MEP-002 Tripping DC Control Circuit Breaker

Jimc

Member
725
1
18
Location
Mullica, nj
it needs power to produce power. when it just starts up you need to hold in the start position to generate the magnetic field so it can produce power. its fairly normal and time needed seems to vary a bit from generator to generator.
 

Isaac-1

Well-known member
1,970
48
48
Location
SW, Louisiana
Like Jim said it varies from generator to generator, but to put it simply the MEP-002a / MEP-003a voltage regulation circuit often can not build to full voltage from the slight amount of residual magnetism in the generator end, so they added a field flashing circuit that operates while the switch is in the start position. I suspect it is partly due to the voltage regulators reverse acting design. Either way it is a simple matter of holding the switch in the start position long enough for the voltage to come up, the mistake people make is treating the start switch like a car ignition key and not holding it in the start position long enough for oil pressure to come up and voltage to build.
 

Keith_J

Well-known member
3,657
1,313
113
Location
Schertz TX
Or it could be something with the rotor causing the rotating field to quench. Like a shorted rotor diode. Electricity is easily produced. Spin a magnet in a coil is the method, the magnet here is an electromagnet, made by spinning a coil through a magnetic field, then converting it to direct current and powering the field.
 

Gnoz

New member
20
0
1
Location
Saint Louis
I just re placed a defective VR on a MEP 0002A and now, with the new one, I am getting excessive voltage between 260 and 300vlt on a 120/220 setting. I was wondering what could have possible gone wrong. When I start the generator, before it is operating at 1800 rpm, I get 124vlt and then once it is running at its full speed, the voltage jumps to 250, then when load is applied, the voltage increases some more. Thanks
 

R Racing

Active member
2,767
15
38
Location
St. Leonard, MD
I just re placed a defective VR on a MEP 0002A and now, with the new one, I am getting excessive voltage between 260 and 300vlt on a 120/220 setting. I was wondering what could have possible gone wrong. When I start the generator, before it is operating at 1800 rpm, I get 124vlt and then once it is running at its full speed, the voltage jumps to 250, then when load is applied, the voltage increases some more. Thanks
Mine use to peg. I found out I had a bad spot on either VR12 or VR15 so I would turn them a turn to the left. then to the right. then back to center then my voltage was 240.
 

Gnoz

New member
20
0
1
Location
Saint Louis
I am looking for replacement CR Diodes (Rotating diodes) for my MEP002A. I have not been able to locate them anywhere and I was wondering if anyone on here had a lead. Thanks
 