• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

mpe803a

kloppk

Well-known member
Steel Soldiers Supporter
2,330
4,198
113
Location
Massachusetts
When I gave the directions on things to probe you weren't suppose to put S1 in START, only to the Prime/Run position.
I gotta sign off, go do some grilling and have dinner with the family.
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
18,135
27,230
113
Location
Burgkunstadt, Germany
There is a very slim chance, that it could have been the A2, (fault Indicator panel). Saw the problem only a few times. The A2 controls not just the lights, but also the funtion to shut the set off, or even restart it, if the A2 has not been reset after a fault.
 

mchlsprgn

Member
143
14
18
Location
jamul cal
There is a very slim chance, that it could have been the A2, (fault Indicator panel). Saw the problem only a few times. The A2 controls not just the lights, but also the funtion to shut the set off, or even restart it, if the A2 has not been reset after a fault.
I started the gen first it ran fine then installed the new VR and then no start . I have another new vr maybe put it in or reinstall the old one Kurt said the vr has nothing to do with the start function, what mess must have screwed somthnig up
 

mchlsprgn

Member
143
14
18
Location
jamul cal
When I gave the directions on things to probe you weren't suppose to put A1 in START, only to the Prime/Run position.
I gotta sign off, go do some grilling and have dinner with the family.
good idea ! i'll sign off with this i have 23 volts on k16 a and b THANK YOU MUCH
 

kloppk

Well-known member
Steel Soldiers Supporter
2,330
4,198
113
Location
Massachusetts
If you had 24 volts at both K16-A and K16-B with S1 in Prime/Run and the engine was NOT running then it points to a possible issue with S14.
S14 is on the far left of the row of relays.
S14 is suppose to switch K16-B to ground causing K16 to pull in with S1 in Prime/Run and the engine was NOT running.

A couple of more voltage measurements needed with S1 in Prime/Run and the engine was NOT running
1) Measure the DC voltage at S14-7 It should be ~ 24 volts DC
2) Measure the DC voltage at S14-8 It should be ~0 volts DC
3) Measure the DC voltage at S14-1 It should be ~0 volts DC
4) Measure the DC voltage at K16-B It should be ~0 volts DC

Let us know what you find
 

mchlsprgn

Member
143
14
18
Location
jamul cal
When S1 is in the prime and run position, you have 24VDC at K16-A, right?
NO i have 23 volts dc
If you had 24 volts at both K16-A and K16-B with S1 in Prime/Run and the engine was NOT running then it points to a possible issue with S14.
S14 is on the far left of the row of relays.
S14 is suppose to switch K16-B to ground causing K16 to pull in with S1 in Prime/Run and the engine was NOT running.

A couple of more voltage measurements needed with S1 in Prime/Run and the engine was NOT running
1) Measure the DC voltage at S14-7 It should be ~ 24 volts DC
2) Measure the DC voltage at S14-8 It should be ~0 volts DC
3) Measure the DC voltage at S14-1 It should be ~0 volts DC
4) Measure the DC voltage at K16-B It should be ~0 volts DC

Let us know what you find
OK I will do this today, I think i may have an S 14 . THANKS I APPRECIATE THE HELP
 
Top