    Default mep 803 help

    I bought my second mep 803 and hooked it up to my house and it ran all the lights like my first unit , but i turned on my ac and the unit quit producing power , the i re closed the AC Circuit Interrupter and it produced power again to just kick power off again, turned air conditioning off and it run fine and produced power, my other generator would run the whole house , the generator would be working a little hard but (could tell there was a load) would run for days like this. This new generator never pulled down a load it just stops the producing power never heard it strain before power loss , seen videos of these generators pulling 15kw and still had more , anyone know the problem or how to fix it Thanx in advance
    Clay

  2. #2
    Sergeant Major
    Join Date
    Feb 2016
    Location
    Bainbridge Island Wa
    Posts
    199
    Thanks
    258
    Thanked 81 Times in 54 Posts

    Default

    What is the measured amps you’re attempting to draw on the generator?
    Did you load bank it first to see how much power you can produce up to its rated output?


    Sent from my iPhone using Tapatalk

  3. The Following User Says Thank You to rcamacho For This Useful Post:

    Light in the Dark (10-25-2019)

  4. #3
    2 Star General
    Join Date
    Jan 2012
    Location
    Massachusetts
    Posts
    607
    Thanks
    54
    Thanked 757 Times in 346 Posts

    Default

    Could be due to poor contacts in the S6 or S8 switch's. Poor contact in either of those can cause the Overload sensor to think there is an overload and cause an overload and the contactor to open.
    With the set OFF I'd suggest exercising both switch's by moving them thru all their positions many times and then return them to the desire positions. Then retry the generator with the load. If that doesn't help get yourself a can of Deoxit. With the set OFF spray some Deoxit in the switch's and exercise them to clean the contacts. Then retry the generator with the load.
    If that doesn't help then there may be an electrical issue with the Overload sensing circuit.

    S6 & S8 are the AM/VM switch on the front panel and the Voltage Reconnection switch inside the control cube and the back wall.
    Last edited by kloppk; 10-23-2019 at 07:11.
    MEP-831A Governor Controller Replacements for the SLC100, 2990-01-477-1371, 98-19539. https://www.steelsoldiers.com/showth...90#post2233190
    MEP-802A/MEP-803A Remote Start Kits
    https://www.steelsoldiers.com/showth...92#post2233192
    MEP-831A Battery Charger Repair & Repair Kits https://www.steelsoldiers.com/showth...83#post2231683
    MEP-831A Remote Start / Governor Controller Kits https://www.steelsoldiers.com/showth...49#post2245549

  5. The Following 5 Users Say Thank You to kloppk For This Useful Post:

    69birdman (10-23-2019), Farmitall (10-23-2019), Guyfang (10-23-2019), Light in the Dark (10-24-2019), rcamacho (10-23-2019)

  6. #4
    2 Star General
    Join Date
    Aug 2013
    Location
    West greenwich/RI
    Posts
    612
    Thanks
    20
    Thanked 386 Times in 220 Posts

    Default

    I second Kurt's suggestions on the switches. I've seen this same problem several times and cleaning the switches has worked every time for me!
    Getting to the guts of the AC select switch requires removing the front cover, so my suggestion is to clean and exercise the AM/VM switch and just give the AC select switch a good workout ( with the machine off ) and see if that fixes it. If not, remove the cover and go after the AC switch with contact cleaner.

  7. The Following 3 Users Say Thank You to Ray70 For This Useful Post:

    Farmitall (10-23-2019), Guyfang (10-23-2019), Light in the Dark (10-24-2019)

  8. #5
    4 Star General
    Join Date
    Mar 2014
    Location
    Efland, NC
    Posts
    1,834
    Thanks
    459
    Thanked 1,429 Times in 837 Posts

    Default

    Also worth popping the top covers off and checking all the wire terminals. Look for anything loose or discolored.
    Chris Medico
    MEP-003a (sold), MEP-803a, MEP-802a, & MEP-831a

  9. The Following 3 Users Say Thank You to DieselAddict For This Useful Post:

    Farmitall (10-23-2019), Guyfang (10-23-2019), Light in the Dark (10-24-2019)

  10. #6
    4 Star General Guyfang's Avatar
    Join Date
    Dec 2015
    Location
    Burgkunstadt, Germany
    Posts
    6,243
    Thanks
    12,039
    Thanked 5,553 Times in 2,677 Posts

    Default

    Or critters. And they CAN lead to such problems as what you have.

  11. The Following 2 Users Say Thank You to Guyfang For This Useful Post:

    Farmitall (10-23-2019), Light in the Dark (10-24-2019)

  12. #7
    Sergeant Major
    Join Date
    Feb 2016
    Location
    Bainbridge Island Wa
    Posts
    199
    Thanks
    258
    Thanked 81 Times in 54 Posts

    Default

    Quote Originally Posted by Guyfang View Post
    Or critters. And they CAN lead to such problems as what you have.
    Mothballs in battery tray and behind operator panel help


    Sent from my iPhone using Tapatalk

  13. The Following 2 Users Say Thank You to rcamacho For This Useful Post:

    Guyfang (10-23-2019), Light in the Dark (10-24-2019)

  14. #8
    General
    Join Date
    Dec 2017
    Location
    Green OH
    Posts
    435
    Thanks
    83
    Thanked 127 Times in 86 Posts

    Default

    Mice love to build nests right where the wires junction coming from the gen head. I'd pull the top off and inspect wiring and clean the switches with Deoxit. This has fixed several units with problems for me.

  15. The Following 4 Users Say Thank You to smokem joe For This Useful Post:

    Farmitall (10-23-2019), Guyfang (10-24-2019), Light in the Dark (10-24-2019), rcamacho (10-23-2019)

  16. #9
    4 Star General
    Join Date
    Sep 2011
    Location
    Ripley/TN
    Posts
    1,165
    Thanks
    139
    Thanked 923 Times in 561 Posts

    Default

    So when it disconnects do you get the fault indicator OVERLOAD? If so, then everyone's comment on cleaning the switches is correct.

  17. The Following 2 Users Say Thank You to jamawieb For This Useful Post:

    Guyfang (10-24-2019), Light in the Dark (10-24-2019)

  18. #10
    4 Star General Light in the Dark's Avatar
    Join Date
    Aug 2016
    Location
    MA
    Posts
    1,526
    Thanks
    1,378
    Thanked 1,161 Times in 694 Posts

    Default

    Deoxit is the savior of many anomalies. Get a few cans for your stash.