mep803a was generating power to home but not now
Retired Wood Guy
Geneva Fl
Hi I am new to this invaluable form Steel Soldiers but not getting lost chasing rabbit trails.
Short story. Generator worked flawlessly 3 years ago for Hurricane Ian.
I shut down after 30 days in 2022 October.
I had been cranking every few months to keep active.
I needed home power about 4 months ago and set would not generate power.
I printed the TM 642-24 and started the eating procedures and following all you guys on the post.
I have tested S5 a couple times. one test good. one bad. i tested again for 3rd time and its good.
I also tested S5 diode between points 2 and 5 and did seems in right direction and tested ok.
I have power to the convenience receptacle
I bench tested the K1 relay and it had to be helped closing.
I have a new K1 relay from Callie colt.
I installed and it will not close in while running the set.
I do not believe I am getting 24 volts to y on K1
I read on this form to check the terminal plug where it goes through the panel and spray with contactor spray cleaner and re connected.
my 3amp td fuse next to ac interrupter is good.
I have written down all my testing but am now getting weary and in need of help.
Thank all of you fellas on this Form. It has been so helpful at finding out what my problem is not. I haven't hit the problem yet but hopefully with help I will.
Bob
Scoobyshep
2,188
Florida
Bob
If it's just not getting past the contactor the good news is it's a fairly simple control circuit just have to figure out what is not allowing it to close.
By the way Geneva Florida as in right next to Sanford?
Retired Wood Guy
Geneva Fl
yes
My 2 sons in Army (retired) grew up here In Geneva.
1/2 way between Sanford and Titusville
One of the last things was tracing was the x and y on k1
I pulled of wire leads x and y just to make sure the new K1 i installed was working. It was and working.
I had 24v dc on Y. I don’t remember if closed the the s5 or not but I think I closed the s5 to check For 24 dc Reading.
I feel like the X on the K1 is the negative, Am I possibly correct?
The X on the K1 goes to the K20 oil pressure relay.
I had a new one so I replaced for good measure.
I checked the diode CR1and CR3 and the values and they were good.
Going to call it a night.
Thanks for any advise
Ray70
7,084
West greenwich/RI
If I recall correctly, X and Y are just the switched leads for the illumination bulb +. I think 24V power comes into X and when the K1 contactor closes it allows 24V to pass through to the illumination bulb.
11 and 12 are the + and - that control the K1 relay itself.
12 being - and 11 being + coming from the switch, passing through K8 ( the Over Load / Short Circuit relay.
You can check this with a meter to verify continuity from 12 to battery / chassis -
To test the K1 ( with the engine off ) you can simply remove the wire from the 11 terminal and put a small wire from 24+ and touch it to the 11 stud on K1 and you should hear a loud CLUNK if K1 closes.
If it closes consistently I would call K1 good.
If it doesn't always close you can try opening it to clean it internally.
If it does not close at all I would suspect it is stuck. A few whacks from a rubber mallet while K1 is powered from the battery may free it up, but if it does, that still indicates K1 probably needs to be cleaned inside. If not, K1 has bigger issues internally.
Retired Wood Guy
Geneva Fl
OOPS
I meant to say I am getting overwhelmed chasing rabbit trails. I believe I will stick with Steel Soldiers.
That will cut down on my confusion.
Possible Hurricane in Atlantic now so I will go over TM 642-24 trouble shooting methodically now.
Short Story is Mep803a worked perfectly in 2022 October
Set cranks and runs well
110v ac at conv. plug
AC interrupter switch not closing and lite not coming on
no power to main lugs
I am in urgent need of advise
Thank You all
Bob
DieselAddict
2,347
Efland, NC
Be sure to get the updated DC schematic.
Retired Wood Guy
Geneva Fl
I Just checked and when I closed the S5 No Light No Power to the L1 L2 L3
I checked the Ground fault breaker at the Panel face with Genset running. GFI tripped as it should No power to convenience receptacle. Hit reset and power back to receptacle, but not to L1 L2 L3 No voltage. I wanted to get back to you asap
BUT tried one more thin I read in the Mep803a threads.
They mentioned holding the Master switch for 10 seconds after the Gen cranked. I am not in the habit of holding the key switch on anything for 10 seconds past the time the engine cranked. I thought I would try to hold Master Switch for at least 10 seconds longer.
and
Everything on my MEP803 has came back to life. S5 I heard close in. AC Circuit lite came on and is staying on.
120v on L1 120v on L3 240 volts between L1 and L3
Last week I ordered a K20 Relay (oil pressure relay) and thought I would put in for giggles. Last week I had no success and everything I was checking was good. Last thing I did Saturday was to install the K20 and try the S5 (ac circuit relay) and it did not close in, so I gave up for the day.
Today I cranked to be able to answer your question. The only thing I did different was to hold the Master Switch Longer. Everything worked as normal.
The takeaway with all this is My K20 oil pressure was bad. With the new one installed AND me holding the Master switch for 10 more seconds, I am back in working order. (to back verify the old K20 I put back in and nothing worked)
I thank all of you for all your expertise and prior post. I have read many of them and was loosing faith in my Mep803a.
Now because of you guys I have been renewed.
Kindest Regards
Bob the retired wood guy.
Light in the Dark
6,758
MA
If you had power at the 120v outlet, the extended cranking shouldn't have done anything... The field was excited and the genhead was making power the whole time. Perhaps you got lucky and some corroded item found a path through it, but I don't think your problem is 'gone'.
peapvp
1,645
Basehor, KS
A General note:
The easiest way of checking if K20 is working is by observing M3, the Hour Meter while Genset is running.
Off course this requires the Hour Meter to be operational in the first place.
Both circuits, for K1 Terminal X and Hour Meter Terminal + get their +24 V Supply from K20.
So, without even using a VOM or DMM, K20 can be ruled in or out.
This leaves then only the K1 Terminal Y to chassis ground.
In this scenario, by just simply holding S5 in close position, the simplified trouble shooting continues:
1. K1 activates, but drops off as soon as S5 is released back to center / resting position, then the problem lies solely in the Self Holding Contact 11 and 12 of K1 or Diode CR 3 or K8 SC / OL Contacts
2. If K1 does not activate while holding S5 in close position, then the problem is from K1 Terminal Y all the way to S5 Switch Terminal 5 and from Terminal 6 to chassis Ground.
Retired Wood Guy
Geneva Fl
Good Morning, Before yesterday my hour meter was not advancing. I checked to see if the hour meter was advancing yesterday with new K20 and it was.
Just for grins changed back to the old K20 and I cranked Master Switch for the Genset without holding in the start position 5 seconds. I could not get the S5 to activate the K1. I Cranked the Master switch this time holding the Master switch for 5 seconds and the S5 would not activate the K1.
I turned off and again and installed new K20 and Cranked the Master Switch and held in the crank position for 5 seconds longer. Everything came back to life again. All is working as it should. With new K20 I just cranked and let go. S5 would not Activate the K1.
Curious point for me.
Sooo, I decided to go over cranking instructions procedure TM 642-10
2-10.1
c. Hold the Master Switch in the Start position UNTIL The OIL PRERESSURE REACHES 25 PSI
d. Release Master Switch
What is known by me is I also had changed out my old K20 oil pressure relay with a new one. Now when I follow the cranking instructions in the Operators Manual Everything works as it should.
My Questions below
1. Could my problem be that simple?
2. Should I be looking as to why my old K20 was defective?
In an earlier some one mentioned I may have another problem. Should I look further?
I feel a little dumb asking this but I will anyway
Can I put a 12vdc solar charger on each Battery independently?
I have volt meter probed each battery and they are coming up with 12 volts dc according to the batt post.
I understand why and how the batteries produce 24 vdc when properly connected but can not understand if it is ok to charge with 12v if properly connected to the corresponding + or - Battery post.
My Expertise is all Voltage that happens AFTER connected L1, L2, and L3
Everything before the Load bushings is Black Box to me!
I thank all of you for helping me get my GenSet working properly and am hoping some one else gets the benefit of your Skills through the Steel Soldiers Form.
Regards
Bob Hughes
PS I am a retired from FPL also as a Lineman and Cable Splicer.
Ray70
7,084
West greenwich/RI
One thing that may clarify things for you too is that as mentioned earlier, the GFCI plug and K1 get their power from the same place. If your GFCI was working but K1 wouldn't close and the light not illuminate, has nothing to do with anything you did holding or not holding the S1 switch.
Same as if you see voltage and Hz on the meters, the generator is producing power and sending it to the GFCI and K1.
All holding S1 does is flash the field ( usually not necessary to produce power unless the gen has been sitting a long time ) and redirect power to the fuel solenoid around the low oil pressure switch while sufficient oil pressure builds up to close the oil pressure switch and allow you to release S1 without the FSS killing the engine.
Holding S1 has nothing to do with K1 closing or not closing if the gages are showing voltage and Hz.
So if K20 died.... replace and move on... I wouldn't worry about trying to determine what killed it, unless the replacement happens to quickly go south as well!
As for battery chargers, yes you can definitely use 2 12V solar chargers attached to the individual batteries, while the batteries are connected in series. Many say that 2 12V chargers is a better way to charge as opposed to a single 24V charger..... others may disagree, but I personally use a pair of 12V battery chargers ( not solar ) on everything I own with dual batteries.
Scoobyshep
2,188
Florida
The disadvantage to charging 2 12v batteries in series is 1 will take more of a charge than the other. As they age and the sulfides build up the battery internal resistance changes, they hardly ever have the same internal resistance.
Really kind of a moot point, a battery is 6 cells wired in series anyway so if anything You're just doubling the risk of charge imbalance.