MEP 803 10 kw Will not start from S1 on panel

Tugood

New member
4
8
3
Location
Florida
My military MOS was 52 B 20 Generator operator mechanic. That was roughly 48 years ago. Yes, I can read a schematic. Generator is new to me, and it will start and run in battle mode if I hold the magnetic plunger back in the retracted position. I was reading an old post on this non start issue and traced a 24-volt reading as far as the S1 switch. I have 24 volts up to the S1 on 2 and 4 but not on 6 and 8 terminals. Thanks for your response. I recently purchased the technical manual dated 20 October 1983 also identified as TM56115-585-24P. I am unaware of downloadable TM's. I have only started and run the genny for a short period of time as oil pressure gauge does not register and I am assuming that is part of the electrical issue. I plan on installing a direct oil pressure gauge as a secondary confirmation of pressure. Any assistance would be greatly appreciated. Jack.

 

Guyfang

Moderator
Staff member
Moderator
17,802
26,596
113
Location
Burgkunstadt, Germany
Jack,

We may know one another! I too started out as a 52B20.

I have to run, but, if you have 24 volts on S1-2 & S1-4, you have to have voltage on S1-6 & S1-8, unless the S1 jumpers are missing. The first two versions of S1 had the jumpers external, the third version had them built in. So test again, in the run position. If still no joy, then the jumpers are missing. I have to go now to work. Later,

Guy wiltfang
 