% load guage working now
David
Thanks Ike. The generator is currently connected to the shop providing power to the 220v panel and for the last 45 minutes the % load guage is working again as it should. I'll leave well enough alone for now and will report back with any changes.Trace the wires back from the output breaker and make sure they are running through the CT loops. Someone may have rewired it at some point and forgot to run the new wires through the loops.
Ike
David