Good Day: If your checks of all the external things does not provide the answer, you may have to carefully drill the rivets of the K8 to open it. Then you can see if things inside are in order, or overheated in a spot. POP rivet it closed if nothing found, or find short screws.
Seeing as I have a high voltage on terminal 3, to me, it is a definite cause and effect. Correct me if I am wrong, but to suspect K8, the voltages have to be correct...correct?
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
KloppK, question. Can I do a real time voltage reading on either side of R12 and R13 under a 5K load? (or 4K). If the resistors and the contacts are good, I should get the same reading on both, correct? If the contacts were bad, wouldn't I get a different reading on R13?
 

kloppk

Well-known member
Steel Soldiers Supporter
2,330
4,198
113
Location
Massachusetts
Correct. If the AC voltages to the K8 terminal pairs is less than 5.6 volts AC and you get an overload fault then I'd say K8 is bad. Since you are seeing voltage in excess of that then the issue is with the switch contacts, wiring or R12 or R13.
Yes, you would normally see the same AC voltage across R12 and R13 when running loaded in 120/240 mode.
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
Correct. If the AC voltages to the K8 terminal pairs is less than 5.6 volts AC and you get an overload fault then I'd say K8 is bad. Since you are seeing voltage in excess of that then the issue is with the switch contacts, wiring or R12 or R13.
Yes, you would normally see the same AC voltage across R12 and R13 when running loaded in 120/240 mode.
Ok. For that matter, I can take a voltage reading on either side of the contacts on K8. I've left the covers off the gen until I solve this mystery so I will see if I can spare a few minutes to test that. Thank you so much for the help!
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
I'd have another go at cleaning S8. Get the cleaner inside the switch contacts and work the switch aggressively, then spray it again!
It sounds like the last cleaning made an improvement to where you can now apply a 5K load, but can't sustain it indefinitely?
Sorry Ray. Just saw this. No, no real change. It's able to handle a 5K load for about 15 seconds. Long enough for me to take a reading. I am headed out now to take readings on either side of K8 and both burden resistors. I'll do it at a 4K load so I don't have to rush. First I have to find the alligator clips for my Fluke. Clipping one to terminal 4 of the overload will make my life easier.
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
More testing today. All tests done at 4K load. I switched my test lead from terminal 4 to terminal 3 on K8.

R12...6.8
R13...7.0
Terminal 14...6.8
Terminal 13...6.8

To me, that eliminates S8. As I understand this circuit, the voltage is an inductive current from the output of the generator. The burden resistors add a load to that circuit.

Because R12 and 13 are soldered, I can't isolate them to test. Looking closely it appears that they have been soldered in a non factory way. I don't belive in coincidences so I'm thinking someone's been down this road before.

My question is, what is my next step? Could is still be K8? It seems to be doing it's job because it opens the output contactor when it sees a high voltage. I'm confident is it not S8.

@kloppk, @Ray70
 
Last edited:

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
Since you have the same voltages across R12 and R13 I'd suspect one of those burden resistors failed and is open circuit.
Makes sense. I have to remind myself that I am dealing with low voltage inductive current. Before I see if anyone has a couple of burden resistors, I really should unsolder the both of them and test them. I will do that in the next couple of days and report back.
 

grywitt

Active member
Steel Soldiers Supporter
274
214
43
Location
Nm
I've found you can isolate the resistors by pulling the wires off k8 and unplugging J6. The component to component wire list they made sure helped when I was wanting to measure them. R10 goes to K8-1, R11 goes to K8-2, R12 goes to K8-3 and R13 goes through J6 so if you unplug that then the wire is isolated. It was the bottom wire on the K8 terminals when I checked them.
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
I've found you can isolate the resistors by pulling the wires off k8 and unplugging J6. The component to component wire list they made sure helped when I was wanting to measure them. R10 goes to K8-1, R11 goes to K8-2, R12 goes to K8-3 and R13 goes through J6 so if you unplug that then the wire is isolated. It was the bottom wire on the K8 terminals when I checked them.
It's funny I woke to see this! I was thinking about it last night and it occurred to me that all I need to do is remove the wires from K8, terminal 3 and I can test the resistors. I looked at the wiring schematic and didn't see J6. I'll be out there today and will check. I have the TM's so I'll check the wire list. Thank you!
 

grywitt

Active member
Steel Soldiers Supporter
274
214
43
Location
Nm
I've been dealing with a very similar issues with a 10k so I have been following this thread pretty close. I think i found my problem but I'm testing now to be sure. ( dirty contacts in K1 maybe )
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
I've been dealing with a very similar issues with a 10k so I have been following this thread pretty close. I think i found my problem but I'm testing now to be sure. ( dirty contacts in K1 maybe )
Interesting! No chance to isolate the burden resistors today. Had to pick up my 14 month old golden girl from our friends house where she got to spend 3 weeks with when she came into season. I have an apartment above me and the tenant has 2 intact boys. Not fair to make her jump through hoops so Winnie took a nice vacation. Things are settling nicely so I will finish up testing the resistors tomorrow. Of course I will post the readings
 

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
I've found you can isolate the resistors by pulling the wires off k8 and unplugging J6. The component to component wire list they made sure helped when I was wanting to measure them. R10 goes to K8-1, R11 goes to K8-2, R12 goes to K8-3 and R13 goes through J6 so if you unplug that then the wire is isolated. It was the bottom wire on the K8 terminals when I checked them.
I've been looking but cannot find J6. What and where is it? (I feel stupid for asking!)
 

grywitt

Active member
Steel Soldiers Supporter
274
214
43
Location
Nm
Interesting! No chance to isolate the burden resistors today. Had to pick up my 14 month old golden girl from our friends house where she got to spend 3 weeks with when she came into season. I have an apartment above me and the tenant has 2 intact boys. Not fair to make her jump through hoops so Winnie took a nice vacation. Things are settling nicely so I will finish up testing the resistors tomorrow. Of course I will post the readings
I'm sure you will get it figured out. I've ran 3 hours at full load and am 40 minutes into 11kw of load plus I'm at 3000 feet elevation so I feel pretty confident that was it. I'll post my findings also just for help for the next person chasing this issue. This thread helped me a lot.

BTW J6/P6 is right above the storage container door. You unplug it from underneath the control box. Once unplugged R 13 is isolated on one end. I'll be interested to find out what your issues is.
 

Guyfang

Moderator
Staff member
Moderator
18,136
27,237
113
Location
Burgkunstadt, Germany
Look in the control panel. The plugs are on the Bottom of the control panel.

First take the wire off K8-3, and measure from there to the Burden Resister. If you get nothing, then unscrew P6. Look at the schematics to see what pins to check in P6/J6.

P6/J6 can also be loose, or have a bent/burnt pin. Open the lower door s lay on your back with a light and inspect.
 

Attachments

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
I'm sure you will get it figured out. I've ran 3 hours at full load and am 40 minutes into 11kw of load plus I'm at 3000 feet elevation so I feel pretty confident that was it. I'll post my findings also just for help for the next person chasing this issue. This thread helped me a lot.

BTW J6/P6 is right above the storage container door. You unplug it from underneath the control box. Once unplugged R 13 is isolated on one end. I'll be interested to find out what your issues is.
Thank you. If my testing doesn't reveal a smoking gun, I'll be reading what you did with great interest.
 
Last edited:

Summerpaws

Active member
Steel Soldiers Supporter
97
207
33
Location
Hampton, NH
Look in the control panel. The plugs are on the Bottom of the control panel.

First take the wire off K8-3, and measure from there to the Burden Resister. If you get nothing, then unscrew P6. Look at the schematics to see what pins to check in P6/J6.

P6/J6 can also be loose, or have a bent/burnt pin. Open the lower door s lay on your back with a light and inspect.
Thanks Guy. I got it now. It's nice when I have more things to check/test. I'm sure I will solve this problem. The TM you attached is the one I know I downloaded but couldn't find. I did download the wire list but not all of it. I'm not blaming the computer, just the stoopid human punching the keys. Hopefully I will have a good report tomorrow.
 