Thread: Size of Generator needed

  1. #1
    Private
    Join Date
    Aug 2017
    Location
    timmins
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Size of Generator needed

    What size of genset would I need to run a 12 foot shelter with 18,000 BTU/HR air conditioner and lights and all. Thanks

  2. #2
    Chief and Indian 155mm's Avatar
    Join Date
    Oct 2011
    Location
    Guymon, OK
    Posts
    871
    Thanks
    365
    Thanked 848 Times in 426 Posts

    Default

    Is it a military shelter prewired? If yes, what is thesize of the main breaker?
    "Artillery Brings Dignity to What Would Otherwise Be Just A Vulgar Brawl"

    "Happiness Is A Belt-Fed Weapon"

  3. The Following User Says Thank You to 155mm For This Useful Post:

    Guyfang (10-24-2019)

  4. #3
    Private
    Join Date
    Aug 2017
    Location
    timmins
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default

    Yes prewired has a small panel but no main breaker. 100 amp panel I think. It was made as a Dental LaboratoryIMG_2134.jpg
    Last edited by staker; 10-22-2019 at 20:19.

  5. #4
    Chief and Indian 155mm's Avatar
    Join Date
    Oct 2011
    Location
    Guymon, OK
    Posts
    871
    Thanks
    365
    Thanked 848 Times in 426 Posts

    Default

    Photo the breakers and post
    "Artillery Brings Dignity to What Would Otherwise Be Just A Vulgar Brawl"

    "Happiness Is A Belt-Fed Weapon"

  6. The Following User Says Thank You to 155mm For This Useful Post:

    Guyfang (10-24-2019)

  7. #5
    Private
    Join Date
    Aug 2017
    Location
    timmins
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post

  8. #6
    Chief and Indian 155mm's Avatar
    Join Date
    Oct 2011
    Location
    Guymon, OK
    Posts
    871
    Thanks
    365
    Thanked 848 Times in 426 Posts

    Default

    Thats only single ph 240, so 10kw is max
    "Artillery Brings Dignity to What Would Otherwise Be Just A Vulgar Brawl"

    "Happiness Is A Belt-Fed Weapon"

  9. The Following User Says Thank You to 155mm For This Useful Post:

    Guyfang (10-24-2019)

  10. #7
    Private
    Join Date
    Aug 2017
    Location
    timmins
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default

    Ok thanks alot.

  11. #8
    Former SSG 98G's Avatar
    Join Date
    Aug 2013
    Location
    AZ/KS/MO/OK, varies by the day...
    Posts
    4,305
    Thanks
    6,603
    Thanked 3,549 Times in 1,641 Posts

    Default

    Quote Originally Posted by staker View Post
    Ok thanks alot.
    How much stuff do you plan on running at once?

    10kW is generally plenty/overkill for a largish house. For 18,000BTU AC and some lights I doubt very seriously you'll need that much.

    Count up the amps of the largest combination of things you plan to ever have on all at the same time....

    Edit to add example -

    An 18,000BTU AC may draw from 12-20 amps of 120v single phase AC current, depending on efficiency. Assume 20 amps just for purposes of discussion. That's 2.4kW. Running ten 100Watt incandescent bulbs adds another kW (3.4kW total). With all this on and running, want to run a power tool? Say an angle grinder? Maybe another 11 amps (1.3kW) for 4.7kW total.

    I'm betting the lights are not incandescent. If they're LED this will take off almost all your lighting load. (If they're incandescent change them to LED and save thousands on genset cost)

    Even without load management a 5kW MEP802 covers everything easily....
    Last edited by 98G; 10-22-2019 at 21:50.

  12. The Following 2 Users Say Thank You to 98G For This Useful Post:

    155mm (10-24-2019), Guyfang (10-24-2019)

  13. #9
    Private
    Join Date
    Aug 2017
    Location
    timmins
    Posts
    8
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default

    Thanks. I could probably get away with less as don't need air conditioner this time of year. Was thinking 3kw

  14. The Following User Says Thank You to staker For This Useful Post:

    SCSG-G4 (10-24-2019)

  15. #10
    2 Star Admiral Daybreak's Avatar
    Join Date
    Mar 2015
    Location
    Northern, Virginia
    Posts
    1,266
    Thanks
    210
    Thanked 1,655 Times in 716 Posts

    Default

    Howdy,

    Since it was military, look at what the wire plug looks like. That should have a sticker nearby, or the type of plug, and how many wires are there.
    ~~Later Mike