MEP 803a generator.

Sapporo

New member
11
5
3
Location
Alaska
First off thanks for having me. I recently bought an MEP 803 a generator. Frequency meter is reading low but I noticed on the gauge at the bottom there's a screw. Can you turn that to adjust the dial to correct the meter reading. Thanks my name is Scott by the way.
 

Scoobyshep

Well-known member
914
989
93
Location
Florida
First off thanks for having me. I recently bought an MEP 803 a generator. Frequency meter is reading low but I noticed on the gauge at the bottom there's a screw. Can you turn that to adjust the dial to correct the meter reading. Thanks my name is Scott by the way.
Yes that can make minor adjustments. Use a multimeter to get an accurate reading. Be advised that the factory frequency meters are not the most robust

Sent from my SM-S908U using Tapatalk
 

Sapporo

New member
11
5
3
Location
Alaska
Yes that can make minor adjustments. Use a multimeter to get an accurate reading. Be advised that the factory frequency meters are not the most robust

Sent from my SM-S908U using Tapatalk
Okay I have set it at 61.5 frequency. Hopefully I can make the gauge read the same. Now that I know I can thanks a bunch.
 

Digger556

Well-known member
Steel Soldiers Supporter
232
534
93
Location
Denver CO
Welcome to the forums Scott.

Have you read through the TM yet? There is a procedure for testing that meter that measures the current from the transducer and compares it against the machine's frequency. It would be good to verify if the meter is off because of the meter or the transducer.
 

Sapporo

New member
11
5
3
Location
Alaska
Welcome to the forums Scott.

Have you read through the TM yet? There is a procedure for testing that meter that measures the current from the transducer and compares it against the machine's frequency. It would be good to verify if the meter is off because of the meter or the transducer.
No I haven't I'll look it up thank you.
 