MEP-804A won't stay running

blhar15

Active member
117
5
28
Location
Waterloo, IA
I have a nice condition MEP-804A 15KW generator that I am having issues with. First off we have to jump it every time, so I know it needs batteries. However, when we hook up the jumper cable it starts fine, but when you release the starter switch it stops running. Any ideas?

Thanks
 

jamawieb

Well-known member
1,412
512
113
Location
Ripley/TN
Oil pressure switch, are you getting any fault indicators? I mean, we can all guess at different things. Is the fuel cut solenoid being activated when it shuts down or does it sound like it's starving for fuel?
 

Guyfang

Moderator
Staff member
Moderator
15,855
22,040
113
Location
Burgkunstadt, Germany
You may not need batteries. First off, what kind of batteries are they?

Try this. Start the set, hold the S-1, (start switch) up and don't let go yet. Turn the S-7 Battle short switch on and then let S-1 go. What happens? Continue to run? or not?
 

Guyfang

Moderator
Staff member
Moderator
15,855
22,040
113
Location
Burgkunstadt, Germany
In all probability, you just didnt hold S-1 up long enough for the oil pressure to build up and close the contacts in the LOP, (Low Oil Pressure) switch. Glad that's all it was! What engine you have in it?
 

Newgen

New member
1
0
0
Location
El paso
Hi I’m new to this site and was wondering what if after I turn the s7 on it still won’t stay running? What should I look at next?
 

Guyfang

Moderator
Staff member
Moderator
15,855
22,040
113
Location
Burgkunstadt, Germany
Like Zed told you, get the TM's downloaded.

Now, we need info.
Is this set new to you?
Have you ever seen it run right?
When you have in in emergency by pass, (S7 up, S1 down) are any idiot lights on?
Have you read the trouble shooting guide for the problem?

We need to know where to start. Your answers make it easyer to do it.
 

sportman

New member
12
5
3
Location
miami, florida
Hello folks I'm new at this forum need to see if I can get some technical assistance. Last May of 2019 I purchased an MEP804-a through Iron Planet picked it up in PA. I changed the oil filter put fresh oil, fuel filter, water separator filter and cleaned the fuel tank that had some slime at the bottom of the tank. The unit when turning the S1 switch to preheat you would get no response if turn it to start run it would run but release it quit I did see the oil pressure gauge work but no power to the panel lights. I read that the blue S1 switch are a problem. I ordered the S1 from Electroswitch #75902LV now I have power to the panel but one question I have to what #'s to connect the jumper wire in witch direction is the current is to flow. I had connected it the wires to the same location than the blue switch but still when the star switch release it quit running. Now the overspeed idiot light would come on when you hold the start and run. Any assistance would be greatly appreciated.. Thanks
 

Guyfang

Moderator
Staff member
Moderator
15,855
22,040
113
Location
Burgkunstadt, Germany
Hello folks I'm new at this forum need to see if I can get some technical assistance. Last May of 2019 I purchased an MEP804-a through Iron Planet picked it up in PA. I changed the oil filter put fresh oil, fuel filter, water separator filter and cleaned the fuel tank that had some slime at the bottom of the tank. The unit when turning the S1 switch to preheat you would get no response if turn it to start run it would run but release it quit I did see the oil pressure gauge work but no power to the panel lights. I read that the blue S1 switch are a problem. I ordered the S1 from Electroswitch #75902LV now I have power to the panel but one question I have to what #'s to connect the jumper wire in witch direction is the current is to flow. I had connected it the wires to the same location than the blue switch but still when the star switch release it quit running. Now the overspeed idiot light would come on when you hold the start and run. Any assistance would be greatly appreciated.. Thanks
Partner, Please start your own thread. When you start in here, its hard for people to keep whats, what, straight. You will get much more help with your own thread. If you need help starting a thread, then let us know and someone will walk you through it.
 

sportman

New member
12
5
3
Location
miami, florida
Partner, Please start your own thread. When you start in here, its hard for people to keep whats, what, straight. You will get much more help with your own thread. If you need help starting a thread, then let us know and someone will walk you through it.
Thank you Guyfang
 

sportman

New member
12
5
3
Location
miami, florida
Like Zed told you, get the TM's downloaded.

Now, we need info.
Is this set new to you?
Have you ever seen it run right?
When you have in in emergency by pass, (S7 up, S1 down) are any idiot lights on?
Have you read the trouble shooting guide for the problem?

We need to know where to start. Your answers make it easyer to do it.
Thanks for replying Guyfang; I will check this weekend for the idiot lights. The unit is new to me since day one when I crank it up before changing the S-1 switch had no power to the panel and yes hold the switch to start and starts up nicely release and it quit. That's why I replaces S-1 switch, now I have power to the panel and glow plugs. I haven't down loaded the TM just looked at the diagram on the generator door panel. I will down load the TM and see where it will lead to.
 
Top