MEP-501A Voltage/Load Gauges Inop

kubotaman

Well-known member
Steel Soldiers Supporter
1,049
124
63
Location
RI/MI
Hi All,
Last year I picked up a MEP-501A with about 200 hours from a friend for charging trucks. It runs well and produces power as it should. However, I bought it with the voltage and load gauges not working. It came with a replacement voltage gauge and I just installed it and nothing changed. I checked the instrument panel fuse as per the TM but the fuse was fine.

I tried hooking up the old gauge to 24V and it showed no voltage and I assumed the old gauge was broken. Is it possible my new gauge is defective? Should I bench testing that one with 24V as well? Is there any other known culprits I should check before running down the checklist in the TM? Thanks
 

Dieselmeister

Active member
Steel Soldiers Supporter
168
234
43
Location
Flagstaff, Az
Since both gauges are not working, there is a possibility that the set is wired wrong, or has been "re-wired". Check your voltmeters with a power supply, or a 9 volt battery to se if they work. Don't check the load gauge with a battery or power supply. That gauge has a 50mv full scale deflection.
The MEP-531A ARMY TM 9-6115-673-13&P manual has the wiring diagrams in the back. You can use a voltmeter to check the voltages on the back of the meters while the set is running, and putting out power, to see if the meters are getting any power.
 