Howdy,

Part of the BII list a grounding stud which was supposed to be installed. The manuals show 2 locations to which it can be installed.
Trailer grounding stud 1.jpg

Front right corner
Trailer grounding stud 2.jpgTrailer grounding stud 3.jpg

Where it is going on this unit
Trailer grounding stud 4.jpgTrailer grounding stud 5.jpg
 

JRM

Member
166
9
18
Location
Brightwood, Oregon
I was wondering about this, my 803A is in the back of my Toyota that has a plastic bed liner- is the house ground enough or should I ground the MEP as well?
IMG_20160403_133727.jpg
 

Daybreak

2 Star Admiral
Steel Soldiers Supporter
1,521
740
113
Location
Va
I was wondering about this, my 803A is in the back of my Toyota that has a plastic bed liner- is the house ground enough or should I ground the MEP as well?
View attachment 624368
Howdy,
If you have it connected to house, then you should have a 4-wire connection. The bonding connection should be disconnected.

The grounding stud is meant for a ground connection for the trailer as it continues on to the ground stud in the generator.

PU-797A = 5kw on LTT-TQG
PU-798A = 10kw on LTT-TQG
 

Guyfang

Moderator
Staff member
Moderator
15,676
21,604
113
Location
Burgkunstadt, Germany
You can and should run a ground wire from the gen set to a ground rod, driven into the ground. Using the ground from the house is fine, but wha happen, say when your cable to the house is damaged, and you have no ground from the house? The gen set should always have its own ground.
 

MtnSnow

New member
1,466
14
0
Location
NSL, UT
The gen set should always have its own ground.
Not true here in the USA as that is usually contrary to electrical codes when used as a home backup power source. Yes, a ground rod should be used when operating the generator out in the field.
 

Daybreak

2 Star Admiral
Steel Soldiers Supporter
1,521
740
113
Location
Va
Howdy,
OK,

In the field,
ground rod in the ground and connected to generator ground, neutral-ground bond connection in place

To a house,
you are using your panels grounding system, 4-wire connection to your panel, neutral-ground bond disconnected.
 

Daybreak

2 Star Admiral
Steel Soldiers Supporter
1,521
740
113
Location
Va
Howdy,
I have a 6 awg wire which is hooked at the ground lug terminal which goes out to this ground stud placed on the corner of the trailer flat. The connection is actually at the mounting point on the bottom of the stud.
 