MEP -003 intermittent voltage on L1:L3 ....

Guyfang

Moderator
Staff member
Moderator
15,959
22,319
113
Location
Burgkunstadt, Germany
Guyfang,
I want to confirm something with you on this switch

-34, Pg. 6-16, Change 7, Table 6-5 ,
shows the switch, when in position 2 , the first layer of contacts all have continuity with each other , if one contact does not have or show continuity with the other two contacts , then the switch has rotated to far in rotation or a contact may be burned. (I would say this is probably the culprit.)
So taking it one step further , if one rotated the switch to the correct position so the first layer of contacts have continuity with each other then one could select position 2 and check all layers for continuity on the contacts layer by layer? (Correct)
Then do position 1 and then do position 3 to check for burned or non continuity where each layer shows 2 or more x's. (once again, correct)

Am I correct in my read of table 6-5?
 