hurst01
Member
- 76
- 1
- 8
- Location
- Jeffersonville, Indiana USA
I just recently picked up another MEP002A 5 KW from GL that was listed as B4. This translates into "Serviceable, for issue condition". Yeah, Right!
I went to pick it up and it looked really good, even had batteries and over half tank of fuel. The batteries are from 2004 and of course were bone dead. Surprisingly enough, I charged them for almost three days and they came up and turn pretty decent. I can't trust them to hold up though so I will replace them.
Again, no fuel at the injectors. I pulled the cap on the head of the IP, took out the delivery valve and tapped lightly on the plunger with a flat ended punch and hammer. Surprisingly enough it moved. I disconnected the fuel pumps and hit the starter briefly. It stuck again. After about 10 times it finally stayed in against the cam. Put everything back together and it took a bit but it started. It sounded really good with no smoke at all. I throttled it down to shut it down to change the voltage to 220 single phase. It died before I could shut it off. I was able to start it again and it ran for about three minutes and then sounded like it was going to come apart. It started puffing blue smoke and rattling with a lot of vibration.
I put some fuel injector cleaner in the tank and ran it a bit longer. It is not very responsive at all. I could throttle it down and bit and then throttle it up and it was very noisy with lots of smoke. Kind of sounded like it was running on only one cylinder instead of two. I guess I will have to pull the IP and clean it good.
Has anyone ever cleaned the injectors on one of these gensets? When it does start, it takes a very long time to fire off.
It has 557 hours and I believe them to be original from the way it looks. I even got the paperwork and some logs with it. When I went to pick it up I looked at several more that was ending that day. They were listed as F7 and H7 and looked every bit as good or better than mine. Some even had batteries and fuel in the tanks. A 10KW only had 207 hours and even looked better than mine. If I had about $5K to spare at the time I could have had several really good generators.
Ed
I went to pick it up and it looked really good, even had batteries and over half tank of fuel. The batteries are from 2004 and of course were bone dead. Surprisingly enough, I charged them for almost three days and they came up and turn pretty decent. I can't trust them to hold up though so I will replace them.
Again, no fuel at the injectors. I pulled the cap on the head of the IP, took out the delivery valve and tapped lightly on the plunger with a flat ended punch and hammer. Surprisingly enough it moved. I disconnected the fuel pumps and hit the starter briefly. It stuck again. After about 10 times it finally stayed in against the cam. Put everything back together and it took a bit but it started. It sounded really good with no smoke at all. I throttled it down to shut it down to change the voltage to 220 single phase. It died before I could shut it off. I was able to start it again and it ran for about three minutes and then sounded like it was going to come apart. It started puffing blue smoke and rattling with a lot of vibration.
I put some fuel injector cleaner in the tank and ran it a bit longer. It is not very responsive at all. I could throttle it down and bit and then throttle it up and it was very noisy with lots of smoke. Kind of sounded like it was running on only one cylinder instead of two. I guess I will have to pull the IP and clean it good.
Has anyone ever cleaned the injectors on one of these gensets? When it does start, it takes a very long time to fire off.
It has 557 hours and I believe them to be original from the way it looks. I even got the paperwork and some logs with it. When I went to pick it up I looked at several more that was ending that day. They were listed as F7 and H7 and looked every bit as good or better than mine. Some even had batteries and fuel in the tanks. A 10KW only had 207 hours and even looked better than mine. If I had about $5K to spare at the time I could have had several really good generators.
Ed