Thread: MEP-002A and -003A main breaker

  1. #41
    4 Star General Triple Jim's Avatar
    Join Date
    Aug 2012
    Location
    North Central NC
    Posts
    1,243
    Thanks
    87
    Thanked 602 Times in 391 Posts

    Default

    I exercised my MEP-003A today. While it was powering my house's normal loads, I let enough air out of the tank to make my 5hp compressor start. It's an industrial compressor with a real 240V 5hp 1725 rpm motor that is rated at 24 Amps at full load. It started and ran OK, although you could tell that it started a little slower than when on commercial power. The breaker on the 003A did not trip.

    Based on this and the posts earlier in this thread, if the breaker on the generator trips too easily on surges, I'd suspect something is wrong with the fluid-delay type breaker.

  2. #42
    Private
    Join Date
    Oct 2012
    Location
    Bloomington, IN
    Posts
    19
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Default Former Townie

    I have recently purchased a MEP003A that had been setting outside for several years. After new starter and batteries I was able to start it only to find it's not generating. I have spent some time studing the schematic and checking continuity oflot's of wiring and have yet to find any opens or shorts. I am beginning to suspect the gen is the culprit. Is there an easy test for this. Make it easy, 24V is about as high as this 40 yr heavy equipment mech is familiar with.

  3. #43
    General sewerzuk's Avatar
    Join Date
    Mar 2010
    Location
    Seaside, OR
    Posts
    526
    Thanks
    64
    Thanked 334 Times in 104 Posts

    Default

    Quote Originally Posted by keen4007 View Post
    I have recently purchased a MEP003A that had been setting outside for several years. After new starter and batteries I was able to start it only to find it's not generating. I have spent some time studing the schematic and checking continuity oflot's of wiring and have yet to find any opens or shorts. I am beginning to suspect the gen is the culprit. Is there an easy test for this. Make it easy, 24V is about as high as this 40 yr heavy equipment mech is familiar with.
    Probably best to start a new topic on this...as it doesn't really pertain to the main breaker issue
    But the most likely culprit on an -003a is a bad VR board.
    Sold most of my military toys and bought an airplane
    90 Samurai: onboard air, toyota PS, lockers, 6.5 tcase, Warn 9.5XP etc.
    96 Sidekick sport, onboard air, lockers, winch, 2.3L J23 engine, etc.
    Boats, motorcycles, and other junk
    Lots of MEP's
    One very understanding wife

  4. The Following User Says Thank You to sewerzuk For This Useful Post:

    steelandcanvas (12-02-2012)

  5. #44
    Private
    Join Date
    Nov 2012
    Location
    Kansas
    Posts
    8
    Thanks
    1
    Thanked 1 Time in 1 Post

    Default

    Was it ever resolved if MEP-002a and MEP-003a gensets that Sewerzuk had troubles with air compressors (or other large hard start loads in 240v) had actual breaker problems or required "adjustment" of some kind?

    I'd hoping that MEP-002a that I plan to purchase will handle my 3 ton A/C for house if load is managed with slow start by the A/C unit (ie may need to install hard start kit). Any users with MEP-002a successful in running their A/C units? Others having breaker trip problems like Sewezuk?

  6. #45
    General jbk's Avatar
    Join Date
    May 2009
    Location
    livingston la.
    Posts
    416
    Thanks
    3
    Thanked 66 Times in 57 Posts

    Default

    i had similar thoughts this year posted a thread. i wanted to start 2 1/2 or 3 ton central unit with the 002. rla was the killer. 17 240 amps to run but the rla was 112 240 no way the 002 would do it. i used a 003 for this ac this hurricane season and it made the meter jump real good. so check your spec. on the ac some of the older units have just 2 times to run surge.
    mep-003a X2
    mep-802a TQG
    mep-002a X2
    116a2 trailers X3
    mep-017a
    mep-016a
    jim

  7. #46
    4 Star General storeman's Avatar
    Join Date
    Oct 2010
    Location
    Mathews County, VA
    Posts
    1,347
    Thanks
    605
    Thanked 202 Times in 156 Posts

    Default

    Jim,
    Are you sure "rla" of 112 or "lra" of 112? what size breaker is the central unit on?
    Jerry
    MEP-003A
    MEP-002A
    M101A3
    Too much welding equipment to list.
    jerry@queenscreek.com

  8. #47
    General jbk's Avatar
    Join Date
    May 2009
    Location
    livingston la.
    Posts
    416
    Thanks
    3
    Thanked 66 Times in 57 Posts

    Default

    i think your right jerry. i dont recall the breaker size it was my daughters house. i just know this was the max. surge of the ac, 112 amps 240. 17.6 to run
    my old 4 ton unit states 26amps to run and 46 surge.
    mep-003a X2
    mep-802a TQG
    mep-002a X2
    116a2 trailers X3
    mep-017a
    mep-016a
    jim

  9. #48
    4 Star General storeman's Avatar
    Join Date
    Oct 2010
    Location
    Mathews County, VA
    Posts
    1,347
    Thanks
    605
    Thanked 202 Times in 156 Posts

    Default

    Mine is 19.6 and 118 on the ac, 17.5 and 72.5 on heat pump. I haven't tried the heat pump on the 002a, but plan to.
    MEP-003A
    MEP-002A
    M101A3
    Too much welding equipment to list.
    jerry@queenscreek.com

  10. #49
    Private
    Join Date
    Nov 2012
    Location
    Kansas
    Posts
    8
    Thanks
    1
    Thanked 1 Time in 1 Post

    Default

    Thanks so much to Speddmon, Ike, Sewerzuk, JBK, Storeman, etc. for sharing all your experiences and knowledge. You guys are awesome!

    I've spent last 2 days reading EVERY post on MEP-002a and MEP-003a so some of this info swimming around upstairs . . . . it was around 29 pages of 20 posts per page x number of pages in all those posts!

    Ran thru calculation that Speddmon provided for my specific 3 ton A/c which is 13.4 RLA and 78 LRA. That equates to 1.73 x 208 x 78 x .8 / 1000 = 22.45 Kw Thus, looks my best bet is trying MEP-003a if I hope to run 3 ton A/C on house with MEP-003a as backup generator. The little MEP-002a just won't cut it.

  11. #50
    4 Star General quickfarms's Avatar
    Join Date
    Mar 2010
    Location
    Orange Junction, CA
    Posts
    3,488
    Thanks
    40
    Thanked 710 Times in 503 Posts

    Default MEP-002A and -003A main breaker

    This is a very interesting post.

Page 5 of 15 FirstFirst 1 2 3 4 5 6 7 8 9 ... LastLast

Similar Threads

  1. Mep 002a, 003a automatic starting
    By bmwsyc in forum Generators
    Replies: 15
    Last Post: 01-11-2015, 23:42
  2. Mep 002a and mep 003a test runs
    By JAYHAWK 1962 in forum Generators
    Replies: 26
    Last Post: 07-31-2010, 14:02
  3. Muffler for MEP 002a
    By Buckeye Mike in forum Generators
    Replies: 10
    Last Post: 06-14-2010, 10:49
  4. 002 vs 002a and 003 vs 003a GenSets
    By joesco in forum Generators
    Replies: 19
    Last Post: 03-03-2010, 19:40

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •