    Ok..thanks

  2. #42
    Private vanderwoude's Avatar
    Join Date
    Jul 2012
    Location
    Townshend, Vt
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default

    "L0 is bonded to the frame where the two groups of wires come out of the generator head itself, they go into the lower control panel on the left, but one of those wires also swings back around and bonds L0 to the frame...that's the one that should be disconnected and isolated. This is a picture I took a while back for someone else, but it shows the bonding wire."

    I just looked at the connections and would have a lot of hassel in disconnecting and re-connecting LO from the grounding split bolt; instead I will clip the wire from LO, as close as I can to the back of the split bolt lug, strip it and put a large wire nut on it. If I use the gen as a SDS, i can just uncap the LO wire and fasten it in the split bolt along with my ground rod wire.

  3. #43
    4 Star General
    Join Date
    Apr 2009
    Location
    SW, Louisiana
    Posts
    1,976
    Thanks
    35
    Thanked 384 Times in 296 Posts

    Default

    I would strongly suggest no using a wire nut for such safety connection in a high vibration environment

  4. #44
    Private vanderwoude's Avatar
    Join Date
    Jul 2012
    Location
    Townshend, Vt
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default

    Your right, I should have added "tapped" wire nut!

  5. #45
    2 Star General EO2NMCB's Avatar
    Join Date
    Dec 2007
    Location
    DeSoto, MO
    Posts
    612
    Thanks
    425
    Thanked 138 Times in 86 Posts

    Default

    So which is the correct hookup, post #20 or post #32? They seem to conflict with each other.
    m35a2c
    m813
    m816
    m927
    m931a1
    m1009
    m1101
    m1102
    m1061a1
    m101a1
    m105a2 x2
    m416
    m116a2
    m116a3
    mep002 x2
    mep003 x2
    MVPA-24541

  6. #46
    Blind squirrel rehabiltator Speddmon's Avatar
    Join Date
    Apr 2009
    Location
    Cambridge, Ohio
    Posts
    4,678
    Thanks
    347
    Thanked 1,174 Times in 652 Posts

    Default

    Read post #25...#20 was before I started digging deeper into the NEC
    Quote Originally Posted by Recovry4x4 View Post
    That's why I knew the answer and you didn't. I read the kindling.
    He is "anti-doghead".

    Even a blind squirrel finds an acorn every now and then!



    1970 M35A2 "The Stone Wagon" SOLD
    1985 M1028/M1031 w/700R4 "Road Oiler"
    MEP-003a 3000 hrs
    MEP-003a 1500 hrs
    1964 Case 530CK "Construction King" Backhoe/loader "Yard Oiler"

    MEP-002a & MEP-003a Spin-on oil filter kits are still 4 sale in the classified section

  7. #47
    2 Star General EO2NMCB's Avatar
    Join Date
    Dec 2007
    Location
    DeSoto, MO
    Posts
    612
    Thanks
    425
    Thanked 138 Times in 86 Posts

    Default

    Thanks Speddmon I corrected my hook up when I got home.
    m35a2c
    m813
    m816
    m927
    m931a1
    m1009
    m1101
    m1102
    m1061a1
    m101a1
    m105a2 x2
    m416
    m116a2
    m116a3
    mep002 x2
    mep003 x2
    MVPA-24541

  8. #48
    Private tm050712's Avatar
    Join Date
    May 2012
    Location
    Jackson, MS
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default MEP-002A: Ground wire for 120v connection?

    Hi Guys - I've been following this and other threads regarding connecting my 002 to a small cabin I have. The cabin is already wired and has a meter base (with ground rod) that will not be connected to the power company grid for quite some time (transfer switch not presently needed). I plan on using the 120v mode for the connection to the breaker panel so I won't have to be concerned with balancing loads like I would if I used a 220v connection.

    Based on what I've read so far here and in the TM, I believe that my connection should be: L-3 (hot) to lugs on breaker panel and L-1 (neutral) to neutral/ground buss on the breaker panel. My question is: Where should the Ground wire be connected - L-1, L-O, or not at all? The Change 6 wiring modification mentioned in the TM has been made. Any advice will be greatly appreciated.

  9. #49
    3 Star General
    Join Date
    Apr 2010
    Location
    LA
    Posts
    920
    Thanks
    5
    Thanked 74 Times in 57 Posts

    Default

    Quote Originally Posted by tm050712 View Post
    Hi Guys - I've been following this and other threads regarding connecting my 002 to a small cabin I have. The cabin is already wired and has a meter base (with ground rod) that will not be connected to the power company grid for quite some time (transfer switch not presently needed). I plan on using the 120v mode for the connection to the breaker panel so I won't have to be concerned with balancing loads like I would if I used a 220v connection.

    Based on what I've read so far here and in the TM, I believe that my connection should be: L-3 (hot) to lugs on breaker panel and L-1 (neutral) to neutral/ground buss on the breaker panel. My question is: Where should the Ground wire be connected - L-1, L-O, or not at all? The Change 6 wiring modification mentioned in the TM has been made. Any advice will be greatly appreciated.
    If you go that way you should probably wire one side of your panel and put all your loads (breakers) on that side.
    I would just wire it 220 and maybe try and put 1/2 the loads on one side of the panel and 1/2 the loads on the other side.
    I don't know if it is against code to jump a single 120V leg to both sides of a 220V panel but is surely seems incorrect.
    Unless you are planning to run it way up near full capacity and can't possibly split the load logically in the panel I would be more worried about questionable wiring than unbalanced loads.
    Just my opinion. Many people like to backfeed through their dryer outlet and that works, too, but sometimes there are surely better ways to do things.


  10. #50
    Private tm050712's Avatar
    Join Date
    May 2012
    Location
    Jackson, MS
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default

    Derf, thanks for the suggestion to just connect to one side of the breaker panel - I plan on doing just that. Balancing would be a problem so I believe that the 120v configuration is the best way for me to go. I still have the question about grounding at the generator though. The only connections I've seen so far just mention the L-3 hot and the L-1 neutral. You would think that the TM would cover that.

Page 5 of 15 FirstFirst 1 2 3 4 5 6 7 8 9 ... LastLast

Similar Threads

  1. Replies: 7
    Last Post: 01-19-2015, 19:04
  2. MEP 003 Question
    By bumperjumper in forum Generators
    Replies: 32
    Last Post: 07-15-2012, 18:11
  3. MEP 003a intake area wire harness needed
    By maddog in forum Generators
    Replies: 9
    Last Post: 10-09-2009, 16:37
  4. XM818 trailer hook up question
    By mmhsv in forum 5-ton and up
    Replies: 9
    Last Post: 06-18-2009, 06:57

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •