• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

Price for a 803A in good shape

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,580
5,148
113
Location
MA
Within reason... an 803 is an 803 any year. With that said... if you have a choice, Fermont made a better product (versus the earlier Libby models).
 

csheath

Active member
713
196
43
Location
FL
Before you go crazy bidding on unknowns consider what you can purchase a brand new diesel generator for. Hardy Diesel Generators is one source to look at. Note that their units are either single or three phase but not both. They also price muffler and enclosure kits separate.
 

jaxbill

Member
101
12
18
Location
FL
Before you go crazy bidding on unknowns consider what you can purchase a brand new diesel generator for. Hardy Diesel Generators is one source to look at. Note that their units are either single or three phase but not both. They also price muffler and enclosure kits separate.
I've been looking at them and Aurora. I think I would be into a well over $10,000 investment with either. I guess it really depends on what a MEP -803A in good shape will go for. I am hoping I would do a lot less than that. I think I can get a Kubota 11kW for $6K, albeit 3600 RPM, but it's a relatively small unit.
 
Last edited:

Suprman

Well-known member
Supporting Vendor
6,842
654
113
Location
Stratford/Connecticut
Once you start adding in acoustic case and an onboard tank the prices really rise. If you have somewhere to mount a gen and don't need the case and tank then they are a decent deal.
 

jaxbill

Member
101
12
18
Location
FL
I've been searching the archives for awhile. Is there a 803A inspection checklist? I mean something lightweight for inspecting a unit you're considering to purchase.

I am reading through the TM more closely. I can use some logic to come up with things to check for each major system. I don't know exactly what you can visually see with doors open and what you can see without disassembling stuff.
 

csheath

Active member
713
196
43
Location
FL
Once you start adding in acoustic case and an onboard tank the prices really rise. If you have somewhere to mount a gen and don't need the case and tank then they are a decent deal.
Yeah you would have to add the $325 muffler kit but they have a drum kit for $129 and I think I could build an enclosure for way less than they sell them for.
 

windyhill

Member
31
16
8
Location
PA
I've been watching 803a auctions for the last few months. I just picked up a sweet 2010 (like new) on the trailer for $3800. 91 actual hours, not reset, green camo paint isn't even faded. Oil looks new, fuel was even clean when I drained it. Bolts still have lines painted on them, there's not even a spider web in this thing! Must have been stored inside. I'm replacing return fuel lines, and bungs in fuel tank for longevity, and new batteries. But I don't even need to change fluids. I'm very happy with my machine. I think I got a good deal.
 

jaxbill

Member
101
12
18
Location
FL
I've been watching 803a auctions for the last few months. I just picked up a sweet 2010 (like new) on the trailer for $3800. 91 actual hours, not reset, green camo paint isn't even faded. Oil looks new, fuel was even clean when I drained it. Bolts still have lines painted on them, there's not even a spider web in this thing! Must have been stored inside. I'm replacing return fuel lines, and bungs in fuel tank for longevity, and new batteries. But I don't even need to change fluids. I'm very happy with my machine. I think I got a good deal.
Excellent find.
 
Last edited:

csheath

Active member
713
196
43
Location
FL
Why 10kw? Well, I've calculated that based on what I think I need for other types of generators but I realize that might not apply to a MEP, given that it's overbuilt. 10kW could be too much. I'd love to go smaller if I can make the math add-up. I do have a load shedding system already that will work independent of the generator (i.e. not Generac's proprietary controller-based stuff).

- I have 3.5 ton heat pump. 117 LRA. I need to start that. My 60A blower/evaporator circuit carries 8kW electric heater strips that cycle on possibly a dozen or so nights about 3 months a year. I actually thought I didn't need them until they broke once. I guess I wasn't aware of exactly when that heat pump just can't keep up the exchange.
Was just reading back through your post and noticed the quoted comments. I think you will find the 60 amp circuit is just the supplemental heat strips. You should have a 40 amp circuit that runs the actual heat pump/ac unit including the evaporator and condenser fans. My MEP will start and run my 3.5 ton unit with a grunt during start but I don't think it would run the additional heat strip circuit. If power goes out with the temps in the twenties I will just have to be content with a system running non stop to keep the house at 60. If you want ALL the amenities of an all electric house during an outage you will probably need to pony up for a 24KW or larger unit.

I have load tested my 803 to 13,000+ and it will maintain voltage and hertz at such a load but I haven't run it long term at more than 40 amps. I think the MEP-803A is a great generator for us budget minded folks that can do the load management required to use them. It certainly outshines the gas or dual fuel units claiming to be 10,000 max. I bought one of those for my daughter and 10,000 watts will make it crash and burn but it will maintain a 8100 watt load.

So far we have had little need even for AC during the hurricane outages and no need for heat. Outside temps have been pretty mild but that doesn't mean it will always work out that way.
 
Last edited:

jaxbill

Member
101
12
18
Location
FL
Was just reading back through your post and noticed the quoted comments. I think you will find the 60 amp circuit is just the supplemental heat strips. You should have a 40 amp circuit that runs the actual heat pump/ac unit including the evaporator and condenser fans. My MEP will start and run my 3.5 ton unit with a grunt during start but I don't think it would run the additional heat strip circuit. If power goes out with the temps in the twenties I will just have to be content with a system running non stop to keep the house at 60. If you want ALL the amenities f an all electric house during an outage you will probably need to pony up for a 24KW or larger unit.

So far we have had little need even for AC during the hurricane outages. Outside temps have been pretty mild but that doesn't mean it will always work out that way.
Thanks. My panel isn't labeled all that well and I wasn't exactly sure. I do have a 40 amp circuit as you described. My heat strips are only 8,000 watts. Isn't that only 33 amps even though the breaker is much larger?

I was figuring I could run the strips and maybe the fridge with everything else shutoff. I think I can program my thermostat to lock out the heat pump and just turn the strips on with the blower, if needed. This is a good reminder to figure all of that out.
 

jaxbill

Member
101
12
18
Location
FL
I learned something new about heat pumps today that *might* be relevant to sizing the load for a generator to some people in certain climates. Someone more knowledgeable about HVACs might be able to correct me but I think this is mostly correct.

I didn't realize that in very cold weather the condenser unit automatically defrosts itself by running the coolant in the reverse direction, which is actually air condition mode. I'll admit I didn't know it needed to defrost itself in the first place. It seems obvious in retrospect that drawing hot air from inside (just like it does all summer) is a good way to defrost the condenser.

Apparently the condenser unit outside triggers the heat strips independent of the thermostat settings/configuration. If the strips were disabled (via breaker or control wire), it's basically like turning the AC on for as long as the defrost cycle runs. Without the strips, I am guessing you'd actually reduce the temperature inside the house and ultimately waste fuel to bring the temp back up when the defrost cycle ends.

I read that defrost mode will trigger when the sensor inside the condenser reaches 32F. I actually don't know how long the cycle takes, how long it would try if it was really frozen up, or how often it could possibly trigger in a given time interval. I imagine there is some kind of hold down timer so it's not defrosting every 30 minutes but I have no idea.

I never anticipated the heat strips being enabled by anything except the thermostat (i.e. auxiliary heat mode when the thermostat realizes the pump is not keeping up with the user selected temperature OR when the user manually chooses "emergency heat" mode to disable the heat pump). Sure, it sounds like we can kill the breaker for the heat strips to avoid them ever coming on but I did not expect to create a situation where I will be cooling my house at the worst possible time and then using more fuel to heat it back up again.

My strips are only 8,000 watts @ 240V but this might be a bigger deal for folks with larger homes and strips with a much larger draw. I wasn't going to factor this into my load management kit setup but now I think I might. I don't mind shedding my 5,500 watt water heater (assuming it's active) and some other circuit so I can run the strips for a few minutes. I might even save generator fuel by avoiding the heating > cooling > re-heating cycle.

I didn't learn this the hard way during today's storm but this really reinforces a lesson about testing everything in as many situations as possible. It's easy to live in Florida and get caught up in testing for a hurricane but ignore the "once every 5 year" winter scenario.
 

eatont9999

New member
120
0
0
Location
DFW, Texas
I'm still trying to sell an 803A with a little over 5000 hours on it. Everything works and I refreshed it when I got it. I still have not had a serious buyer. I'm asking $3000 but will negotiate. People like to call on it, setup a showing and then fall off the planet.
 

csheath

Active member
713
196
43
Location
FL
I don't think heat strips are required for normal heat pump function. Heat pumps come without them installed. Maybe it's because different sized are optional.
 

dougco1

Well-known member
Steel Soldiers Supporter
824
558
93
Location
Cooperstown NY
I'm still trying to sell an 803A with a little over 5000 hours on it. Everything works and I refreshed it when I got it. I still have not had a serious buyer. I'm asking $3000 but will negotiate. People like to call on it, setup a showing and then fall off the planet.
This will make you cry. My municipality is signed up with the Federal surplus donation program that enables us to requisition surplus as its released. We have first dibs on all surplus "after other Federal agencies" and what is not spoken for gets sent for public auctions that you all see. Yes we do pay a fee for the transfers to cover the paperwork but its very reasonable. In the last year I have picked up 3 trailer mounted gensets 802A, 803A, and an 804B all in great shape and low hours "less than 100hrs" for 5% of original government purchase price. That works out to be about $600, $750, $900 respectively. I keep these around for emergencies or as back ups for our communication towers. The 5K we find very handy and drag it with us to remote job sites that my department gets involved in. After 18 months the municipalities own them.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks