MBU V3 Error 3
SCSG-G4
PSVB 3003
5,393
3,462
Lexington, South Carolina
Do you have the TM's for it? Has it run right before?
@SCSG-G4
Table 1. Controller Error Codes.
Code Meaning Suggested Action
ER01 No Flame or flameout
See troubleshooting procedure “Burner fails to start or shuts
down during operation.”
ER02 Overvoltage Check voltage at power source. Check cables and connections
between power source and MBU.
ER03 Undervoltage Check voltage at power source. Check cables and connections
between Power source and MBU.
ER04 Tank not full after
four minutes of
fueling
See troubleshooting procedure “MBU fails to refuel.”
ER05 Flame detected If there is a flame in the burner (when there should NOT be), then
extinguish it, or allow to burn out before attempting to operate
burner again. If no flame is present, then check flame sensor.
All from TM 10-7310-281-13&P, page 89, Work Package 0008
If the TM is not in the TM section, I can upload it. Mike
Thorh
Kristiansund, Norway
four minutes of
fueling
I have the TM, i know err3 is undervoltage, but anoter MBU runs fine with the same power supply....