    I have two test subjects.
    A dryer and oven. (maybe 60 amps total. Haven't checked the tags)
    Had to get my tractor running this weekend to move everything under roof.
    Will be connecting the three phase to single phase trans to the gen.
    Then the dryer and oven to the trans.
    Then I will be able for the load test.
    Kris
    Murphy is my friend

  2. The Following 4 Users Say Thank You to KLChurch For This Useful Post:

    flydude92 (10-21-2019), Guyfang (10-22-2019), peapvp (10-21-2019), Zed254 (10-21-2019)

  3. #662
    Sergeant Major flydude92's Avatar
    Join Date
    Aug 2012
    Location
    Waterville, Ohio
    Posts
    102
    Thanks
    360
    Thanked 152 Times in 56 Posts

    Default








  4. The Following 4 Users Say Thank You to flydude92 For This Useful Post:

    Chainbreaker (10-25-2019), Guyfang (10-25-2019), KLChurch (10-25-2019), peapvp (10-25-2019)

  5. #663
    General KLChurch's Avatar
    Join Date
    Aug 2013
    Location
    Montgomery/TX
    Posts
    474
    Thanks
    212
    Thanked 457 Times in 216 Posts
    Murphy is my friend

  6. The Following 3 Users Say Thank You to KLChurch For This Useful Post:

    flydude92 (10-28-2019), Guyfang (10-28-2019), peapvp (10-28-2019)

  7. #664
    General KLChurch's Avatar
    Join Date
    Aug 2013
    Location
    Montgomery/TX
    Posts
    474
    Thanks
    212
    Thanked 457 Times in 216 Posts

    Default

    IMG_20191028_143319.jpgIMG_20191028_143351.jpgIMG_20191028_143400.jpgIMG_20191028_143419.jpgIMG_20191027_150836.jpgIMG_20191027_150849.jpgIMG_20191027_150921.jpg
    This was finished today.
    Connected a breaker box to transformer.
    Connected a dryer to breaker box.
    Lastly one of my pet deer's. (you have to zoom in)
    I believe I am ready to load test.
    L0 is not connected to anything
    Kris
    Last edited by KLChurch; 10-28-2019 at 16:11.
    Murphy is my friend

  8. The Following 3 Users Say Thank You to KLChurch For This Useful Post:

    flydude92 (10-28-2019), Guyfang (10-28-2019), peapvp (10-28-2019)

  9. #665
    Colonel peapvp's Avatar
    Join Date
    Oct 2013
    Location
    Basehor, KS
    Posts
    333
    Thanks
    422
    Thanked 445 Times in 223 Posts

    Default

    OK, Showtime:

    1. Start Generator

    2. Set Output Voltage to 208VAC on L1/L2

    3. Warmup Genset for 1 Min

    4. Turn on Contactor

    5. Check Hz, adjust governor as necessary to 60 Hz

    6. Turn on Dryer ( make sure Breaker is ON ) - check Power / KW reading on Frontpanel

    7. Let run for 1 hour

    8. Turn OFF Dryer

    9. Turn Off Contactor

    10. Cool Down for 5 Minutes

    11. shut Genset Down





    Quote Originally Posted by KLChurch View Post
    IMG_20191028_143319.jpgIMG_20191028_143351.jpgIMG_20191028_143400.jpgIMG_20191028_143419.jpgIMG_20191027_150836.jpgIMG_20191027_150849.jpgIMG_20191027_150921.jpg
    This was finished today.
    Connected a breaker box to transformer.
    Connected a dryer to breaker box.
    Lastly one of my pet deer's. (you have to zoom in)
    I believe I am ready to load test.
    L0 is not connected to anything
    Kris

  10. The Following 3 Users Say Thank You to peapvp For This Useful Post:

    flydude92 (10-28-2019), Guyfang (10-28-2019), KLChurch (10-28-2019)

  11. #666
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    6,254
    Thanks
    12,073
    Thanked 5,561 Times in 2,682 Posts

    Default

    Why did you run it in the door? Run the cable in the sock hole there, and yes, the ground wire should have been connected to LO. as you have a wire from the back side of LO to the back side of the ground stud. Or am I wrong here? That way you can close the door if you want, but LO and the ground stud are connected, as far as I remember. Wire X13B if my old rummy eyes are seeing half way right. The gen set ground is suposed to be hooked to a ground for the set.

    Kris, the load terminals are to be tightened up, with "gefühl". With feeling. Do not over tighten them. They strip easy.

    Otherwise, looks good.
    Last edited by Guyfang; 10-28-2019 at 18:33.

  12. The Following 3 Users Say Thank You to Guyfang For This Useful Post:

    flydude92 (10-28-2019), KLChurch (10-28-2019), peapvp (10-28-2019)

  13. #667
    General KLChurch's Avatar
    Join Date
    Aug 2013
    Location
    Montgomery/TX
    Posts
    474
    Thanks
    212
    Thanked 457 Times in 216 Posts

    Default

    Guy
    That's what I was thinking but I was told not to connect L0 to anything. Just connect the transformer ground to the frame and the frame to the ground rod.
    The wires are just connected for the load test. Will wire it correctly after the test. I will have to move the gen in a different location after the load test.
    Kris
    Murphy is my friend

  14. The Following 3 Users Say Thank You to KLChurch For This Useful Post:

    flydude92 (10-29-2019), Guyfang (10-29-2019), peapvp (10-28-2019)

  15. #668
    General KLChurch's Avatar
    Join Date
    Aug 2013
    Location
    Montgomery/TX
    Posts
    474
    Thanks
    212
    Thanked 457 Times in 216 Posts

    Default

    Started the gen and ran the dryer for over a hour.
    Had to adjust the hz twice and volts once. (not very much)
    After I shut down the dryer the hz jumped to 61 hz.
    So far the gen has run total two hours since bought it.
    The fuel gage still shows full after the two hours.
    The load meter showed 30% while running the dryer.
    The transformer seemed to consume 2% without the dryer running.
    Kris
    Murphy is my friend

  16. The Following 3 Users Say Thank You to KLChurch For This Useful Post:

    flydude92 (10-29-2019), Guyfang (10-29-2019), peapvp (10-29-2019)

  17. #669
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    6,254
    Thanks
    12,073
    Thanked 5,561 Times in 2,682 Posts

    Default

    Kris

    I think you are looking at a solid gen set. 59, 60, 61 hertz? Its all the same. Close enough. The set is after all, not a Precise Gen set.

    Don't refill the tank. Run it a few more times under load, to see if the fuel level sending unit is working. They sometimes get hung up, or gummed up, or come apart. So give it a work out.

    Under long term running conditions, like I said before, we did 6 or 8 hour checks. Don't even have to turn it off. You can check the oil level while running. Correct me if I am wrong, but I seem to remember that the oil dip stick reads on both sides. Running and stopped. Do not confuse them!

    At the same time, you check the gauges. We wrote the gauge reading down, and followed them if they started to change.

    Then fuel it up. Diesel is not real flammable. I never worried about hot re fueling on a gen set. Herman Nelson heater? Different story there. But a gen set? Nope. Or better yet, use the Aux fuel system. We always used it when we could. You just aint ever lived until you refuel 8 gen sets at night, in the rain, without a light, with 5 Galleon fuel cans.

    Have you checked the shutter assy?

  18. The Following 3 Users Say Thank You to Guyfang For This Useful Post:

    flydude92 (10-29-2019), KLChurch (10-30-2019), peapvp (10-29-2019)

  19. #670
    General KLChurch's Avatar
    Join Date
    Aug 2013
    Location
    Montgomery/TX
    Posts
    474
    Thanks
    212
    Thanked 457 Times in 216 Posts

    Default

    Ok,
    I will make a 2 hour run.
    The dryer shuts off after an hour. So I will run the dryer twice.
    Then I will make another two hour run.
    The shutter stays open. It does not open freely.
    The IP leak is fixed.
    Will recheck the oil
    Kris
    Murphy is my friend

  20. The Following 3 Users Say Thank You to KLChurch For This Useful Post:

    flydude92 (10-30-2019), Guyfang (10-30-2019), peapvp (10-30-2019)

Page 67 of 70 FirstFirst ... 17 57 63 64 65 66 67 68 69 70 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •