mep803a working great but no reading on the load guage

joshua1001

New member
24
0
0
Location
Simpsonville SC
Anybody have this issue, didnt see anything on the TM. Did I overlook it? I ran the house the other day on this unit but since I didnt have an ampmeter yet I didnt proceed. Also should I see the frequency drop just a little when something big like the HVAC kicks on? Thanks for patience with a newby in advance.
 

Korgoth1

New member
191
2
0
Location
radford, va
Excercise the selector switch a couple times, most of the time they are crusty causing issues. Some have had faulty current transformers(test ct output, specs are in the manual), or it could be the guage itself.
 

jamawieb

Well-known member
1,414
515
113
Location
Ripley/TN
I would try to rotate the reconnection switch a few dozen times to see if start getting readings. The load gauge receives it signal from a transformer and then goes to the reconnection switch, then to the gauge. I've had a few units that would read low on the load gauge and after rotating the reconnection switch, it got better. The reconnection switch, is the switch behind the gauges on the back wall, that allows you to switch phases.
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,486
1,890
113
Location
Efland, NC
I would try to rotate the reconnection switch a few dozen times to see if start getting readings. The load gauge receives it signal from a transformer and then goes to the reconnection switch, then to the gauge. I've had a few units that would read low on the load gauge and after rotating the reconnection switch, it got better. The reconnection switch, is the switch behind the gauges on the back wall, that allows you to switch phases.
AND Don't switch it with the generator running.
 

Guyfang

Moderator
Staff member
Moderator
16,055
22,613
113
Location
Burgkunstadt, Germany
Thank you Diesel Addict!!!!!!!!!!! That's the biggest killer of switches there is.

Depends on how big the load is, and how big the gen set is. But yeah, the freq meter should move a bit. Nothing earth shattering, but a bit. You may have to adjust it back up if it drops down too far.
 

Guyfang

Moderator
Staff member
Moderator
16,055
22,613
113
Location
Burgkunstadt, Germany
When the load is large enough, the frequency, (engine speed) can drop a tad. If so, yes, adjust it back up to 60 hertz. Normally, it will only be a few hertz. A large drop in the hertz, would lead me to believe that the engine needs to be exercised at ever increasing loads to correct what everyone calls "wet stacking".
 