Caliglas
New member
- 5
- 3
- 3
- Location
- Sarasota FL
I checked the MPU as recommended from a friend and it's 2.5 and the switch is set to 60HZ. It ran fine half way thru Milton running AC pool pump and everything else fine. All of a sudden the AC fan outside was running slow. I checked the frequency and it said 50HZ. While running, it pops up for a split second to 60 or so. My friend thought it was surely the MPU. The PEC potentiator behind the frequency knob is corroded. Nothing else on the machine shows any corrosion like the PEC pot. I ordered a new potentiator and will solder it on this week. Anywhere else I can look? FWIW the only reason I know about the MPU is the info from a friend. I'm pretty good mechanically but electric can be trying.
Jerry