• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

MEP 804A no/low voltage

bgoebel

New member
23
0
1
Location
maxwell, nm
I recently bought an 804A, about 1600 hours, good clean condition, runs nice but it is not generating power, most of the time. But, on at least two start-ups it has generated good voltage, first when i first got it home two months ago, and once last weekend when we started to hook it up to put to work. I have learned that need to hold start switch longer, and have done some testing. It does send 24 volts dc out of #7 on the S-1 switch. I have adjusted the mag pickup on engine flywheel, has 3 volts there and at the control box. The under voltage fault light comes on at startup. No obvious loose connections at output box. The voltage meter on control panel shows around 25 volts, my meter on contactor in output box shows 14 v. On the occasions when it has worked it has shown 208 volts on all three legs on the panel meter.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Working on other stuff today, but got back to this tonight.

OK, did that Guyfang. Starts normal, still low voltage, but now the circuit interrupter indicates (by the light) that it is closed when I move switch. Still shows only 25 volts on meter, my tester shows same on contactor at L1-L2, L2-L3, etc. on both sides. Previously i was checking each to ground and getting the 14 v reading (still do this time too)

I am wondering if i should start doing diagnostic tests on governor, voltage regulator, etc. that are described in the technical manual.
 

Guyfang

Moderator
Staff member
Moderator
15,686
21,625
113
Location
Burgkunstadt, Germany
Should not be a governor problem. You are not getting excitation voltage to the exciter coil. Hence you only get the 25 volts from inductance.

The first thing you need to check is the volt reg system. Here is the story. Back in the day, there was a series of components that the Libby company made to control the AC volt regulator system.

Then along came the TRC company. They made a replacement AC volt regulator system for the gen sets.

BUT, they are not compatible. If you have a pure Libby system, and install even one TRC part, it wont work. I have tried to attach the list of parts by manufacturer, but am unable to do so. I am sure I have up loaded the info in the TM forum, but will send you the list by other means. You need to look at each part, and see if its a Libby or TRC system. And not mixed.

EDIT: OK, so it did upload the list. Click on the black square and it will download.
 

Attachments

Last edited:

Hard Head

Member
Steel Soldiers Supporter
540
21
18
Location
Greenville SC
I have one a customer shipped me that was a nightmare for him. Wiring wrong, mixed 400 and 60 hz parts. Came out of Tier 2 reset and has 6 hours on it! Some days I just wonder why some people get to use a screw driver!
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Is this component compatibility issue consistent with the fact that we have on occasion gotten this machine to generate power without knowingly doing anything different?

I printed your list guyfang and will take a look later this morning.

I know i have seen TRC label on the voltage regulator, and i have seen a Letterkenny reset label on side of generator cover.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Ok, here's what i found

TRC volt regulator 19870

TRC power transformer 17910

I do not find R16 resistor

R1 is listed on my schematic as Volt Adjust potentiometer. Maybe this is what your list has as rheostat? This has been changed, the connections aren't original, soldering is messy. The component at R1 is a PEC with two sets of numbers: KU2031S28 0620, RV4NAYSD203A

Every other component that is easily visible is from TRC
 

bgoebel

New member
23
0
1
Location
maxwell, nm
For what it's worth:

When the generator did show good power on the meters for both me and the other guy, we both turned the voltage adjust knob and saw voltage change on the meter.
 

Guyfang

Moderator
Staff member
Moderator
15,686
21,625
113
Location
Burgkunstadt, Germany
I do not find R16 resistor (Its located on a panel in the control box. The panel has a fuse/circuit breaker and a switch for 50/60 hertz mode. On the back side is the R16. Most folks would never in a million years look there!)

R1 is listed on my schematic as Volt Adjust potentiometer. Maybe this is what your list has as rheostat? This has been changed, the connections aren't original, soldering is messy. The component at R1 is a PEC with two sets of numbers: KU2031S28 0620, RV4NAYSD203A (clean up the messy solder. I guess the R1 will work. Not sure.)

Every other component that is easily visible is from TRC

Now, when you start the set, turn S1 to start, you measured that the S1-7 has voltage. As you start the set, open the control panel. Look at K15. is it activating? It has a small "flag" in it to show you it is operating. The K15 has to activate, to close two contacts allowing the main gen to get excitation. Make sure the relay is working, and that its in its socket right. Also look for loose wires and broken wire connectors.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Guy, the K15 relay is working. I couldn't see it well through front opening so I took the top panel off. Its apparent that the top panel has been removed previously. I didn't see any "flag" but it is easy to see it operate from the top. It activates when S1 is turned to start, de-activates when S1 is released.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Guy,

I still can't locate R16

On the panel on the control box you seem to be describing, there are, on the top row: Battery Charger Fuse, Load Sharing Adjust, Reactive Current Adjust; on the bottom row, DC Control Power, frequency Select (60/50), Overspeed Reset. There isn't anything else on the back side.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
I tried to check the governor control A-5 according to 4-2.1 in the TM.

While holding Master Switch (S-1) in START position, check for voltage from pin positions 1,3,5 on GCU (A-5) ground. Readings should be battery voltage. If there is no voltage between any connections, GCU (A-5) is not receiving proper voltage and wiring harness should be checked.

Not sure how to do this. I put dead crank switch to off. Where is the GCU ground?
 

bgoebel

New member
23
0
1
Location
maxwell, nm
I tried to check the governor control A-5 according to 4-2.1 in the TM.

While holding Master Switch (S-1) in START position, check for voltage from pin positions 1,3,5 on GCU (A-5) ground. Readings should be battery voltage. If there is no voltage between any connections, GCU (A-5) is not receiving proper voltage and wiring harness should be checked.

Not sure how to do this. I put dead crank switch to off. Where is the GCU ground?

Also, Guy, I told you earlier that all the components were from TRC. The governor control is a Woodward.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
(Its located on a panel in the control box. The panel has a fuse/circuit breaker and a switch for 50/60 hertz mode. On the back side is the R16. Most folks would never in a million years look there!)
Guy, I did after all find R16 i think. On the back side of the 50/60 switch as you said. I was looking on the back side of the panel, not the switch per se. I disconnected one end and get 1.3 ohms. Your Libby/TRC list says 1K ohms.
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Guy

I also checked resistance on the R1, without disconnecting anything. Checked across 2 outside connections. Middle connector is wired to one outside connector. Just like in the picture at 76.121.108.2 › D 15kw MEP-804A and B TQG


It reads 1.6 k ohms (dialed all the way down) to 1.9 k ohms (dialed all the way up) 1.9 k ohms at mid-point on dial. NOT 20 k ohms
 

Guyfang

Moderator
Staff member
Moderator
15,686
21,625
113
Location
Burgkunstadt, Germany
Guy

I also checked resistance on the R1, without disconnecting anything. Checked across 2 outside connections. Middle connector is wired to one outside connector. Just like in the picture at 76.121.108.2 › D 15kw MEP-804A and B TQG


It reads 1.6 k ohms (dialed all the way down) to 1.9 k ohms (dialed all the way up) 1.9 k ohms at mid-point on dial. NOT 20 k ohms
Bill,

According to TM9-6115-643-24, page 2-102, (PDF reader page 164), to test the R1, you need to take it out, read that unhook the wires. Check it that way, so you know its right.
 

Guyfang

Moderator
Staff member
Moderator
15,686
21,625
113
Location
Burgkunstadt, Germany
I tried to check the governor control A-5 according to 4-2.1 in the TM.

While holding Master Switch (S-1) in START position, check for voltage from pin positions 1,3,5 on GCU (A-5) ground. Readings should be battery voltage. If there is no voltage between any connections, GCU (A-5) is not receiving proper voltage and wiring harness should be checked.

Not sure how to do this. I put dead crank switch to off. Where is the GCU ground? (A5-4 wire 100J is ground. ANY wire that has the number 100 in it, is ground)

Also, Guy, I told you earlier that all the components were from TRC. The governor control is a Woodward.
On A5-16 and A5-17 need a signal from the MPU, of 3 Volts AC, when cranking. Do you have that?
 

bgoebel

New member
23
0
1
Location
maxwell, nm
Ok, I disconnected the wires from R1

It does make a difference. The resistance across the top connector (looking at it as if the control panel is closed) and the bottom one is 18Kohms. Across the top and the middle connectors it varies with the dial, however it may be malfunctioning as the tester reading bounces around even if i only wiggle the dial, and as i turn the dial it does not go up or down uniformly. It bounces around from about 14k to 30k.

I did check the mpu signal at A5 several days ago and got the 3 V AC.

Bill
 

Guyfang

Moderator
Staff member
Moderator
15,686
21,625
113
Location
Burgkunstadt, Germany
Ok, I disconnected the wires from R1

It does make a difference. The resistance across the top connector (looking at it as if the control panel is closed) and the bottom one is 18Kohms. Across the top and the middle connectors it varies with the dial, however it may be malfunctioning as the tester reading bounces around even if i only wiggle the dial, and as i turn the dial it does not go up or down uniformly. It bounces around from about 14k to 30k. This is not normal. And it could be why you have voltage sometimes, and sometimes not. You could hit a dead spot and then the excitation falls off.

I did check the mpu signal at A5 several days ago and got the 3 V AC.

Bill
.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks