• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

A/C new install

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
OK, new A/C install with gen2 evaporator, high side 225, low side 25, what should air from evap be? I barely get 65°. R134A
 

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
Nope, that's not it. Same temp readings as 4 lb charge and 5 lbs. Pressure was too high at 275 and 45 so I went down to 4 lbs and high side is 200 but low side is 25, way to low for 134. Still blows 65° at 82° ambient. New gen 2 unit has been sitting for years.
 

Ronmar

Well-known member
3,188
6,477
113
Location
Port angeles wa
Low coolant or low coolant flow. Since your testing shows it isnt low coolant and with the high pressure split, Perhaps the TRV(Or somewhere else in the circuit) has an obstruction Which isnt letting the refrigerant flow properly... Are the condenser fans operating and giving good flow thru the condenser?
 
Last edited:

simp5782

Feo, Fuerte y Formal
Supporting Vendor
12,091
9,248
113
Location
Mason, TN
Not enough air across the condenser.

I assume its 65 at idle sitting in the driveway? Not at road speed?

Did you insulate your ac hoses? This will help a ton and drop temps by about 15 degrees.

Or switch to R12. I did. 48 degrees at 92 ambient with 70% humidity
 

Attachments

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
Low coolant or low coolant flow. Since your testing shows it isnt low coolant and with the high pressure split, Perhaps the TRV(Or somewhere else in the circuit) has an obstruction Which isnt letting the refrigerant flow properly... Are the condenser fans operating and giving good flow thru the condenser?
Inlet to condenser is very hot, outlet is almost at ambient temp so condenser is doing a great job, it is a very large condenser. 968 square inches. Air from evap is same temp regardless of engine rpm. I feel like the expansion valve is restricting the flow to much but everything is new.
 

Ronmar

Well-known member
3,188
6,477
113
Location
Port angeles wa
Inlet to condenser is very hot, outlet is almost at ambient temp so condenser is doing a great job, it is a very large condenser. 968 square inches. Air from evap is same temp regardless of engine rpm. I feel like the expansion valve is restricting the flow to much but everything is new.
Well you could pull the TRV, warm its bulb and back-flush it with compressed air...
 

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
Yes it seems like it must be restricted. I suppose I could just take the lines off under the cab and do it there since the cab temp is at least 100°!! Maybe I could catch something coming out the inlet.
 

MAdams

Active member
373
123
43
Location
San Dimas, CA
I'm having the same problem on my 7 ton. Low side pressure is 18psi, warm outlet air from evap and I charged the system to the correct 2.25lbs of 134a. I think my TXV is either bad or possibly backwards if that's possible. I didn't have the correct high side adapter for my gauge set

Sent from my SM-G975U using Tapatalk
 

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
I started taking the case apart in the truck and the first thing I found was 34° at the header feeding the coil. And it looks like they allowed a huge amount of air to just go around the coil on the ends. I have 30 of these units so tomorrow I am going to take another apart to see how it was made. On the LMTV does the A/C only work on recirculate? Heater hoses are both cold so that is good. If I move the TXV bulb to a warmer spot the low side should come up meaning more refrigerant being fed to coil, right? And using more should lower high side?? As I said, my condenser is huge, my thought being to small is bad but never can be to big. Normal system holds 4.2 lbs?? So I figured 5 lbs, pressure will tell.
 

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
Well air going around the evap isn't being chilled:)
Exactly. Now I am not yet positive of this but will know tomorrow. What do you think about relocating the TXV bulb to trick it into opening more? I would know if it works by the low side pressure.
 

MAdams

Active member
373
123
43
Location
San Dimas, CA
Post a picture of your txv. I just found out some are adjustable with a brass screw on the bottom

Sent from my SM-G975U using Tapatalk
 

Third From Texas

Well-known member
2,700
6,312
113
Location
Corpus Christi Texas
I'm kinda surprised that the gen2 kits hadn't ironed out these sort of issues.

I've been going back-and-forth with just building a system from scratch or using a surplus kit for simplicity. I know all the bits that I need, and where I can get the civilian equivalents but I figured that the surplus kit would be more plug-n-play friendly.

Now I'm not so sure.

Following
 

Ronmar

Well-known member
3,188
6,477
113
Location
Port angeles wa
Well if you can get all the air to pass thru the evap, you shouldn't have to relocate the bulb... one of the main functions of the TRV and its temp sensor/bulb is to keep the evap from freezing the condensed water On the evap...
 

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
OK, found 3 things. There is a baffle so all the air does go through the evaporator coil. The A/C only works on recirculate. It does NOT use a TXV, it is an AXV. I think this was a very bad decision since with a high heat load it will actually cool less.
 

Ronmar

Well-known member
3,188
6,477
113
Location
Port angeles wa
Ok, well an AXV simply maintains outlet pressure on the evap. So either it is set too low(sure there isnt an adjustment screw on it, that is usually how the low pressure is set to match the flow). Or something else in the system is restricting the flow or the compressor isnt working to spec and the AXV is regulating the evap outlet pressure accordingly. Or it is broke/clogged...
 

m-35tom

Well-known member
Supporting Vendor
3,020
220
63
Location
eldersburg maryland
Ok, well an AXV simply maintains outlet pressure on the evap. So either it is set too low(sure there isnt an adjustment screw on it, that is usually how the low pressure is set to match the flow). Or something else in the system is restricting the flow and the AXV is regulating the evap outlet pressure accordingly. Or it is broke/clogged...
Would you agree that a TXV works much better than an AXV? There is a plug on the bottom of the block opposite the control diaphragm. Air out should be at least as low as 40° and maybe as low as 30° in my view. My car is 41° my M35 was 28°, all with 134A
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks