    Quote Originally Posted by Speddmon View Post
    I know this thread has gotten off track quite a bit from the original post, but I feel I need to clear a few things up for ya’ll. This may clear them up, or it may confuse you even more. This all deals with the NEC language, and even after all of these years dealing with it, I still get confused, as you will see as you read this long explanation. Thanks to Isaac-1 for questioning this and forcing me to dig deeper into the NEC and research the answer.

    When to drive a ground rod at your generator? There are a few different answers to this question, and they all relate to the type of installation you have. The only time you are required to drive a ground rod at your generator is if the generator is considered a “separately derived system” (SDS) by the NEC….in general, most all residential generator hook-ups are NOT separately derived systems. The definition of a SDS is one in which the neutral wire is broken at the transfer switch...meaning there is no solid path back to the generator by any current carrying conductor (all three lines should be broken by your transfer switch, both hot lines and the neutral) However, you should still be using 4 wire cable so you have a ground running with the others as well.


    Non SDS (which are the most common) have a solid neutral bus in the transfer switch for connecting the neutral. As is the case for many of us that use the back-feed method using a double pole breaker in our main panel, we are creating a Non SDS because the neutral wire has a permanent complete path back to the generator. This means that no ground rod is to be driven at the generator if your neutral runs unbroken (electrically) back to your generator.


    Clear as mud right??? Now, here is where most of the confusion comes into play with our beloved MEP generators…the neutral wire on the generator is bonded to the frame of the generator. If you have a SDS, meaning the transfer breaks the neutral as well as the hot wires when you throw the switch, you are fine. Leave everything hooked up as it was when you bought the generator and make sure you drive your ground rod, because you have the SDS in its purest form. However, if you, like most of us have a NON SEPERATELY DERIVED SYSTEM, then you must

    A)NOT DRIVE A GROUND ROD!!!!
    B)UNHOOK THE NEUTRAL (L0) BOND AT THE FRAME!!!

    Now that clears it all up, right??? Wrong. Now, what if you have a hook-up where you have a cord running to your house going into a pin and sleeve connector at your transfer switch and your transfer switch is set up to be a non SDS system. In that case you must not have a ground rod driven at the set, and you must have the neutral un-bonded from the frame….but what about if you want to use the generator as a stand-alone unit to run some equipment in your shop, like a welder or something by itself and not have it hooked up to your house….now the generator is back to being it’s own power source like the military used them for and must have the neutral bonded again and have the ground rod driven.

    So, to save yourself the hassle and confusion of all of this, use a transfer switch that switches the neutral wire as well as the hot wires, drive a ground rod at the generator and leave the generator frame/neutral bonding just as it was when you bought it. If you want to use it as a stand alone generator, then you are covered; if you want to use it for your house when needed, you’re covered.

    I know this was long winded, and you probably still are confused about this all, as I said, I was confused as well. Dealing with the NEC is very tricky business and requires a lot of research. I am sorry if I misled any of you with my earlier posts.
    My head hurts now....

    Could you put in a cut over switch of some kind to break/reconnect the frame to neutral bond at the gen as needed..?

    Andy..
    Seabees - We Build We Fight

  2. #32
    Blind squirrel rehabiltator Speddmon's Avatar
    Join Date
    Apr 2009
    Location
    Cambridge, Ohio
    Posts
    4,678
    Thanks
    347
    Thanked 1,174 Times in 652 Posts

    Default

    Andy, I am not aware of any specific code prohibiting it, but I highly doubt that you would pass any kind of an inspection simply because there would be no way to ensure that you couldn't possibly have the switch in the wrong position at any given time. That's the whole point of having the transfer switches, and some other codes in the NEC relating to disconnecting means used in industrial installations...They want the stuff to be as fool proof and safe as posssible.

    Quote Originally Posted by jbk
    is that the wire from rear connector j2 thats connected to the back of the ground lug?
    It's actually J10 in that picture (the lower, innermost connector on the back side of the AC reconnection box) . The neutral bond wire is the one that has the funky black polygon drawn around it. It actually bonds to the frame on the inside of the ground splitbolt in the picture.


    Here are some pictures that Bjorn asked for.

    To clarify the differences of the two types of systems, the generator, the load center and the main service have nothing to do with whether it is a Separately Derived System or not. The deciding factor is whether or not your neutral wire remains electrically connected to the main service entrance from the power company. If it remains connected, then you have a Non SDS, and no ground rod should be driven, as well, the wire in the connectors coming from the generator head that ties the neutral to ground should be disconnected and isolated from the frame (wrap it in electrical tape if necessary, but this wire should not be touching the frame for a proper installation)

    You’ll notice in the first picture of a SDS, the generators’ neutral wire is bonded to the frame of the generator, and the generator is grounded via a separate ground rod.

    In the second picture of the Non SDS, you can see how the neutral remains electrically unbroken throughout the entire circuit. Also, that the generator neutral conductor is not bonded to the generator frame. The generator frame ground is still tied together with all of the other grounds in the system, but there is not a separate ground rod.
    Attached Images Attached Images
    Last edited by Speddmon; 09-14-2009 at 22:11.
    Quote Originally Posted by Recovry4x4 View Post
    That's why I knew the answer and you didn't. I read the kindling.
    He is "anti-doghead".

    Even a blind squirrel finds an acorn every now and then!



    1970 M35A2 "The Stone Wagon" SOLD
    1985 M1028/M1031 w/700R4 "Road Oiler"
    MEP-003a 3000 hrs
    MEP-003a 1500 hrs
    1964 Case 530CK "Construction King" Backhoe/loader "Yard Oiler"

    MEP-002a & MEP-003a Spin-on oil filter kits are still 4 sale in the classified section

  3. The Following 11 Users Say Thank You to Speddmon For This Useful Post:

    aspann (06-14-2011), Boatcarpenter (09-15-2009), bsorcs (10-07-2019), cranetruck (09-15-2009), cucv1833 (09-04-2012), DesertRunner (12-30-2010), DeucesWild11 (10-17-2012), Engine5 (10-05-2009), glcaines (01-10-2010), steelandcanvas (01-03-2012), storeman (09-24-2013)

  4. #33
    4 Star General
    Join Date
    Apr 2009
    Location
    SW, Louisiana
    Posts
    1,976
    Thanks
    35
    Thanked 384 Times in 296 Posts

    Default

    Speddmon, to address Andy's potential question of switching back and forth (assuming we are talking about a situation where the generator would be connected to the house for backup power by a pin and sleeve connector as you suggested and might also be used to power 3 phase shop tools, etc. at other times) It seems like a simple solution would be to add another pin and sleeve outlet at a junction box with a ground rod connected to the neutral, then said tool/shop connected to this box. It is my understanding that the NEC only applies to electrical systems connected the power grid, I am not sure about local regulations that may mirror the NEC, so even if this system is not NEC friendly it may still be legal, and fairly safe.

    Ike

  5. #34
    Blind squirrel rehabiltator Speddmon's Avatar
    Join Date
    Apr 2009
    Location
    Cambridge, Ohio
    Posts
    4,678
    Thanks
    347
    Thanked 1,174 Times in 652 Posts

    Default

    NEC Article 90.2 Scope (from the 2008 McGraw Hill NEC Handbook)
    “ (A) Simply stated, the code applies to all electrical work-indoors and outdoors-other than that work excluded by the rules of part (B) in this section.”


    The NEC in Article 100 defines a Separately Derived System as:
    Separately Derived System. A premises wiring system whose power is derived from a battery, from a solar photovoltaic system, or from a generator, transformer, or converter windings, and that has no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system

    So, even though the separate switch would not be part of the utilities electric supply, it is still covered by the rules/regulations of the NEC because it is a separately derived system. That being said, Yes, Andy could put in a separate switch and ground rod. That’s a little different than what Andy had mentioned, he wanted to just switch the neutral/frame ground bond for use as a stand-alone unit.
    Quote Originally Posted by Recovry4x4 View Post
    That's why I knew the answer and you didn't. I read the kindling.
    He is "anti-doghead".

    Even a blind squirrel finds an acorn every now and then!



    1970 M35A2 "The Stone Wagon" SOLD
    1985 M1028/M1031 w/700R4 "Road Oiler"
    MEP-003a 3000 hrs
    MEP-003a 1500 hrs
    1964 Case 530CK "Construction King" Backhoe/loader "Yard Oiler"

    MEP-002a & MEP-003a Spin-on oil filter kits are still 4 sale in the classified section

  6. #35
    Moderator cranetruck's Avatar
    Join Date
    Jan 2005
    Location
    Meadows of Dan, Virginia
    Posts
    10,375
    Thanks
    118
    Thanked 985 Times in 598 Posts

    Default

    Thanks, the images complete the picture.
    Bjorn

    Avatar: XM757 in OK prepared for 1,000 mile trip home. Part of 6,000 mile journey in 2006.

    1969 Ford XM757 8x8, 5-ton Pershing 1A truck tractor...the "improved MV".

    "Some things can't be made better, just differently......a lot of things actually"

  7. #36
    Sergeant
    Join Date
    Jan 2009
    Location
    Tallulah, La
    Posts
    69
    Thanks
    2
    Thanked 5 Times in 5 Posts

    Default

    Wow! What a very insightful thread! I finally got the good 003a genset on a trailer and was looking for answers about hooking it up as stand by and to use as a stand alone. Many thanks guys for so much GOOD information!

  8. #37
    Moderator cranetruck's Avatar
    Join Date
    Jan 2005
    Location
    Meadows of Dan, Virginia
    Posts
    10,375
    Thanks
    118
    Thanked 985 Times in 598 Posts

    Default

    Ref Isaac-1 post #3 above.

    Looked at the wiring on the 10kw genset today and compared my findings to the above referenced post, no biggie, but anyway...
    On the mep018a, the load connections are to L2 (not L1 as stated above), L3 and L0.
    I'll post this and reread Isaac's post in case I missed something.
    Attached Images Attached Images
    Bjorn

    Avatar: XM757 in OK prepared for 1,000 mile trip home. Part of 6,000 mile journey in 2006.

    1969 Ford XM757 8x8, 5-ton Pershing 1A truck tractor...the "improved MV".

    "Some things can't be made better, just differently......a lot of things actually"

  9. The Following User Says Thank You to cranetruck For This Useful Post:

    Floridianson (07-30-2010)

  10. #38
    2 Star General lindyp38's Avatar
    Join Date
    Dec 2009
    Location
    ulster county ny
    Posts
    788
    Thanks
    11
    Thanked 40 Times in 32 Posts

    Default

    Quote Originally Posted by speddmon View Post
    andy and the rest of you guys. I would have jumped into this discussion earlier, but i have been out of town.

    Grounding!!!!!!!!! You do not need to disconnect the neutral ground of the generator. You also do not need to drive a ground rod at the generator! As a matter of fact, you should not drive a ground rod at the generator. The nec states that only one earth ground shall be installed. This was done at your main service panel when your house was wired and built. You do not drive a second ground rod at the generator, the military does this because these sets are the main power source out in the field. They are not the main power source in your home.

    To install them properly, you should be running 4 wires from the generator to the transfer switch/hook-up spot in your house. Two of those wires should be the two "hot" legs of the generator, one wire should be the "neutral" from the generator, and the last wire should be a continuous unbroken ground going back to the grounding bus in the main panel. You could also do as ike suggested and isolate the neutral bond at the frame of the generator and then drive a second ground rod. This is safe to do, but depending on your electrical inspector you still may have a tough time getting it to pass muster, because as i've stated the nec specifies only one (1) ground rod shall be driven!

    The reason for only havine one ground rod is this. If you look at your main electrical panel you will notice that the neutral buss and the ground buss are bonded together, they are essentially (electrically) the same buss. If you drive a ground rod at the generator and do not remove the neutral bond, you now have two (2) pathways for the neutral current to get back to the generator, the neutral wire and the earth ground because of the second ground rod you drove....this is a big no no!!!! The current will parallel the two pathways and now the earth ground becomes a current carrying conductor, and as per the nec this as a violation. The ground shall never be a current carrying conductor. If you feel better doing as ike sugested, you can go to the trouble of disconnecting the neutral bond on the generator and driving a ground rod, but if you want to go according to the nec, that is still not a proper installation, is it safe? Yes!

    If you have not hooked up the generator yet, save yourself the trouble and hassels, and just run the 4th wire (the ground) back to your panel and do it the easy way. If you have 4 wires going from the generator to your house already, leave the ground wire hooked to the generator frame and remove the one going to the second ground rod (just be sure the neutral bond is connected to the frame).
    thank you...as i will be firing up the mep 803a shortly..and i wanna be sure ill be doing this correctly and safely.......

  11. #39
    2 Star General lindyp38's Avatar
    Join Date
    Dec 2009
    Location
    ulster county ny
    Posts
    788
    Thanks
    11
    Thanked 40 Times in 32 Posts

    Default

    im missing this fuse.......what does it look like....?
    ITS MARKED ...F U 1
    thanks
    Attached Images Attached Images

  12. #40
    Blind squirrel rehabiltator Speddmon's Avatar
    Join Date
    Apr 2009
    Location
    Cambridge, Ohio
    Posts
    4,678
    Thanks
    347
    Thanked 1,174 Times in 652 Posts

    Default

    not a great quality picture, but that looks like a standard fuse holder (missing the fuse and cap of course) for a glass automotive (old style automotive) fuse.
    Quote Originally Posted by Recovry4x4 View Post
    That's why I knew the answer and you didn't. I read the kindling.
    He is "anti-doghead".

    Even a blind squirrel finds an acorn every now and then!



    1970 M35A2 "The Stone Wagon" SOLD
    1985 M1028/M1031 w/700R4 "Road Oiler"
    MEP-003a 3000 hrs
    MEP-003a 1500 hrs
    1964 Case 530CK "Construction King" Backhoe/loader "Yard Oiler"

    MEP-002a & MEP-003a Spin-on oil filter kits are still 4 sale in the classified section

Page 4 of 15 FirstFirst 1 2 3 4 5 6 7 8 14 ... LastLast

Similar Threads

  1. Replies: 7
    Last Post: 01-19-2015, 19:04
  2. MEP 003 Question
    By bumperjumper in forum Generators
    Replies: 32
    Last Post: 07-15-2012, 18:11
  3. MEP 003a intake area wire harness needed
    By maddog in forum Generators
    Replies: 9
    Last Post: 10-09-2009, 16:37
  4. XM818 trailer hook up question
    By mmhsv in forum 5-ton and up
    Replies: 9
    Last Post: 06-18-2009, 06:57

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •