cap is the first thing to get rusted on the inside making it difficult or impossible to read the "Open/Close" markings. Sometimes you can take a pocket knife, or what have you, and scrape the rust off and read it but the rust usually comes back fairly quickly. Regardless, I always know that it is in the "Open" position if I can pull on the center of the tab and the spring underneath allows it to travel up just a bit. If its tight feeling when you pull up on it, its in the "Closed" position. Another way to know is that in "Open" it allows the crosswise piece to fall into the lower most indentation in underside of cap with the help of the little spring holding it up. Think of it as having a sealing gasket on top of a small hole and when its pulled down tight its "Closed" since the underneath tab is in the raised position on the cam keeping it tight .
    #1 House Gen PU-751/M: 1986 MEP-002a/M116A2 w/Aux Tank & OEM cover
    #2 Spare Gen PU-751/M: 1991 MEP-002a/M116A2 w/Aux Tank & OEM cover
    #3 Shop Gen NF-2 Enclosure: MEP-002a w/Aux Tank

    * Disclaimer - My comments on this forum are based on my opinion and my experiences only. Any information or suggestions I share could sometimes be inaccurate or misinterpreted. It is your responsibility to verify any information before using or to hire a professional.

  12. The Following 3 Users Say Thank You to Chainbreaker For This Useful Post:

    Farmitall (06-27-2019), Guyfang (06-26-2019), Zed254 (06-26-2019)

  13. #8
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    5,600
    Thanks
    10,249
    Thanked 4,849 Times in 2,349 Posts

    Default

    OK. Let clarify what we saw with the clip. I watched it 5 times. The gen set ran with no load, most of the clip? Or did it have a load the whole time? Or you put it on load, and then it started hunting? Or with no load, after warm up, it started to hunt? What I do see is you pulling the plug out, and sticking it back in, under load. That WILL cause it to hunt. And its not good for the plug, nor 120 volt outlet. Try that at night, and you will see a great big fat arc. Also noted, your percent of rated load meter is not reading. What position do you have S8 in? Because S6 control what you should see on the meter. They have to be in the same ball park, so to speak. The reason I want to see what the % rated load is, so we can see just how big your load is.

  14. The Following User Says Thank You to Guyfang For This Useful Post:

    Farmitall (06-27-2019)

  15. #9
    General
    Join Date
    Feb 2017
    Location
    NY
    Posts
    549
    Thanks
    41
    Thanked 307 Times in 211 Posts

    Default

    I had a surging 802 before. If i remember right there was a plunger that was stuck on the injection pump. You could also try adjusting them as per the TM.

    Of corse all of this should be after lunricated new fuel is put in and the fuel filters changed.

  16. The Following User Says Thank You to Bmxenbrett For This Useful Post:

    Farmitall (06-27-2019)

  17. #10
    Private
    Join Date
    Jun 2019
    Location
    Central PA
    MVPA
    833-6872
    Posts
    8
    Thanks
    4
    Thanked 1 Time in 1 Post

    Default

    found a large 240v 10kw heater that took it up to 75% load on the gauge. frequency drooped a good bit but held steady, only thing disconcerting was the embers and blue smoke that came out of the exhaust.