• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

803a first time (for me) under a load

k9medic

Member
96
14
8
Location
Florida
I finally got everything running on the 803a so I figured I would hook it up to the house to see what it would do.

After wiring everything up, I started slowly flipping breakers on to put a load on the generator. Eventually I had all of the breakers on to include the Air conditioner which has a RLA of 78. The fan was not spinning as fast as it normally does though.

Here is what I found:
  • AC circuit interrupter switch light would not go out and I still have voltage on the lugs. I can hear the relay "click" when I try to open the relay but nothing happens.
  • AC load gauge does not seem to work. I had a decent load on the generator and the needle didn't move. The engine didn't bog down either.
  • The following gauges don't work - fuel, oil pressure, temperature

For the circuit interrupter, this is a new issue. Yesterday it worked. Today it does not disconnect.

Thoughts?
 

fa35jsf

Active member
135
31
28
Location
OKC, OK
Maybe it’s sticky. Mine wouldn’t connect when I first bought it. Had to hit it with the handle of a screw driver. Then I took it apart and cleaned it.


Sent from my iPhone using Tapatalk
 

k9medic

Member
96
14
8
Location
Florida
Ugh... Now I am getting a contactor trip overload light at well with no load applied. Just running it comes on.
 
Last edited:

k9medic

Member
96
14
8
Location
Florida
Yeah, I disconnected it. This is very frustrating!

Just pulled the AC relay. Full of water. SMH.
 
Last edited:

Chainbreaker

Well-known member
1,748
1,834
113
Location
Oregon
I would be hesitant to check the machine hooked to the house...maybe get a load bank and work out the bugs...
He can assemble a quick load bank by utilizing a garage space heater like this. Just add an adequate cable and he's in business with two available load/heat settings. Also, these Comfort Zone heaters often go on sale from time-to-time around this time of year if you shop around.
 

Guyfang

Moderator
Staff member
Moderator
15,881
22,133
113
Location
Burgkunstadt, Germany
Yeah, I disconnected it. This is very frustrating!

Just pulled the AC relay. Full of water. SMH.
this is a common fault. Dry it in an oven, set to a VERY low temp. Then blow it out with air. Then bench test it. Apply 24VDC to the coil. Will the applying and removing VDC to the coil circuit open and close the relay? The st the output contacts with a multimeter set to ohm's. Test all three terminals. Then check the circuit for turning on the light. Same way. Activate the coil. If it all works, put it back together and hook it up. Then start the set, and then test it again by starting it up, opening and closing the relay. Light has to come on, turn off and you should get power at the lugs. I would have given you wire numbers, but am not home to look at schematics.
 

k9medic

Member
96
14
8
Location
Florida
Thank you.

I ran the test on the relay before I pulled it and it failed which is what prompted me to pull it.

When I applied 24v to X I got a “clunk.” When I activated the s5 to open I got a clunk but no changes. When I switched to closed there was no change.

I removed it, sprayed it down with wd-40 and blew it off with a compressor. I’m going to get some context cleaner today and try to salvage it.

If not, a new relay is in my future...


Edited - sprayed relay down and retested. Tested good. Reinstalled - works as advertised.

Sent from my iPhone using Tapatalk
 
Last edited:
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks