• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

MEP-003a Start failure

DMZ11b40

New member
7
0
0
Location
Columbus, Ohio
I purchased a MEP003a 10k generator and it ran fine until I pulled the emergency stop. Yes, the emergency stop does indeed work. However, now the unit cranks but will not start/run. Planning to soon pull injector pump (IP) and clean/blow out. Anyone have tips on the IP clean process or is there more to the emergency stop reset? Any suggestions will be appreciated. With winter coming getting a little here in central Ohio. Thanx
 
Last edited:

doghead

4 Star General /Moderator
Staff member
Super Moderator
Steel Soldiers Supporter
26,247
1,168
113
Location
NY
Do you mean 3KW generator, or do you have an mep-003a 10kw generator?
 

doghead

4 Star General /Moderator
Staff member
Super Moderator
Steel Soldiers Supporter
26,247
1,168
113
Location
NY
If you mean the DC circuit breaker(on the control panel), yes, push it back in , to reset it.
 
Last edited:

DMZ11b40

New member
7
0
0
Location
Columbus, Ohio
Yes the Emergency Shut Off on the control panel. I pushed it back in and unit failed to start. Must now check on fuel shut off solenoid from ESO to see if its operating. Previous thread indicated it occasionally sticks once activated.
 

Triple Jim

Well-known member
1,373
277
83
Location
North Carolina
Don't make more work for yourself than you have to. If pulling the stop breaker was the last thing you did before it failed to start, then look for a problem with the stop breaker. If it checks out with a meter, then move on.
 

MarcusOReallyus

Well-known member
4,524
811
113
Location
Virginia
Don't make more work for yourself than you have to. If pulling the stop breaker was the last thing you did before it failed to start, then look for a problem with the stop breaker. If it checks out with a meter, then move on.



Bingo.


The place you touched is the place to start looking.
 

DMZ11b40

New member
7
0
0
Location
Columbus, Ohio
Makes sense to me. Getting around now to head to where the generator lives and throw meter on pull stop. Just downloaded the manual. Will let all know how she runs. This happened in March and I forgot about it until Superstorm Sandy hit us. Thanx
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks