  1. R

    MEP-831A 3kw generator, overload @ 2.4kw

    I’ll go through the adjustment procedure and see what yields. I installed the digital governor controller a while back so I don’t think that would be the problem. Sent from my iPhone using Tapatalk
  2. R

    MEP-831A 3kw generator, overload @ 2.4kw

    I was able to sustain 2.7kw for about 15 minutes with no issues so it appears that the jumper worked. So that would indicate that a relay isn’t latching? Any idea which relay I should check out? Interestingly, when I loaded up to 3kw, the governor started to intermittently close. Keep running...
  3. R

    MEP-831A 3kw generator, overload @ 2.4kw

    I’m running in 120V mode, off of L1 for this test. I installed a supplemental 120V 20A receptacle, which is fed from L1. Sent from my iPhone using Tapatalk
  4. R

    MEP-831A 3kw generator, overload @ 2.4kw

    Greetings, looking for some trouble shooting assistance. My MEP-831A runs well but trips overload after running for less than a minute at loads above 2.4kw. I’ve removed and inspected the inverter assembly and didn’t see any evidence of leaking / damaged capacitors or overheating of components...