@Scoobyshep we havent installed a backup battery yet.

The MeBay documentation does not specify a particular Battery or a even a voltage.
What is also important is that the Plus terminal off this back up battery is grounded to chassis and the negative terminal connects to E3 on Mebay Controller!

There is a Parameter # 28 in Group 1 listed for Auto start operation, in case of mains failure for the D72 Version
I have absolutely no clue of what ABF is or what they are talking about in this parameter description

If you find any more information Scoobyshep please let us know.
 

2Pbfeet

Well-known member
713
1,431
93
Location
Mt. Hamilton, CA
@Scoobyshep we havent installed a backup battery yet.

The MeBay documentation does not specify a particular Battery or a even a voltage.
What is also important is that the Plus terminal off this back up battery is grounded to chassis and the negative terminal connects to E3 on Mebay Controller!

There is a Parameter # 28 in Group 1 listed for Auto start operation, in case of mains failure for the D72 Version
I have absolutely no clue of what ABF is or what they are talking about in this parameter description

If you find any more information Scoobyshep please let us know.
😯 Wow.

A positively grounded battery on a modern piece of electronics seems unusual to the point where I would be wondering about a documentation error. It would certainly have me being extremely careful. If you probe the (-) point when the controller is powered up is there a voltage?

I realize it is a long shot, but have you reached out to MeBay directly? They do, at least reportedly occasionally, respond, sometimes with useful information.

All the best,

2Pbfeet
 

peapvp

Well-known member
Steel Soldiers Supporter
1,256
1,589
113
Location
Basehor, KS
😯 Wow.

A positively grounded battery on a modern piece of electronics seems unusual to the point where I would be wondering about a documentation error. It would certainly have me being extremely careful. If you probe the (-) point when the controller is powered up is there a voltage?

I realize it is a long shot, but have you reached out to MeBay directly? They do, at least reportedly occasionally, respond, sometimes with useful information.

All the best,

2Pbfeet
@2Pbfeet
Yes, I agree. The back up battery has not been a priority for Larry. It affects only the Date and Time and therefor Maintenance schedules, which can be setup.

I checked several other MeBay Controllers and those have integrated 1.5 V Battery's as Backup or no backup at all.

We have not contacted MeBay as this has not been a priority.
 

peapvp

Well-known member
Steel Soldiers Supporter
1,256
1,589
113
Location
Basehor, KS
@Scoobyshep and @2Pbfeet

when Larry and I started this project a few months ago, I thoroughly investigated this reversed battery polarity issue by checking several older D7x manuals and the controller itself without contacting MeBay.

The reversed polarity for this backup battery is consistent in all of their manuals, written and in wiring diagram.
All of their specs as to I/O’s checked out during test and implementation.
I would say that it is save to assume that this battery connection is reversed polarity for whatever illogical reason they did it this way.
IMG_4179.jpeg
IMG_4180.jpeg
76688348204__797DE919-7871-42CF-83C0-E74EC3558461.jpeg
 

2Pbfeet

Well-known member
713
1,431
93
Location
Mt. Hamilton, CA
@Scoobyshep and @2Pbfeet

when Larry and I started this project a few months ago, I thoroughly investigated this reversed battery polarity issue by checking several older D7x manuals and the controller itself without contacting MeBay.

The reversed polarity for this backup battery is consistent in all of their manuals, written and in wiring diagram.
All of their specs as to I/O’s checked out during test and implementation.
I would say that it is save to assume that this battery connection is reversed polarity for whatever illogical reason they did it this way.
View attachment 950146
View attachment 950147
View attachment 950148
That does look convincing similar for negative input/positive ground, though I wonder a bit at the diagram in both places of a multi-cell battery for a 1.5V input.

Learn something new every day!

Thanks.

All the best,

2Pbfeet
 

peapvp

Well-known member
Steel Soldiers Supporter
1,256
1,589
113
Location
Basehor, KS
That does look convincing similar for negative input/positive ground, though I wonder a bit at the diagram in both places of a multi-cell battery for a 1.5V input.

Learn something new every day!

Thanks.

All the best,

2Pbfeet
We do not know what the voltage input is rated for.
That’s the big question mark.
 

peapvp

Well-known member
Steel Soldiers Supporter
1,256
1,589
113
Location
Basehor, KS
@2Pbfeet
I just rechecked with MeBay HQ website and they released the MK III version of the DC70 DC72 on April 2nd and guess what

they call the back up battery now UPS Battery Pack and have changed Terminal E2 for + Pole and left E3 as - Pole of battery
Allowable voltage input range: 0 to 100VDC

I am pretty sure they had plenty of Chinese customers scratching their head on this thing with the backup battery thing on the MK II units and a few off those probably went up in smoke…

IMG_4183.jpeg

IMG_4182.jpeg
 

peapvp

Well-known member
Steel Soldiers Supporter
1,256
1,589
113
Location
Basehor, KS
@peapvp That seems like a nice find! Congratulations.

0-100V seems like quite the range though, but it does take so little to keep an RTC going.

All the best,

2Pbfeet
@2Pbfeet
MeBay makes ATS and they use DC to switch the contactors. They operate at 72VDC and have 6 pcs 12V 10Ah batteries to bridge and operate the whole system including DC7x between Mains failure and Genset power available.

A 9V battery should suffice to power RTC
 