    MEP-004A parts, and problems

    WWWEEELLLL Excuse MMMEEEE.......... I use terminology I saw from other users posting. I do not need a know it all posting in condensation tone.. I asked for help and provided information which you either did not see in your post given you mentioned the very things I had already done. So far no...
  2. B

    MEP-004A parts, and problems

    You are referring to the DC breaker which I mentioned is working fine in my post. From reading I think there is a reset switch some where else that I am missing.
  3. B

    MEP-004A parts, and problems

    Hello, I have issues with the MEP 004a I bought. No crank and no panel lights, no fault lights on indicator panel when test switch is used.. Check DC breaker and has 24v before and after it; pulled it and it cut the 24v and pushed it in and 24v back. S/R/S switch has 24v to it. Thing is I...
  4. B

    10 kw generator mep 803a

    If you are referring to me? I've been gone due to work and just was able to look again at this thread. I haven't been able to run the meter tests yet and will up date in about three to four weeks when I get back state side.
  5. B

    10 kw generator mep 803a

    No problem your help has been tremendous.:) I was aware that compartment is the high voltage section; but I needed to find out what kind of relay was clicking back there when I turned the master switch to start; is it the disconnect starter relay? I looked for this terminal strip in the diagram...
  6. B

    10 kw generator mep 803a

    Hey Thanks again. Jeez I spent an hour unscrewing ALLOT of rusted small bolts with rusted nuts on the backside of bulkheads and in places I've never dreamed I'd have to jam my hand. I also pulled the panel in the back where the fuel pump is at the tank. Think I did finally find and you...
  7. B

    10 kw generator mep 803a

    zarathustra again many thanks for your help. I've looked at the manual again and the CR5 diode you mentioned; is it on the resistor diode board shown in the manual inside of the control box? Also which is the K12 relay? Is there a "K12" on it or by the socket in the relay bank show in one of my...
  8. B

    10 kw generator mep 803a

    Thanks much for the information. I will check your suggestion next weekend. I forgot to mention I did pull the plugs at both fuel pumps and float sensor on main tank and the CB1 still popped. This sounds stupid but where is that other relay I could hear clicking ( somewhere in the generators...
  9. B

    10 kw generator mep 803a

    After a delay work caused I was able to check and try your suggestion. I found number #3 to cause CB1 to trip. I left it disconnected and I could hear the fuel pump now run with switch in the first 12 o'clock position. Pump stopped at the second position and when I turned it to start I could...
  10. B

    10 kw generator mep 803a

    Thanks for the info; I will try it this weekend and give an update. I haven't hot wired around the CB1. I just setup a switch and fused wiring to energize the fuel pump and stop solenoid and use the crank switch to turn it over to fire it up; then flip it back to normal. Everything is dead on...
  11. B

    10 kw generator mep 803a

    HHHEEEELLLLPPPPP... Sorry for long delay; work took me away all this time. Recap I have a MEP 803a TQG. Every time I turn the Master Switch from the off position the CB1 breaker trips. I replaced the master switch with the "newer" one and the CB1 still trips. I can turn it to the preheat and...
  12. B

    10 kw generator mep 803a

    I just printed out the manual at the link I was given. WOW 27.6 gig buffered/spooled 293 pages. Printer laser can print both side. When it was done I'd swear my printer gave me the middle finger..
  13. B

    10 kw generator mep 803a

    Thanks for the info. It helps allot.
  14. B

    10 kw generator mep 803a

    Thanks, Would you recall where those threads are or were? Just in case I have started to look for another master switch; but if I can't find one maybe I have to install a set of switches to energize and prime then start. Looks to be four - One momentary contact for glow plug; one on/off for...
  15. B

    10 kw generator mep 803a

    Thanks, Where can I find the switch besides eBay? Also where can I find the wiring diagram or info as to the master switch's terminals where they go to?