• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Bigboy down again,M923 won't build air past 59psi

The HUlk

Member
469
7
18
Location
Cincy, OH
Have you ruled out the horn air solenoid valve by disconnecting the wires to see if it stops blowing? A spring causes it to stop blowing the horn which may be wore out or stuck.

I don't know where that connection is in the wiring you asked about. I would guess it's on the engine side of the firewall because the PCB and Horn Fuse are both located there. However a short to the horn wire you highlighted should not cause the horn to blow because the highlighted wires are both always energized when the ignition switch is on.
 
Last edited:

tbar123

Member
691
24
18
Location
enon,oh
I just went out and disconnected wire 26 from the new horn solenoid( not used stock) and the horn did not blow. The original problem is still there with or with out the transfer case engaged.So should I replace the shift lock solenoid or cylinder next?
 

The HUlk

Member
469
7
18
Location
Cincy, OH
Okay, now we know the horn solenoid is not the problem. Wire 26 is not the problem either, it should always have 24V on it. Somewhere wire 25 is being grounded is what is causing the horn to blow. Wire 25 could be making contact against the body anywhere between the horn solenoid and the horn switch.
 

tbar123

Member
691
24
18
Location
enon,oh
I was able before the rain came in today to replace the shift lock solenoid and cylinder. I also replaced the damaged transfer case shifter electronic components.The parking brake wires have been disconnected ( because I don't have the replacement part yet) . So with the horn still disconnected I started bigboy back up and there is no change to his status. The air is still escaping into the intake stack. I did shift the transfer into low and back a few times and that didn't change anything. Any other suggestions? Thanks for any and all advice!
 

Andyrv6av8r

Well-known member
Steel Soldiers Supporter
1,200
457
83
Location
Spartanburg,SC
I was able before the rain came in today to replace the shift lock solenoid and cylinder. I also replaced the damaged transfer case shifter electronic components.The parking brake wires have been disconnected ( because I don't have the replacement part yet) . So with the horn still disconnected I started bigboy back up and there is no change to his status. The air is still escaping into the intake stack. I did shift the transfer into low and back a few times and that didn't change anything. Any other suggestions? Thanks for any and all advice!
Have you tried applying shop air without the truck running? If so, was the air still escaping into the intake stack?
 

tbar123

Member
691
24
18
Location
enon,oh
I have not. I tried once before in one of the glad hand places and couldn't get the ttruck to air up. Is there a better way to go about it?
 

Andyrv6av8r

Well-known member
Steel Soldiers Supporter
1,200
457
83
Location
Spartanburg,SC
I have not. I tried once before in one of the glad hand places and couldn't get the ttruck to air up. Is there a better way to go about it?
Did you use the red one' front or rear, and open the valve? No reason why this shouldn't work.
 

tbar123

Member
691
24
18
Location
enon,oh
I hooked up shop air today and the air is escaping into the intake stack. I then removed the air line from the cylinder on the rear drivers side just in front of the parking brake drum. The air stopped leaking into the intake. SO I followed that line down and took all 3 lines off from the item in the picture. I then tracked that line down which goes to the front axle engagement switch on the dash. On another note the other line leads to the air horns.IMG_20160506_111338839.jpg
 

swbradley1

Modertator
Staff member
Super Moderator
Steel Soldiers Supporter
14,249
1,701
113
Location
Dayton, OH
That's funny, it looks like the same place they take air for the Frankentruck air ride seats.

(Yeah Ben, I know you don't think it's funny now...)
 

tbar123

Member
691
24
18
Location
enon,oh
Ok, I have no idea what to think now. I started bigboy yesterday just to make sure that the problem was still there, and of course it was. I came home today and helped Yolner load his stuff and then took the dash switch for the front axle out. I thought that I would take the exit line off and there would be the problem. Nope! So I put the switch back in and tracked all the lines down again and couldn't figure it out. So I said what the heck,I'll start the truck and see what happens. NO AIR LEAKING!!!!!! Ok this is good,but WTF. So I flipped the switch for the front axle and after about 5-8 seconds the leak started,Shut it off and no leak. Switch right! But why would it leak only with the front axle engaged? Not at the switch?
So after reading what another person had wrote, I checked the temp on the air compressor. The head was 154.8 Just 8" below where the cummins stamp is was 78. I also noticed that the air was a lot slower building after I introduced shop air.
I just hope I can go for drive tomorrow!
 

BenRoberts

Certified insane
1,367
208
63
Location
southwest/ohio
I didnt go through all the previous post so sorry if this is a repeat but could the spring brake rubber be leaking causing it to go back through the intake?
 

tbar123

Member
691
24
18
Location
enon,oh
I found the problem( Major thanks to a fella named Marc,not sure if he has an account here or not.)With his guidance we went through what could be the problem. He suggested that I take the lines off this valve and blow shop air through them to see if this was it. Bingo! I blew air through the line in the rear of this valve and sure enough air was bleeding into the stack. So I took the valve out to see if I could rebuild it.Nope of course not. But I got it working good enough to reinstall to double check the problem. Problem fixed.But the air horn problem is still present. I think when the transfer case lever shorted out it burnt the horn solenoid!IMG_20160529_125204547.jpgIMG_20160529_111318261.jpgIMG_20160529_131654996.jpgIMG_20160529_133538370.jpgIMG_20160529_133527278.jpg
 

Andyrv6av8r

Well-known member
Steel Soldiers Supporter
1,200
457
83
Location
Spartanburg,SC
If I were you, I would bypass and disable that valve anyway. You can manually engage the front end with the switch on the dash.
 

tbar123

Member
691
24
18
Location
enon,oh
So after replacing the above valve, I thought everything was good to go, NOPE! I flipped the dash switch and there was the air in the stack again. So I called Marcfeld up and he pointed me in the right direction again with a few tests to do. I aired the truck up with shop air and when I flipped the dash switch I could hear a dull ping sound coming from the transfer case.So I had my sister (Thanks Hope) flip the switch while I was under the truck. It was coming from the "front axle engagement air cylinder". So I took it out and it looked brand new on the inside. After further investigating, The seal on the piston looked to be in wrong. So I flipped the piston over and reinstalled it. Problem fixed! It appears somebody installed the piston backwards which allowed the air to slide past the seal causing the problem. Here are a few pictures of the cylinder.IMG_20160624_130715462.jpgIMG_20160624_130640788.jpg First pic correct, second pic wrong!
 

Swamp Donkey

The Engineer
Steel Soldiers Supporter
1,450
119
63
Location
Gray, GA
So after replacing the above valve, I thought everything was good to go, NOPE! I flipped the dash switch and there was the air in the stack again. So I called Marcfeld up and he pointed me in the right direction again with a few tests to do. I aired the truck up with shop air and when I flipped the dash switch I could hear a dull ping sound coming from the transfer case.So I had my sister (Thanks Hope) flip the switch while I was under the truck. It was coming from the "front axle engagement air cylinder". So I took it out and it looked brand new on the inside. After further investigating, The seal on the piston looked to be in wrong. So I flipped the piston over and reinstalled it. Problem fixed! It appears somebody installed the piston backwards which allowed the air to slide past the seal causing the problem. Here are a few pictures of the cylinder.View attachment 630046View attachment 630047 First pic correct, second pic wrong!
That makes about 3 or 4 examples that have been posted of them being installed backwards now. Mine doesn't leak but I think I'll open her up anyways to see. Glad you got it fixed.
 

marchplumber

Well-known member
Steel Soldiers Supporter
3,781
2,785
113
Location
Peoria, Illinois
So glad she's not a paper weight anymore!! Really glad ya got your truck back! Glad there were people out there that could help also!! ENJOY!!
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks