• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

MEP 804 A under voltage Issue

Scott Warren

New member
1
0
1
Location
Texas
Just purchased a MEP804A a few months ago, had installed a 30kv transformer as to keep unit 3 phase and be able to run single phase to house.
All was good until last week when I started unit and got a under voltage light on panel... Traced back to FU2 which was bad. Only porblem was when I pulled fuse I messed up label on fuse.
TM does not tell what size or amp fuse is...I can only make out 100kva and 500v... I replaced temporarily with a 20 amp fuse and all is running well, but I have read in other posts that it may only be a 3 amp fuse...
CAN ANYONE CONFIRM FUSE SIZE PLZ....THANKS IN ADVANCE
 

kloppk

Well-known member
Steel Soldiers Supporter
1,967
3,064
113
Location
Pepperell, Massachusetts
FU2 would be a 3 amp fuse.
KTK-3 I believe.
Replace the 20 amp one with a 3 amp or risk burning out the static exciter.
If FU2 blew it may be a sign your AC Voltage Regulator is failing. Normally FU2 should not blow unless there is an issue.
 
Last edited:
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks