Thread: MEP-803a Auto/Remote start module

  1. #1
    Sergeant
    Join Date
    Oct 2017
    Location
    Miami, FL
    Posts
    100
    Thanks
    64
    Thanked 7 Times in 6 Posts

    Lightbulb MEP-803a Auto/Remote start module

    I am currently laying the foundation for the concrete pad for my generator. Next I'm going to run 2 conduits from the pad to the service entrances (one for power and one for control cables.

    If if I had to guess, I'm running about 150' of conduit/cable. Was going to ask an electrician friend what gage wire to use for the power. But I doubt he would know what to use for the remote start/stop. Any suggestions? I was planning on 12/2.

    Purchasing a Kohler ATS with the remote switching control installed in the house. At a later time I might add the load shedding and go fully automatic. But for now, I'll have to manually shed the breakers and manually start the generator.

  2. #2
    4 Star General frank8003's Avatar
    Join Date
    May 2012
    Location
    Ft. Lauderdale, Florida
    Posts
    3,988
    Thanks
    2,809
    Thanked 6,276 Times in 2,148 Posts

    Default

    a question:
    One inch or bigger conduit and wire at five bucks a foot?
    I was here, had a good time.

  3. #3
    Sergeant
    Join Date
    Oct 2017
    Location
    Miami, FL
    Posts
    100
    Thanks
    64
    Thanked 7 Times in 6 Posts

    Default

    Not sure what you're question is?

  4. #4
    4 Star General
    Join Date
    Mar 2014
    Location
    Efland, NC
    Posts
    1,834
    Thanks
    459
    Thanked 1,429 Times in 837 Posts

    Default

    I'm a fan of doing a 4 pair, 18 GA shielded cable and a CAT6 in the control conduit. That will give you a number of control and monitoring options.
    Chris Medico
    MEP-003a (sold), MEP-803a, MEP-802a, & MEP-831a

  5. #5
    2 Star Admiral Daybreak's Avatar
    Join Date
    Mar 2015
    Location
    Northern, Virginia
    Posts
    1,266
    Thanks
    210
    Thanked 1,658 Times in 717 Posts

    Default

    Howdy,
    Any battery tender?
    ~~Later Mike

  6. #6
    4 Star General
    Join Date
    Mar 2014
    Location
    Efland, NC
    Posts
    1,834
    Thanks
    459
    Thanked 1,429 Times in 837 Posts

    Default

    Quote Originally Posted by Daybreak View Post
    Howdy,
    Any battery tender?
    Solar one even? That is a great application for solar assuming its not full time shaded. If it is shaded you can go with an oversized panel and still get plenty of energy to keep a battery topped up.
    Chris Medico
    MEP-003a (sold), MEP-803a, MEP-802a, & MEP-831a

  7. #7
    General
    Join Date
    Feb 2017
    Location
    NY
    Posts
    580
    Thanks
    41
    Thanked 328 Times in 225 Posts

    Default

    someone juse used a vehicle alarm system to do a remote start. With 150ft of conduit your prob really only 120ft from the generator. Vehicle remote should work.

  8. #8
    Sergeant Major
    Join Date
    May 2017
    Location
    DFW, Texas
    Posts
    120
    Thanks
    11
    Thanked 42 Times in 29 Posts

    Default

    That's a fairly long run. I would use 100 amp service entrance cable with 2/0 AL conductors. It is cheaper per foot than copper cable. Cat 5/6 for low voltage control cable.

  9. The Following User Says Thank You to eatont9999 For This Useful Post:

    Guyfang (11-21-2017)

  10. #9
    Sergeant
    Join Date
    Oct 2017
    Location
    Miami, FL
    Posts
    100
    Thanks
    64
    Thanked 7 Times in 6 Posts

    Default

    Electrician says it's a 120ft run. Says I can use #6 copper and #8 for ground. I should be good up to 75amps. The 803a rated at 52 amps.

    But since i ran 1-1/2" conduit, i have the option of #4 for my legs and neutral and #6 for ground. Says it will cost more and be more difficult to pull through conduits. But if I ever want to go larger on a generator, I'd be fine for 21kw.

    I still have to run a conduit for the CAT6 control cable ...even though I have outdoor/UV rated cable. I was considering zip-tieing the CAT6 cable under the 1-1/2" PVC conduit. IMG_2402.jpg

  11. #10
    Sergeant Major
    Join Date
    May 2017
    Location
    DFW, Texas
    Posts
    120
    Thanks
    11
    Thanked 42 Times in 29 Posts

    Default

    Quote Originally Posted by TheAlfredo View Post
    Electrician says it's a 120ft run. Says I can use #6 copper and #8 for ground. I should be good up to 75amps. The 803a rated at 52 amps.

    But since i ran 1-1/2" conduit, i have the option of #4 for my legs and neutral and #6 for ground. Says it will cost more and be more difficult to pull through conduits. But if I ever want to go larger on a generator, I'd be fine for 21kw.

    I still have to run a conduit for the CAT6 control cable ...even though I have outdoor/UV rated cable. I was considering zip-tieing the CAT6 cable under the 1-1/2" PVC conduit. IMG_2402.jpg

    52 Amps assuming you have each leg perfectly balanced. These sets are known to be able to handle 135% or more load, so the cable could see more than 52 amps per leg. De-rate your cable to 80% to meet NEC code for bundled conductors over 24" in length. This puts #6 CU at 60A. Also remember that over 120ft, the resistance in the cable builds up more than a short run.

    #6 CU cable only supports up to 75 amps if it is 90C rated. Not sure what you have as far as brand, type, rating, etc.

    You can de-rate the neutral conductor size to be no less than 40% of the size of the current-carrying conductor. You see service entrance cable sold in 4/0, 4/0, 2/0; the 2/0 conductor being the neutral.

    At 6 AWG, you can expect a 3% voltage drop at 120ft. 240V would be 232.8V by the time it gets to the panel. It is up to you how much drop is acceptable.

    Check this out.

    http://wiresizecalculator.net/

    http://www.barr-thorp.com/wp-content...nec-tables.pdf

  12. The Following 2 Users Say Thank You to eatont9999 For This Useful Post:

    1800 Diesel (11-22-2017), Zed254 (11-22-2017)