• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

Running mep802/3 with out batteries

dstang97

Well-known member
1,859
30
48
Location
Clover, SC
Can I slave my mep802 off my cucv with out batteries in the generator? I know your not supposed to do it with the older generators, but have not read anything about the newer ones. I would just leave the cables connected while it's running.
 

kloppk

Well-known member
Steel Soldiers Supporter
1,968
3,069
113
Location
Pepperell, Massachusetts
From the -10 TM

Two batteries are required, one on each side of the generator set. The batteries are electrolyte serviceable, lead
acid, 12 volt type, connected in series. After starting, the generator set is capable of operating with batteries
removed. A diode and a fuse, located behind the control panel assembly, protect the generator set if the batteries
are incorrectly connected.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks