MEP802A Fuse Blowing
dcvm
Severy Kansas
802A when started didn’t produce power. I discovered the “little fuse” was blown so I took the fuse from a 803A and tried again. The voltage was neither 60hz nor 220V and the voltage adjust knob would adjust the voltage. I plugged in a drill and before Any power could be transferred the fuse blew again. I purchased a new voltage regulator but haven’t tested the machine again because I discovered that while the MOV 14D151k resistor had not been installed. The hour meter indicates 90 hours. Where else should I focus my attention while I wait for the resistor to arrive.
loosegravel
Just a retired mechanic who's having fun!
504
892
Enumclaw, Washington
Can you please take a photo of the fuse that you’re dealing with? Is it the one in this photo?B6D24927-6A51-4089-952A-E69B9299960E.jpeg
loosegravel
504
892
kloppk
3,987
Pepperell, Massachusetts
The MOV IS NOT required to make the generator operator work properly.
The MOV is just an add on to help protect the factory AC Voltage from being damaged.
Ray70
6,732
West greenwich/RI
Assuming you're talking about the VR Quad fuse mod. that @loosegravel depicted, make sure you have the right fuse in there. needs to be a 3A Slo-blow.... otherwise it won't work right.
If the fuse is correct maybe you should ohm out the exciter stator per the TM first?
pull off the tin cover on the end of the generator and test the F1 and F2 connections.
dcvm
Severy Kansas
full off the tin cover on the end of the generator and test the F1 and F2 connections.
Thanks, I’ll check that out tomorrow.
