    I'll try to remember to pull one next time I am at my shop. The latest roll was a little bit snugger, but not as tight as what I've gotten locally. I could still seat it all the way on the T fittings and injectors no problem

  2. #82
    Sergeant maniatopoulosg's Avatar
    Join Date
    Mar 2018
    Location
    Miami
    Posts
    89
    Thanks
    235
    Thanked 27 Times in 15 Posts

    Default

    Quote Originally Posted by justicelee26 View Post
    Getting ready to remedy this problem on my machine. The Continental stuff is 12.99 a meter. How much will it take?
    Did you get a response


    Sent from my iPad using Tapatalk

  3. #83
    General
    Join Date
    Jan 2012
    Location
    Massachusetts
    Posts
    504
    Thanks
    50
    Thanked 608 Times in 270 Posts

    Default

    Quote Originally Posted by jamawieb View Post
    Do you have a part number for what you ordered (Gates 1/8 hose)
    In my notes from another thread I have the 1/8" Gates as PN 27000 (1/8" / 3.2mm)
    MEP-831A Governor Controller Replacements for the SLC100, 2990-01-477-1371, 98-19539.
    https://www.steelsoldiers.com/showth...49#post2176649

    MEP-802A/MEP-803A Remote Start Kits

    https://www.steelsoldiers.com/showth...57#post2208457
    MEP-802A, Two MEP-831A's

  4. #84
    General
    Join Date
    Dec 2017
    Location
    Green OH
    Posts
    406
    Thanks
    78
    Thanked 101 Times in 71 Posts

    Default

    Quote Originally Posted by kloppk View Post
    In my notes from another thread I have the 1/8" Gates as PN 27000 (1/8" / 3.2mm)
    This sounds very familiar to me.

  5. #85
    Colonel
    Join Date
    Sep 2016
    Location
    Tallahassee, FL
    Posts
    298
    Thanks
    92
    Thanked 162 Times in 103 Posts

    Default

    I tackled this last night. Soup to nuts, took about 3 hours. My 803 is a 2000 non-reset unit, so most of the nuts are not caged. I went ahead and installed rivnuts, which led to a little extra work that is not necessary to complete the fuel line repair. Here is some of what I did:

    1. remove all of the bolts from the rear panel to get access to the fuel tank to remove/connect the old/new fuel return line
    - the bolts along the bottom have nuts on the back side, all other nuts are caged
    2. remove all of the bolts from the top cover
    - all bolts going into the radiator area are caged
    - most others came off using an light weight impact driver and holding the nut with my fingers
    3. remove front top cover to get access to the support that the front and rear top cover mount to
    - there are only about 10 bolts to get this off, one of them is caged, the rest are bolt and nut
    - the panel cover has to come off and most of the screws broke off while attempting to remove them

    With all of these covers off, locating and removing the fuel return line is easy. My old fuel line pulled apart and came out easily. Getting the old hose off of the Tees required a little more effort, though. I simply took the section of Tees out as a whole line, and rebuilt it on my workbench using the 3.2mm gates hose. The hose was rather tight and I used some WD-40 to lubricate the ends while reassembling. I also had to use a towel and a air of pliers to hold and twist each piece to a secure connection. No hose clamps are required. Once pieced together, I strung the new Tee section back on top of the engine and, using WD-40 again, was able to put the hose onto the return barbs. After getting all the hose connected, I fired up the generator and watched for 5 minutes to verify that there were no leaks.

    With all of the panels off, I was easily able to install the rivnuts. I used Astro Pneumatics 1442 rivnut setter, with a 10-32A mandrel to install the aluminum rivnuts. You will want to use aluminum rivnuts to avoid galvanic corrosion(dissimilar metals). For bolts, I reinstalled the original bolts as they are, I believe, plated to prevent galvanic corrosion. I stripped a few, and broke many of the screws that attach the control panel cover and will be replacing those with zinc plated 10-32 bolts/cap head screws. From what I've gathered, zinc has a lower instance of galvanic corrosion with aluminum, and the plating prevents the steel from contacting the rivnut.

    When installing the rivnuts, I found that installing the rivnut on the tool fully would make it easy to over-pull the rivnut, essentially stripping out the treads. The easy fix is to thread the rivnut onto the mandrel until only a few threads are still uncovered. This limits the full pull of the tool and still creates a strong bond on the rivnut. It did take some trial and error, but I had the process down after the third one. There were a handful of places where I could not install a rivnut due to the mounting hole interfacing with multiple panels, most notably on the front top cover, in which laces I simply reinstalled the bolt and nut.

    All said and done, from disassembly to fully reassembled, I finished this project in roughly three hours. I had put it off for fear of the hundreds of nuts and bolts that would be impossible to reach. After going through it, it is perhaps 40 total nuts and bolts to attack, many of the nuts are caged and therefore not a real problem. I suspect going back with nuts and bolts would have taken much longer than using rivnuts, though. The 1442 tool is overkill for aluminum 10-32 rivnuts, and you can easily strip them out, but it is easy to learn how to do it properly. I have other uses for the tool with larger rivnuts, so that is why I went with it. If you are just wanting to install rivnuts on your MEP, you should be able to get by with either a cheaper, lighter-duty, setter, or just use the bolt/nut/lockwasher method which is well documented in numerous youtube videos.

  6. The Following User Says Thank You to lonesouth For This Useful Post:

    Coug (05-15-2019)

  7. #86
    General
    Join Date
    Dec 2015
    Location
    Eubank, KY
    Posts
    429
    Thanks
    777
    Thanked 312 Times in 183 Posts

    Default

    Quote Originally Posted by lonesouth View Post
    I tackled this last night. Soup to nuts, took about 3 hours. My 803 is a 2000 non-reset unit, so most of the nuts are not caged. I went ahead and installed rivnuts, which led to a little extra work that is not necessary to complete the fuel line repair. Here is some of what I did:

    1. remove all of the bolts from the rear panel to get access to the fuel tank to remove/connect the old/new fuel return line
    - the bolts along the bottom have nuts on the back side, all other nuts are caged
    2. remove all of the bolts from the top cover
    - all bolts going into the radiator area are caged
    - most others came off using an light weight impact driver and holding the nut with my fingers
    3. remove front top cover to get access to the support that the front and rear top cover mount to
    - there are only about 10 bolts to get this off, one of them is caged, the rest are bolt and nut
    - the panel cover has to come off and most of the screws broke off while attempting to remove them

    With all of these covers off, locating and removing the fuel return line is easy. My old fuel line pulled apart and came out easily. Getting the old hose off of the Tees required a little more effort, though. I simply took the section of Tees out as a whole line, and rebuilt it on my workbench using the 3.2mm gates hose. The hose was rather tight and I used some WD-40 to lubricate the ends while reassembling. I also had to use a towel and a air of pliers to hold and twist each piece to a secure connection. No hose clamps are required. Once pieced together, I strung the new Tee section back on top of the engine and, using WD-40 again, was able to put the hose onto the return barbs. After getting all the hose connected, I fired up the generator and watched for 5 minutes to verify that there were no leaks.

    With all of the panels off, I was easily able to install the rivnuts. I used Astro Pneumatics 1442 rivnut setter, with a 10-32A mandrel to install the aluminum rivnuts. You will want to use aluminum rivnuts to avoid galvanic corrosion(dissimilar metals). For bolts, I reinstalled the original bolts as they are, I believe, plated to prevent galvanic corrosion. I stripped a few, and broke many of the screws that attach the control panel cover and will be replacing those with zinc plated 10-32 bolts/cap head screws. From what I've gathered, zinc has a lower instance of galvanic corrosion with aluminum, and the plating prevents the steel from contacting the rivnut.

    When installing the rivnuts, I found that installing the rivnut on the tool fully would make it easy to over-pull the rivnut, essentially stripping out the treads. The easy fix is to thread the rivnut onto the mandrel until only a few threads are still uncovered. This limits the full pull of the tool and still creates a strong bond on the rivnut. It did take some trial and error, but I had the process down after the third one. There were a handful of places where I could not install a rivnut due to the mounting hole interfacing with multiple panels, most notably on the front top cover, in which laces I simply reinstalled the bolt and nut.

    All said and done, from disassembly to fully reassembled, I finished this project in roughly three hours. I had put it off for fear of the hundreds of nuts and bolts that would be impossible to reach. After going through it, it is perhaps 40 total nuts and bolts to attack, many of the nuts are caged and therefore not a real problem. I suspect going back with nuts and bolts would have taken much longer than using rivnuts, though. The 1442 tool is overkill for aluminum 10-32 rivnuts, and you can easily strip them out, but it is easy to learn how to do it properly. I have other uses for the tool with larger rivnuts, so that is why I went with it. If you are just wanting to install rivnuts on your MEP, you should be able to get by with either a cheaper, lighter-duty, setter, or just use the bolt/nut/lockwasher method which is well documented in numerous youtube videos.
    I think you made a mistake putting back the original bolts into aluminum rivnuts. For all the work you did, you should have used all stainless replacement hardware. They are available from a couple of different sources and not expensive.

    You will get galvanic corrosion between plated steel bolts and aluminum rivnuts. Also use anti seize lubricant on everything during reassembly or you'll be breaking screws/bolts left and right in the future when they weld themselves together via corrosion.

    This subject has been covered in threads here on the board.
    Last edited by Farmitall; 05-15-2019 at 14:12.

  8. #87
    Colonel
    Join Date
    Sep 2016
    Location
    Tallahassee, FL
    Posts
    298
    Thanks
    92
    Thanked 162 Times in 103 Posts

    Default

    I did read up on the subject and zinc plated bolts are recommended compared to stainless. Though I'm planning to go back with the anti-seize.

    https://www.albanycountyfasteners.co...-and-aluminum/

    From Anode To Cathode

    To mitigate the effects of galvanic corrosion even further, it is recommended to use materials that are less likely to cause electron transfer when exposed to each other and an electrolyte. The following list is a list of materials. *Note: the closer the two metals on this list, the less likely they will be to suffer from the negative effects of galvanic corrosion.


    • Magnesium
    • Magnesium Alloys
    • Zinc
    • Beryllium
    • Aluminum Alloys
    • Cadmium
    • Mild and Carbon Steel, Cast Iron
    • Chromium Steel (With Less Than Or Equal To 6% Chromium)
    • Active Stainless Steels (302, 310, 316, 410, 430)
    • Aluminum Bronze
    • Lead-Tin Solder
    • Tin
    • Active Nickel
    • Active Inconel
    • Brass
    • Bronze
    • Copper
    • Manganese Bronze
    • Silicon Bronze
    • Copper-Nickel Alloys
    • Lead
    • Monel
    • Silver Solder
    • Passive Nickel
    • Passive Inconel
    • Passive Stainless Steel (302, 310, 316, 410, 430)
    • Silver
    • Titanium
    • Zirconium
    • Gold
    • Platinum

  9. The Following User Says Thank You to lonesouth For This Useful Post:

    Farmitall (05-15-2019)

  10. #88
    General
    Join Date
    Dec 2015
    Location
    Eubank, KY
    Posts
    429
    Thanks
    777
    Thanked 312 Times in 183 Posts

    Default

    Quote Originally Posted by lonesouth View Post
    I did read up on the subject and zinc plated bolts are recommended compared to stainless. Though I'm planning to go back with the anti-seize.

    https://www.albanycountyfasteners.co...-and-aluminum/
    Ok, my experiences have taught me different.

    You can't go wrong with the anti seize, you'll be glad you applied it.

Page 9 of 9 FirstFirst ... 5 6 7 8 9

Similar Threads

  1. Replies: 44
    Last Post: 10-05-2014, 23:00
  2. fuel return line
    By mikey in forum The Deuce
    Replies: 22
    Last Post: 10-02-2012, 17:08
  3. fuel return fittings
    By tiger422 in forum The Deuce
    Replies: 21
    Last Post: 06-29-2011, 15:02
  4. fuel return line?
    By Mikey90744 in forum The Deuce
    Replies: 11
    Last Post: 06-18-2011, 11:14
  5. fuel non return valve?
    By martinsaunders06 in forum 5-ton and up
    Replies: 4
    Last Post: 03-05-2008, 00:17

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •