• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

Looking For Opinions On This Transfer Switch

CT-Mike

New member
238
2
0
Location
CT
So I have finally decided to pull the trigger on a -003 or -803 in an upcoming auction.

I am am wondering if this transfer switch setup would be sufficient for one of these 10KW generators:

http://www.electricgeneratorsdirect.com/Reliance-Controls-EGD-Q510KIT/p13512.html

Would I be better off just going with a 200A service rated DPDT and do manual load management?

I have a 200A service with two heat pumps, two fridges, well pump, and a chest freezer for large loads. Heat and hot water are via a propqne boiler so minimal current draw there.

I also have a hot tub but I know that I would have to seriously step up the generator to be able to power that monster (7.5 KW total heater load and 3 2.5 HP pumps).

Thanks,

Mike
 
Last edited:

CT-Mike

New member
238
2
0
Location
CT
I'm not against an 805, it would be much easier for the wife if she loses power in the middle of the night when I'm at work.

I guess I will have to see how the outcome of this auction goes.
 
Im wondering why load management is an issue as your just switching where the power comes in from I think of it as a water valve in all your doing is diverting the flow of power from power line feed to generator feed right?

So whats wrong with just using the same breakers that the powerline feed made use of down stream from where the power comes in ie just past the --< split
 

CT-Mike

New member
238
2
0
Location
CT
Bunkerbuilder,

If I go with an -803, load management is clearly an issue. It would be easiest to install a 200A DPDT manual transfer switch between my meter and service panel and use the existing breakers.

But if you look at what I listed for loads (forgot to mention electric range and dryer), there is no way for a 10KW genny to power all of that.

By load management I meant manually stripping off loads like the range, dryer, hot tub, and maybe one of the heat pumps before transferring to generator power.
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,482
1,879
113
Location
Efland, NC
If you think the generator will be used by someone that doesn't understand load management then absolutely put in a generator load center that properly segregates what the generator can support.
 
Well no not power everything at the same time.


You Can't Plug in a 2 with a 6.

This automatically came to mind.

http://ia.media-imdb.com/images/M/M...MDU4OTU2MjE@._V1_SY264_CR87,0,178,264_AL_.jpg

http://m.imdb.com/title/tt0592812/



Bunkerbuilder,

If I go with an -803, load management is clearly an issue. It would be easiest to install a 200A DPDT manual transfer switch between my meter and service panel and use the existing breakers.

But if you look at what I listed for loads (forgot to mention electric range and dryer), there is no way for a 10KW genny to power all of that.

By load management I meant manually stripping off loads like the range, dryer, hot tub, and maybe one of the heat pumps before transferring to generator power.
 

PeterD

New member
622
6
0
Location
Jaffrey, NH
So I have finally decided to pull the trigger on a -003 or -803 in an upcoming auction.

I am am wondering if this transfer switch setup would be sufficient for one of these 10KW generators:

http://www.electricgeneratorsdirect.com/Reliance-Controls-EGD-Q510KIT/p13512.html

Would I be better off just going with a 200A service rated DPDT and do manual load management?

I have a 200A service with two heat pumps, two fridges, well pump, and a chest freezer for large loads. Heat and hot water are via a propqne boiler so minimal current draw there.

I also have a hot tub but I know that I would have to seriously step up the generator to be able to power that monster (7.5 KW total heater load and 3 2.5 HP pumps).

Thanks,

Mike
I have a similar transfer switch (I have both a 10 circuit and a 6 circuit one, and use both) and I'd strongly recommend a proper transfer switch over this system. Yes, it works, but I'm not 100% comfortable with it now that it is done. In fact, I now have a proper transfer switch, and when I do a rewire of my circuit box next summer (I hope) I will include the new transfer switch (and a conversion of my MEP-004 to single phase) and have a setup that is better.
 
Last edited:

DieselAddict

Well-known member
Steel Soldiers Supporter
2,482
1,879
113
Location
Efland, NC
During emergencies you can disconnect the defrost and emergency heat coils so you don't OL the generator during the defrost cycles. The HP will blow cold air during the defrost cycle but won't be harmed.
 

m16ty

Moderator
Moderator
Steel Soldiers Supporter
9,576
210
63
Location
Dickson,TN
I've got a 2,000 sq ft house 200amp service, gas heat, gas hot water, gas dryer. Everything else is electric.

Just for fun, I hooked up the MEP-003a, turned every light in the house on, and turned on the range. The fridge and the deep freeze were also running. The MEP handled it fine. I don't think I need to worry about load management.

When warm weather gets here I'm going to try a test with the A/C. I suspect I may have to do some managing then but it will be something as simple as not to run the range when the A/C is on.
 

rhurey

Member
Steel Soldiers Supporter
737
13
18
Location
Bothell, WA
During emergencies you can disconnect the defrost and emergency heat coils so you don't OL the generator during the defrost cycles. The HP will blow cold air during the defrost cycle but won't be harmed.
Yeah. but I gotta open the air handler to do that. Our fan and one bank of heat coils share a circuit. Not a wife compatible option.
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,482
1,879
113
Location
Efland, NC
Yeah. but I gotta open the air handler to do that. Our fan and one bank of heat coils share a circuit. Not a wife compatible option.
Install a switch you can reach on the outside. The coil side of the relay is low current.
 

CT-Mike

New member
238
2
0
Location
CT
For the heat pumps... is the defrost heat supplied by propane?
I don't use the heat pumps for heat in the winter time. I have large pellet stoves upstairs and down to handle winter heat. I am more concerned about having AC in the summer - SWMBO has severe asthma and heat and humidity is a trigger for her.
 

Ratch

Member
586
5
18
Location
Chester County, PA
I would not use that switch, the 50amp, with a 10kw genset for my house. It is a good way to control load, but with a 10kw generator that can overload to 13 or so, I'd use a 100amp switch minimum and maximize what you can get from it without tripping a breaker or potentially overheating the switch.
If you're willing to rewire your emergency circuits to that switch, you could get a standard service rated switch and a separate emergency panel. So you'd split your utility feed to two panels. One is normal loads, the other emergency. Put the switch between the split and the emergency panel.
I don't know if you can do all that for under $660, but used equipment is not bad if it works well.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks