Yeah I have the same plate I guess now I'm just curious as to why it has a plate showing it can do 480. Or am I understanding it wrong?
The voltage adjust rate is the range the voltage adjust rheostat can adjust the output voltage in general.
Its 395 VAC on the low side and 480 VAC on top side. Both are the absolute maximum and minimum ratings of adjustable range.
When the A1 / A11 start to go bad, then the range indicated on name plate can no longer be achieved, resulting in preventive maintenance.
The rating is 416 VAC or 208 VAC, that is what the Generator Head is designed and built for.
Operating the Generator at any other Voltage then 208 VAC or 416 VAC can cause problems and premature equipment failure.
The A1 / A11 is the number one casualty, then the exciter coil assembly and its Diodes
Its up to the operator to make the judgement call and carry the responsibility when operating at extreme limits.
Because of the age and the aging of the components in the A1 / A11, most units won't go higher then ~ 440 to 450 VAC