• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

I'm an idiot!!! - Fermont MEP-802A 5kW

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,574
5,111
113
Location
MA
As a general rule an AC fuse can be used in a DC application as long as the DC voltage is < 50% of the AC voltage rating of the fuse.
The one spec'd out in the TM is O.K. to use up to 60 volts DC.
Did not know that. Thanks for the info.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,574
5,111
113
Location
MA
I can't seem to find a breakthrough amperage rating on the Eaton OEM one, but the alternate Ive bought before (BK/ABC-30-R) shows an interrupt rating of only 200A... so I think that McMaster fuse might not blow when you want.
 

NY Tom

Well-known member
Steel Soldiers Supporter
522
780
93
Location
Riverhead, NY
I can't seem to find a breakthrough amperage rating on the Eaton OEM one, but the alternate Ive bought before (BK/ABC-30-R) shows an interrupt rating of only 200A... so I think that McMaster fuse might not blow when you want.
200A is the listed breakthrough current on that item:


Current Rating:30 A
Fuse Type:Fast Blow
Fuse Size / Group:3AG (6.3 mm x 32 mm)
Voltage Rating AC:250 VAC
Voltage Rating DC:125 VDC
Interrupt Rating:200 A

But the interrupt or breakthrough current is the maximum current the the fuse can interrupt.

Not my words here:

“Interrupt rating” is not the same as “ampere rating,” even though both these are dealing with current values.

When reading technical data about a particular fuse you will see symbols or rather abbreviations such as I.R. or IR which refer to “interrupt rating.” Other abbreviations could be A I.R., A IR, or kA I.R. which is “amperes interrupt rating” or “kilo amperes interrupt rating” respectively.

Given a particular rated voltage, this current rating refers to the maximum amount of instantaneous current that can be interrupted safely without explosion or damage to the fuse link carrier, such as the cartridge or tube. This interruption of current flow can occur in fault or short circuit conditions. This current rating has been approved through standardized tests.

Interrupt rating is also referred to as “breaking capacity.”


In other words the fuse from McMaster is a more highly rated fuse - thus the "3AB" rating vs "3AG".
 

4x4nutz

Active member
Steel Soldiers Supporter
263
101
43
Location
Mico, Texas
THANK YOU gentleman for helping me get me 802A going again. Runs great, just need to get that oil pressure gauge fixed or replaced. It worked fine until we had the battery arc issue. Is it possible it blew the gauge when the batteries arced?
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,574
5,111
113
Location
MA
Entirely possible as the arc would have been on the DC circuit, which this gauge also is. There are testing methods in the TMs for the gauges to confirm if they are good or not.
 

Ray70

Well-known member
2,372
5,073
113
Location
West greenwich/RI
You guys really go deep into fuse selection! many many time I just went to my assortment of glass tube car fuses and grabbed a $.25 30A 1/4 x 1 1/4 AGC fuse, install it and done!
On the oil gage situation I see someone already changed the oil pressure gage, I'd double check the wiring and check the resistance on the sender, that should give you the answer.
 

loosegravel

Just a retired mechanic who's having fun!
504
887
93
Location
Enumclaw, Washington
You guys really go deep into fuse selection! many many time I just went to my assortment of glass tube car fuses and grabbed a $.25 30A 1/4 x 1 1/4 AGC fuse, install it and done!
On the oil gage situation I see someone already changed the oil pressure gage, I'd double check the wiring and check the resistance on the sender, that should give you the answer.
Pretty simple with a one wire sender. This works for any gauge. Ohm check the wire from the sender to the gauge. If that’s good, with the wire disconnected from the sender and the gauge supplied with power, the gauge should be pegged on the high side. With the wire disconnected from the sender and then grounded the gauge should be pegged on the low side.
 

4x4nutz

Active member
Steel Soldiers Supporter
263
101
43
Location
Mico, Texas
Pretty simple with a one wire sender. This works for any gauge. Ohm check the wire from the sender to the gauge. If that’s good, with the wire disconnected from the sender and the gauge supplied with power, the gauge should be pegged on the high side. With the wire disconnected from the sender and then grounded the gauge should be pegged on the low side.
The gauge actually goes down when I apply power....what's up with that?
 

4x4nutz

Active member
Steel Soldiers Supporter
263
101
43
Location
Mico, Texas
Pretty simple with a one wire sender. This works for any gauge. Ohm check the wire from the sender to the gauge. If that’s good, with the wire disconnected from the sender and the gauge supplied with power, the gauge should be pegged on the high side. With the wire disconnected from the sender and then grounded the gauge should be pegged on the low side.
Where is that sending unit for the oil pressure gauge located? The diagram on the inside of the door does not really show anything, and there's no photos on the TM.
 

loosegravel

Just a retired mechanic who's having fun!
504
887
93
Location
Enumclaw, Washington
The two wire switch is for low oil pressure shut-down. It doesn’t affect the gauge. The bell shaped sender with one wire is what works the gauge. It’s basically a variable resistor that changes it’s “R” value when the pressure increases. If you disconnect that one wire and turn S1 on, the gauge should go high. If you ground that one wire and turn on S1, the gauge should go low. If that doesn’t work, then ohm check the wire from the gauge to the sender. If that’s good, then your gauge is not functioning.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks