Hii everyone,

last time you really helped me out on the right speed sensor. The problem right now is. No voltage or hertz is shown. As i iknow i use start to flash the fields. And 130 volts on phases shows up with 45 hertz. When i release start they go back to zero… i checked the relais and the wiring and there all fine. The lights on the avr. Are also working. Not sure what to do now…
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
17,966
26,903
113
Location
Burgkunstadt, Germany
Do you know what a Quad mod fuse is? And if so, have you checked it?

This was a stupid post. I thought this was an A model. My Bad!!!!!!!!!!!!!!!!
 
Last edited:

Dieseljo

New member
11
10
3
Location
Nederland
Do you know what a Quad mod fuse is? And if so, have you checked it?
Never heard of a quad mod fuse.. but i did checked al the fuses i could find. I also checked all the diodes near the field flash relais. The only fuse im not sure of is R2 it gives me an O.L for a second a moment later resistance and back to O.L
 

peapvp

Well-known member
Steel Soldiers Supporter
1,259
1,599
113
Location
Basehor, KS
Never heard of a quad mod fuse.. but i did checked al the fuses i could find. I also checked all the diodes near the field flash relais. The only fuse im not sure of is R2 it gives me an O.L for a second a moment later resistance and back to O.L
R2 is a 330 Ohm / 5W resistor - it should show 330 Ohm on the meter - if it doesn’t then there is only two problems:
1. resistor burnt out and has infinite ohm

2. you do not know how measure resistance and/or how to operate your meter
 

Evvy Fesler

Well-known member
366
772
93
Location
Roxboro, North Carolina USA
It can be misleading to measure a resistor while connected to its circuit. Since it’s not a fuse (usually noted as F), you may not need to check it unless the TM asks you to. Don’t remove it from the circuit, though, as I was just stating a generic rule of thumb. If you need help with the meter and how to use we can coach you. PM me if you like.

Evvy-
 

peapvp

Well-known member
Steel Soldiers Supporter
1,259
1,599
113
Location
Basehor, KS
It can be misleading to measure a resistor while connected to its circuit. Since it’s not a fuse (usually noted as F), you may not need to check it unless the TM asks you to. Don’t remove it from the circuit, though, as I was just stating a generic rule of thumb. If you need help with the meter and how to use we can coach you. PM me if you like.

Evvy-
Thanks Evvy,
R2 is a load resistor, it is connected to the 24 VDC bus after Master Switch S3 and Ground.
It stabilizes the DC Bus when the CIM boots up and during cranking.
If you measure this resistor in circuit with S3 in off position then the parallel resistance of all other devices being supplied here will lower the resistance significantly and it will be more like 30 Ohm + on your meter.
Peter
 
Last edited:

peapvp

Well-known member
Steel Soldiers Supporter
1,259
1,599
113
Location
Basehor, KS
Hii everyone,

last time you really helped me out on the right speed sensor. The problem right now is. No voltage or hertz is shown. As i iknow i use start to flash the fields. And 130 volts on phases shows up with 45 hertz. When i release start they go back to zero… i checked the relais and the wiring and there all fine. The lights on the avr. Are also working. Not sure what to do now…
What this sounds like is a bad voltage regulator, check the LED’s on TCM102 and on the voltage regulator before and during start - make a video of it and post it to YouTube
There is a reason that there are so many LED’s on this backplane…….
 

Dieseljo

New member
11
10
3
Location
Nederland
It can be misleading to measure a resistor while connected to its circuit. Since it’s not a fuse (usually noted as F), you may not need to check it unless the TM asks you to. Don’t remove it from the circuit, though, as I was just stating a generic rule of thumb. If you need help with the meter and how to use we can coach you. PM me if you like.

Evvy-
What this sounds like is a bad voltage regulator, check the LED’s on TCM102 and on the voltage regulator before and during start - make a video of it and post it to YouTube
There is a reason that there are so many LED’s on this backplane…….
Well.. the voltage regulator has allready been replaced. Im going to make a video post it on youtube and get a link down here.
 

Dieseljo

New member
11
10
3
Location
Nederland
R2 is a 330 Ohm / 5W resistor - it should show 330 Ohm on the meter - if it doesn’t then there is only two problems:
1. resistor burnt out and has infinite ohm

2. you do not know how measure resistance and/or how to operate your meter
i made sure it didnt touch it with my fingers. But im doing something wrong for sure….
 

Dieseljo

New member
11
10
3
Location
Nederland
Hii everyone,

last time you really helped me out on the right speed sensor. The problem right now is. No voltage or hertz is shown. As i iknow i use start to flash the fields. And 130 volts on phases shows up with 45 hertz. When i release start they go back to zero… i checked the relais and the wiring and there all fine. The lights on the avr. Are also working. Not sure what to do now…
What this sounds like is a bad voltage regulator, check the LED’s on TCM102 and on the voltage regulator before and during start - make a video of it and post it to YouTube
There is a reason that there are so many LED’s on this backplane…….
 

peapvp

Well-known member
Steel Soldiers Supporter
1,259
1,599
113
Location
Basehor, KS

In this video we can hear a very strange noise right at 23 seconds in, when you excite the unit with the S1 Switch.
I would investigate this first. In the other video you posted, this noise is not present when you excite the system.
Besides this, you need to check the entire wiring system in your genset since you got this free hanging switch on the backside of your front panel and some form of a replacement switch installed.

The LED's where not clearly visible in your videos.

This is a good size project and point towards a complete overhaul of the electrical wiring harnesses for this to work reliably for any extended period of time.

Peter
 
Last edited:

Dieseljo

New member
11
10
3
Location
Nederland

In this video we can hear a very strange noise right at 23 seconds in, when you excite the unit with the S1 Switch.
I would investigate this first. In the other video you posted, this noise is not present when you excite the system.
Besides this, you need to check the entire wiring system in your genset since you got this free hanging switch on the backside of your front panel and some form of a replacement switch installed.

The LED's where not clearly visible in your videos.

This is a good size project and point towards a complete overhaul of the electrical wiring harnesses for this to work reliably for any extended period of time.

Peter
Hi Peter,
At 23 seconds that’s the sound of the starter. I have to switch fault/reset on before i can excite the fields.

I will see what happens when i remove this extra switch and make it original again. But they must have done this for a reason and I’m about to find out. Keep you in touch
 

peapvp

Well-known member
Steel Soldiers Supporter
1,259
1,599
113
Location
Basehor, KS
Hi Peter,
At 23 seconds that’s the sound of the starter. I have to switch fault/reset on before i can excite the fields.

I will see what happens when i remove this extra switch and make it original again. But they must have done this for a reason and I’m about to find out. Keep you in touch
If your starter kicks in during excitation then issue for not getting any power is in the governor control circuit….

Note: the bravo units have two different versions: first version is excitation during start and second version is after Genset started you have to move S1 from Run back to start for 1-3 seconds

in the second version the starter should not engage when S1 is moved back to start for excitation

it is possible that you have mix up of TCM100 / TCM102 and governor controller and CIM between these two versions
The second excitation version was only used I believe with the 3rd revision cim but I am not exactly sure off which cim this requires
Peter
 