Thanks for the reply Kloppk.
I guess I can use my fluke amp clamp to monitor both legs, but it seems like I could route the output from the CT of L1 when the VM/AM is in the L3-L0 V/L3 A setting to actually monitor what’s going through L1 at the CT instead of L3.
I can measure with an amp clamp 40A on L3 & 45A on L1, but the PRC will show 80% because I believe it is only measuring L3 at the CT, when I switch to L3-L0 it shows the same load on L3. I will look further into the schematics to make sure.
I wanted to do the same to my MEP-017a but when in 240v mode current was measured on L3, and L2 was short circuited by the voltage selector switch. Maybe it’s not possible to monitor both legs (lines) going through the CT individually. Maybe it’s not worth the hassle to alter something, I just thought it would be sweet to be able to see the load on each leg.