voltage drop

Ray70

Well-known member
2,369
5,054
113
Location
West greenwich/RI
How much are you looking to raise it? like 5-8 volts? What are you using for cordage?
You can raise the voltage a bit to compensate, but if you're seeing more than about a 5 or 6 volt drop, you might have something else going on.
 

Zed254

Well-known member
866
465
63
Location
S. Hampton Roads, VA
I have ~50 ft of cord with both my 803 and 802, so I routinely bump up voltage at the machine 1 or 2 volts. https://www.calculator.net/voltage-...ce=150&distanceunit=feet&amperes=26&x=48&y=23

Check the voltage at your house with your multi-meter to confirm proper setting.

Something to consider for wire size: That 802 can be configured for single phase 120 volts delivering 52 amps on a single hot conductor. This is the way I run mine for a small camper that does not have a 240 volt distribution box. If you go with #8 awg you will only be good for around 35 - 40 Amps . 4 conductor 6awg will give you a 45 - 55 amp rating: www.cmewire.com/catalog/sec19-FCX/FCX-Cu-01-AMP.pdf .
 

Coug

Well-known member
Steel Soldiers Supporter
2,834
4,048
113
Location
Olympia/WA
it won't hurt the generator to have the voltage up a little bit. There are voltage drop calculators online that will tell you the expected amount of voltage drop using what size cable/length cable/load and stuff like that, but general rule of thumb is 5% at the furthest electrical access point (house outlet) furthest from power source. That translates to meaning if the generator is set to 120VAC, there should be nowhere in the house you see anything lower than 114VAC

Pretty much everything inside your house should be fine anywhere between 110-120VAC with no issues, the only thing to really worry about is making sure the frequency is correct, and frequency doesn't get affected by length and size of wiring.

Using 8 gauge wires with the gen set to 120/240VAC, drawing 26 amps of 240V (which is going to be the same as 2 circuits of 26 amps 120V with a balanced load) the voltage will drop 4VAC over that 150 feet of wire. This is within the allowed 5% (6VAC), so you will most likely be just fine.


The gen specs say you can adjust voltage from 228-252VAC at 240V setting, which is 114-126 for the 120 legs.



If you run it set to 120VAC only, then you hit 5% voltage drop at 32 amps. You would have to go up to 6AWG copper wire to handle 50 amps power at 150 feet distance.

 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,573
5,102
113
Location
MA
Even with that though, most modern appliances have auto switching transformers that will accept down to 50hz.
 

Ray70

Well-known member
2,369
5,054
113
Location
West greenwich/RI
Correct, but you only need to worry about the voltage dropping, the Hz will not change due to the cord size or length , only the voltage will drop.
Hz is solely dependent on engine RPM and will only change when the engine speed changes.
 

Coug

Well-known member
Steel Soldiers Supporter
2,834
4,048
113
Location
Olympia/WA
Even with that though, most modern appliances have auto switching transformers that will accept down to 50hz.
Some appliances will do that, but some won't. A lot of the cheaper modern electronics don't like anything other than being right at 60hz. These military generators have a lot cleaner sine wave than a lot of civilian units do, so electronics shouldn't be an issue as long as you are close.
 

csheath

Active member
713
196
43
Location
FL
My utility voltage measures 248 at the panel. My 803 sits right behind the house and is connected with 12' of 6 gauge wire. I set the gen voltage to match at 248.

Shouldn't hurt a thing IMO.
 