  1. #61
    Private tm050712's Avatar
    Join Date
    May 2012
    Location
    Jackson, MS
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default

    Gotcha! Thanks again. Will connection to L-0 accomplish the same thing for the ground?

  2. #62
    4 Star General acesneights1's Avatar
    Join Date
    Sep 2009
    Location
    CT
    Posts
    1,449
    Thanks
    257
    Thanked 287 Times in 173 Posts

    Default

    This is a very good Thread and I suspect will help alot of people in the future in hooking any kind of genset.
    I vote to Sticky it...Any seconds ?

  3. #63
    2 Star General steelypip's Avatar
    Join Date
    Mar 2007
    Location
    Charlottesville, VA
    Posts
    753
    Thanks
    137
    Thanked 470 Times in 247 Posts

    Default

    Quote Originally Posted by tm050712 View Post
    Gotcha! Thanks again. Will connection to L-0 accomplish the same thing for the ground?
    If you're using a non-separately derived system (see Speddmon's post #25 and #32 (with the very helpful pictures)), then you need to break the connection between L[whatever] - the neutral connection point on the gen head windings and the frame ground and connect the frame ground to your meter box/load center ground rod. This is why residential generator connection cable is always four-wire: two for the hot legs, one for the neutral and one for ground.

    Simply put:

    If you're grounding neutral at the house (non separately derived system) then you disconnect the neutral leg from frame ground on the generator, hook frame ground to house ground and generator neutral to house neutral, and switch the hot legs between utility power and the generator as needed with your transfer switch or interlock kit.

    If you're grounding neutral at the generator (separately derived system) then you have to switch neutral conductors along with hot conductors in your transfer switch and you ground neutral at the generator to a driven ground rod at the generator.

    Almost all residential backup generator installations are non separately derived systems. The military generally doesn't have utility power in the picture when using a generator, so they don't have to worry about there being more than one ground rod or multiple neutral connection points. That's what causes the confusion when using a military generator for utility backup power.

    The take-away:

    1. If you have more than one connection between grounding rods and the house neutral wire at any time, you're doing it wrong.
    2. If you have zero connections between house neutral wire and grounding rod at any time, you're doing it wrong.
    3. If the generator housing and frame are ungrounded at any time, you're doing it wrong.


    Any of the above cases can result in equipment damage, injury, or death (and not necessarily in that order).
    "Not far from here, by a white sun, behind a green star, lived the Steelypips, illustrious, industrious, and they hadnít a care: no spats in their vats, no rules, no schools, no gloom, no evil influence of the moon, no trouble from matter or antimatter Ė for they had a machine, a dream of a machine, with springs and gears and perfect in every respect." - Stanislaw Lem

  4. The Following 2 Users Say Thank You to steelypip For This Useful Post:

    ArnieLerma (01-22-2014), Zebcorod (03-18-2017)

  5. #64
    Colonel bsorcs's Avatar
    Join Date
    Apr 2010
    Location
    New Orleans
    Posts
    206
    Thanks
    91
    Thanked 28 Times in 23 Posts

    Default

    Outstanding thread. I actually understood most of it! Seems to be reference material to me.
    bs

    '73 AMG M35A2C/C turbo w/o w
    '91 PU-753M ['07 tier2 re-set]
    USN MWB6516 [the Stud Duck]

    "...we do not yet know all the basic laws; there is an expanding frontier of ignorance."
    RP Feynman

  6. #65
    General cucv1833's Avatar
    Join Date
    Sep 2010
    Location
    Lake Charles, LA
    Posts
    533
    Thanks
    129
    Thanked 65 Times in 59 Posts

    Default

    Great thread!! So I'm installing a transfer switch soon just want to double confirm

    Here's the description.
    GE Outdoor rated 200 Amp boxed Transfer Switch; 2 Pole with Neutral
    *2 Pole Double Throw Switch with a Third non Switching Neutral Pole.
    includes 2 Inputs (1 for Utility, 1 for a Generator) and 1 Output (to your Ppanel)

    It looks like a NON SDS. So I should disconnect the neutral at the generator ground and bring L1-L3 to hot and L0 to neutral and ground to the ground lug all in the transfer panel correct? A 4 wire system. Just like a civy generator

    My champion 7-9kw has a floating neutral on the generator for the panel or stand alone.

  7. #66
    4 Star General 212sparky's Avatar
    Join Date
    Aug 2010
    Location
    Monroe/ Ohio
    Posts
    1,800
    Thanks
    453
    Thanked 382 Times in 286 Posts

    Default

    That is correct. Make sure you have the frame of the gen set grounded. If you are using aluminum wiring use a no oxide compound. It is also good practice to use it on copper that is out doors as well.
    Rob Edwards



    1971 M35A2C W/W
    1985 MEP-004a with M200a1

  8. The Following User Says Thank You to 212sparky For This Useful Post:

    cucv1833 (09-04-2012)

  9. #67
    4 Star General
    Join Date
    Apr 2009
    Location
    SW, Louisiana
    Posts
    1,976
    Thanks
    35
    Thanked 384 Times in 296 Posts

    Default

    In general you always want to use stranded copper when connecting to generators, motors, etc. due to vibration, MTW (Machine Tool Wire) rated wire is best, as it has finer strands than regular stranded and holds up to vibration better, SO (SOOW,SOEW, SJOW, etc.) cord is another good choice. It sounds like you have it right, (bond neutral to ground at service entrance only, unbond L0 from the frame) for safety it is best to drive a separate ground rod for the generator frame, that way if you have in internal short the frame will not be live, this is not as much of a concern on residential generators, but these MEP's do have control panels on them so people are much more likely to touch them while they are running.

    Ike

  10. The Following User Says Thank You to Isaac-1 For This Useful Post:

    cucv1833 (09-04-2012)

  11. #68
    4 Star General 212sparky's Avatar
    Join Date
    Aug 2010
    Location
    Monroe/ Ohio
    Posts
    1,800
    Thanks
    453
    Thanked 382 Times in 286 Posts

    Default

    Your grounding conductor will keep the frame grounded and drain short circut current. the finer the strand the more flexible and more current the cable will carry. Inspect your cabling before each use for dammage as well.
    Rob Edwards



    1971 M35A2C W/W
    1985 MEP-004a with M200a1

  12. #69
    4 Star General
    Join Date
    Sep 2008
    Location
    Tisbury, Massachusetts
    Posts
    1,545
    Thanks
    146
    Thanked 397 Times in 265 Posts

    Default

    Quote Originally Posted by Isaac-1 View Post
    unbond L0 from the frame) for safety it is best to drive a separate ground rod for the generator frame, that way if you have in internal short the frame will not be live, this is not as much of a concern on residential generators, but these MEP's do have control panels on them so people are much more likely to touch them while they are running.

    Ike
    So it is ok to ground frame as well in a non SDS system? This seems different advice again.

    I am back feeding (in power outage mode w Interlockkit) to panel though old 3 pronged range plug I use for my welder, so this is a Non SDS system. Have run it w frame still bonded to neutral and it seemed OK, but understand I should un bond gen frame from LO. Do have a generator ground rod in place. Sounds like I should have a 4 pinned plug. Am confused about ground rod now.
    Last edited by Speddmon; 09-08-2012 at 22:33.

  13. #70
    4 Star General
    Join Date
    Sep 2008
    Location
    Tisbury, Massachusetts
    Posts
    1,545
    Thanks
    146
    Thanked 397 Times in 265 Posts

    Default

    Been thinking about this last post of mine and understand why no one wants to answer it (besides the dead horse thing). Anyway, I want to thank all of the folks who post here and know electrical theory and code.

    All of us getting great advice from this forum should realize that no one can tell you if your rig and hook up is safe without looking at it and testing it. What we are getting is free advice and is usually worth more than that.

    Anyone who is buying and using these generators should get help from real electrician if they are not sure of what they are dealing with when hooking to grid. Even if they are a good mechanic. ( I have been doing stupid things for years and am now an expert at it. ) Anyway, am having an electrician come over to check my set up out.

    I may continue to ask 'uninformed' questions. I did have an electrician come by, his help kept me from miswireing a couple breakers when I moved them for the Interlockkit. (separate circuits w common neutral have to be on alternating breakers in panel) Glad I called him.
    Last edited by dependable; 09-16-2012 at 19:21. Reason: update

Page 7 of 15 FirstFirst ... 3 4 5 6 7 8 9 10 11 ... LastLast

Similar Threads

  1. Replies: 7
    Last Post: 01-19-2015, 19:04
  2. MEP 003 Question
    By bumperjumper in forum Generators
    Replies: 32
    Last Post: 07-15-2012, 18:11
  3. MEP 003a intake area wire harness needed
    By maddog in forum Generators
    Replies: 9
    Last Post: 10-09-2009, 16:37
  4. XM818 trailer hook up question
    By mmhsv in forum 5-ton and up
    Replies: 9
    Last Post: 06-18-2009, 06:57

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •